American Standard Gas furnace acting weird
I am a heating tech and i am just confussed. Well i think its the board but just looking for a second opinion. Call for heat and the ventor motor starts. after a few seconds the ventor quits and the main blower starts and the fault code states it is reverse wiring, something to do with the ignitor or low voltage. The power comming from the board to the ventor is 120 to ground and 168 volts to neutral. I also have a an amp draw of 10amps at the ventor but if i check the amps at the line wire coming into the furnace i only draw about 1 amp which is normal. I am pretty sure it is the board but i am not used to the american standard furnaces. It is a new american standard stage with reg motor. The main power coming in is good and polarity is good and properly grounded as far as i can see.
  • subzero_hc Jan 21, 2009
    Ya i have checked the polarity and the grounding and they are both good. Doyou think it is posible for the relay for the ventor to have a high resistance through it causing the high amps? but you would think that you would get high amperage at the main power coming in the unit. The fault code does say that oe posibility is that ignitor, but the ventor doesn't even run long enough to go through the sequence of operations. I wonder if the board does some sort of resistance chech on the ignitor as it is calling for heat. I checked the resistance on the ignitor the other day and it was low and didn't seem too high though. But then everything falls back on that weird voltage to the ventor. I cant even find a number to call American Standard. Let me know if you have any questins or ideas...
  • 1,214 Answers
I am concerned of the readings you have given. 120 volts to ground, but 168 volts to neutral? And having 10 amps of current at the "ventor", but only 1 amp for the whole furnace worries me, because power for the "ventor" comes through the furnace.
You should not have 168 volts to anything! Unless somehow 240 volts is feeding the system, and there is a medium resistance short somewhere.
The controller boards are sensitive to AC polarity (if you will). Neutral should be tied to neutral on the board. You can check that by testing for voltage between the neutral terminal and chassis ground (assuming the chassis is properly grounded.). The hot leg of incoming power, which should be 120 volts, should be connected to the terminal that says 120 VAC.
If your getting 168 volts AC somehow, then something is wrong, and you need to disconnect power from this unit until you find the cause.
As a heat-A/C tech, you should know the sequence of operation for all furnaces is pretty much the same. The boards, while manufactured by different manufacturers, all operate pretty much the same way.
Let me know your findings in reply and I will attempt to help you more.
Posted on Jan 20, 2009
  • Mark Egan Jan 21, 2009
    Assuming the "ventor" motor you are talking about is the combustion air fan, if it's power source is the controller board, then the current pulled by the combustion fan should be seen on the power in-feed side to the furnace, and board.
    If it doesn't (and what you describe doesn't), then your looking at an incorrectly wired system. You should be seeing wires that have been cut and spliced that were not factory cut and spliced.
    The relay will not "create" current with a high resistance of some type. You need to go back and remember ohms law to know that (when considering the above as well.), as well as visualize the internal workings of the relay. You whould be able to measure any perceived high resistance that your thinking.
    When you measured the "ventor" motor current, were you measuring the incoming power current at exactly the same time, in order to know the "ventor" was pulling 10 amps while the incoming power was 1 amp?
    Does the ventor motor run?
    I have had a piece of trash (LPS) get in the rubber tube connected to the combustion air "fan prove" switch shut a system down before. Don't remember the code we got, but, the code gave no indication that the combustion air switch was having a problem. And the LPS was hard to identify as it was lose inside the combustion fan housing.
    American Standard is the old Trane. .
Stage 2 is on the screen but no heat will come on. American standard thermostat. A/c comes right on but when heat is turned on "stage2" comes up on the screen but the heat won't Not a touch screen.
You should look at your furnace and see if any safety lights are flashing. Make sure your thermostat is set to heat.Check system your using for updates.
Nov 19, 2016 | American Standard Heating & Cooling
My American Standard Furnace light blinks 3 times stops and blinks 3 times again and so on.
Look inside of service panel for trouble shooting codes and solutions
Feb 13, 2016 | Heating & Cooling
Amana furnace
Are you sure the control board is good? I would look at that before going elsewhere.
May 02, 2017 | Heating & Cooling
Hi :) I have the Trane Furnace that just turn on
on older tranes if 120v power is reversed it would do that try switching leads on pigtail to board. make sure to unplug first!
Oct 31, 2013 | American Standard Trane Ge Gas Furnace...
Heating problems: i have an american standard freedom 78 natural gas furnace. The exhaust fan comes on, the ingiter lights up then the main fan comes on but not the burners. I have cleaned the flame...
sounds like you have a good feel for what your doing. do you have a volt meter? if so look for 24 volt at the gas valve just before the glow bar starts to cool down each time. if 24 volt shows then look first for blocked orifices into the burner and next replace the valve. no power to the valve look to the control board
Feb 05, 2011 | General Heating & Cooling
Gas furnance lights but fan does not come on. buzzing sound from panel near is not jammed it spins freely.unit is seven years old.
Most furnaces equipped with an electronic control board activate the same blower speed for heating and continuous fan. If the cooling speed works, the problem is likely in the circuit board (relay) or wiring to the motor. Check and rectify.
Jan 11, 2011 | American Standard Heating & Cooling
Fault code 6 flashes
Well, as you know the blower comes on because there is a control voltage (24V) failure.
I would trace out all the 24V wiring with the schematic to make sure someone didn't cross up a wire.
Then ohm out each component to make sure there is not a bad part in the 24V cycle.
Make sure you have voltage going to the ignitor from the board.
Obviosly the draft inducer motor is working, so thats not the issue. However the pressure switch could be having problems, thus interupting the 24 V cycle.
If you have power to the ignitor, and no ignitor op, then the board is OK. If the board is not sending power to the ignitor, after recieving signal from the pressure switch, then the board is bad.
Make sure the pressure switch is closing, and sending signal to the board.
Jan 19, 2009 | Heating & Cooling
Carrier Heating furnace
either the gas at the outside valve is off, or the gas valve at the furnace may be off, or the switch on top of the gas valve in the furace may be off. if they are all on, then you may not be getting a call for heat from the stat to the furnace control board. check to see if you are getting a 24 volt signal from the stat to the w terminal and common terminal on the furnace board. if you are then check to see if the voltage is arriving as 24 volts to the wires at the gas valve itself . if it is then the gas valve is possibly bad. if it is not then the board is possibly bad.look for loose or broken connections on the low voltage wiring. most unusual that the board does everything else but send power to the gas valve. you need to zero in on the valve i think and start by turning off power and that should restart the sequence of operation and you can observe it step by step . if you are not getting a call for heat then the stat may be bad be sure you are in heat , fan in auto and temp pushed up to max. if no 24 volts is sent to furnace board white and common low voltage board then stat is bad. remove it if you think its faulty and jumper the white and red wires together on the subbase. that duplicates what the stat normally does. if the furnace lights its the stat. having said that i realize the stat has to be sending a heat signal or the other stuff would'nt start. so..... back to the furnace board. check that 24 volts in from stat and 24 out to valve and that will put you on your problem item. good luck
Oct 30, 2008 | Carrier 38BRC048 Air Conditioner
No heat!, light blinks 3 times
Make sure the inducer motor is free of condensation and that all water is able to drain out. Unfortunately your furnace is a lower-grade “builders” model and does not have the same quality of components and workmanship as a Carrier or American Standard furnace. Prior to these failures, It was about 1/2 the price of the units mentioned. And the warranty drops off quickly. You get what you pay for.
Contact Goodman to see if they will cover the cost of your parts at 1-877-254-4729 US only. Their own motto is “Quality Makes the Difference”. It sure does.
Nov 25, 2007 | Goodman GDS81155CNA Open Flame Mid-Size...
Heating & Cooling Logo
360 people viewed this question
Top Heating & Cooling Experts
Paul Carew
Dan Webster
Dan Webster
Tim Whalen