Question about Gibson Nordyne GR6GD-X42K072C 3.5 Ton 13 Seer 72,000 BTU Gas Electric Package Unit
Open limit switch code
Furnace lights but only runs a couple of minutes,then cycles off, relights and repeat cycle again. After several cycles, fails to relight and blower can only be shut-off by killing power. When power restored blower still running. After a few hours process can be repeated.
Take the Filter out of your furnace and try it again, some times the filter restricts the air flow to much going back to the furnace and it gets to hot and the switch opens. Also check that there is nothing blocking the return vents, like clothes, shoes or the ducts are very dirty but i don't think that's a problem. If the filter is a problem, put one of those spun fiber filters in, the kind you can see through they are blue or green. they are cheap maybe a $1.00 - $2.00
Hope this helps
V6boyo
Posted on Jan 10, 2013
Gas furnace short cycles 2 minutes or less. Multiple troubleshoot steps and replaced components - no help. Any advice?
I did not see that your indoor fan motor started. Near your indoor fan motor there is a temperature switch that is called the fan delay relay. On a temperature rise the relay shuts a contact that turns on the indoor fan motor. If the contact does not close the high temperature limit will shut the gas controls off like your getting. A fan delay relay also allows the fan to run a minute or so to carry away the remaining heat in the furnace and help cool the furnace down. The fan delay relay is normally mounted in a recessed area in the fire wall of the furnace plate. I have also seen them on the top of the furnace heat exchanger. Anyway, the fan delay relay will probably not be available on a sunday, so temporarily until parts are available, try turning the thermostat fan from auto to on and try the furnace again. By turning on the fan to on the high temp limit will not shut you down again.
I have had high temp limit change there trip points, but you said you bypassed it and did the same thing.
Another cause could be using the wrong type of air filter. The new pleated filters sold block to much air flow. If air mass flow rate drops the difference in temperatur go up and when the difference in temperature go up, it gets nearer the high limit and causes it to trip. All pleated filters drop normal air flow through ducts by at least 35%. To make your air duct system work properly use the what is called throw away filters which cost about 1/3 the cost of the pleated filter. Remember to either clean or change the throw away filter monthly to reduce dirt being drawn into your duct system.
Hope this helps.
Feb 13, 2015 | Heating & Cooling
Furnace kicks on and heats up for 5 min. then will shut down - no flame - main blower will run for a few min and then the whole cycle will start again. flame sensor checked ok with meter at approx 5.0
What is your temperature rise during the 5 minutes it does run? Could be overheating and kicking out on limit switch. Watch the diagnostic light for a code. (3 blinks means this, 4 blinks means that etc.)
Jan 09, 2014 | Amana Heating & Cooling
My furnace will not reach the desired house temperature in one cycle. It will run for several minutes, shut off, and repeat. It eventually reaches the desired temp but it take a long time and I feel it...
There are a few different reasons for short cycling of a furnace.
1. Inadequate air flow. Not enough air moving through the furnace can cause it to overheat and trip the high temperature limit switch.
check to see that all registers are open and returns are not blocked.
2 Improper heat anticipator setting on thermostat. Some thermostats have a heat anticipator and too low of a setting can cause short cycling.
4 Partially blocked drain hoses. If the condensate backs up into the furnace it can shut the flame off and then when the condensate drains the furnace starts again. Check all drain hoses to make sure they are clear.
These are just some of the possible reasons for short cycling .
Hope this helps.
Dec 26, 2013 | Heating & Cooling
Furnace is a Rudd UGEB model. Burners ignite and but the blower (squirrel cage) doesn't start. After a couple minutes they turn off and the blower starts and runs for less than a minute and shuts off....
Sounds like the fan limit was not replaced correctly. You can try switching the blower to the On position (instead of Auto), if the furnace runs properly with the blower on that would be the most likely culprit.
Sep 24, 2011 | Ruud UBHC Air Conditioner
Goodman GS9 propane furnace inducer motor runs continuously
it sounds like the low temp limit switch, the one that cools the furnace down with the burner off and the thermostat open, when it cools to a point the fan stops, the other switch in burner area turns burner off/on, hope this helps
Jan 31, 2010 | Goodman GMS90703BXA Heater
Miller furnace model M3RL080 BW, code flashes open limit switch or external load on W, I bought a new limit switch, the furnace runs for 5-10 minutes then the flame goes out, the blower keeps running and...
Check your furnace filter any Limit fault code usually relates to airflow...Not enough...causes the furnace to run too hot and shut off....the furnace can be too big for your house if its new...the ductwork can be too small , also make sure your return air vents are clean and unobstructed . Your furnace can be running too long a cycle ....also if you have central air conditioning the coil for the AC in the Furnace can be dirty...restricting airflow...if all this seems ok you can usually increase the fan speed or try tunning the fan in the "On" position on your thermostat this will promote better circulation
Oct 25, 2009 | Heating & Cooling
Red light blinks 4 times, will only cycle once
the high limit is sensing the internal temprature of the furnace.If your filter is very dirty or you have to many of the registers/dampers shut it will cause the temp. of the furnace to exceed its rating and the high limit will open the circuit and shut down the flow of gas. Your blower will then run until the furnace has cooled and the switch will close and allow it to come back on. This is bad for your furnace, make sure your filter is clean and you dont have to many registers shut. If you have run the unit without a filter the problem could be much more sever requiring blower wheel and coil cleaning and possibly a cracked heat exchanger.
Sep 12, 2009 | Goodman GMS90703BXA Heater
Dayton blower fan repeatedly kicks on and off
chech the air filter is clean and the fan limit switch look to change fan limit
Nov 01, 2008 | Dayton Gas Furnace Heater
Gibson Nordyne GR6GD-X42K072C 3.5 Ton 13 Seer 72,000 BTU Gas Electric Package Unit Logo
100 people viewed this question
Top Gibson Heating & Cooling Experts
john h
Are you a Gibson Heating and Cooling Expert? Answer questions, earn points and help others