I have a goodman model number pgb024075-1 the light is blinking 2 times that means the end switch is open how do I cheack the venter end switch
SOURCE: goodman gmp075-3 led blinks 5 times
I Also have the same and other problems with my furnace model # GDS80703AXBB. First the LED kept blinking 4 times and I too jumped the primary limit, that didn't kelp. After several attemps I moved the wires going to the circut board and everything starting working again. After a week It stopped working again, so I pulled the plug out of the circut board checked all wires for for a bad connection plugged it back in. Now the LED blinks 6 times again I move the wires. Then the LED blinks 3 times. Then the transformer burns out. I have burned out 2 transformers and I have ordered a new circut board.
Posted on Nov 15, 2008
  • 108 Answers
SOURCE: Goodman: My Power Venter (aka Heat and Draft Inducer) won't start
The power ventor most likely needs to be replaced. But be advised. Goodman normally will not sell parts to anyone but a certified technician. I had to show my masters certificate to buy parts from their outlet. This is a part that has a high rate of failure.
Ray
Posted on Dec 01, 2008
aries_67
SOURCE: 1993 goodman status light 4 times blinking
I have a goodman GMP075-3 that won't turn on. I think it is the pressure switch since I do not have a vent blockage. What is a venter and where can I find it??
Posted on Dec 30, 2008
  • 306 Answers
SOURCE: furnace has does not ignite flame
how often do you replace your filter?
On the limit switch that protects your unit when it gets to hot the number one reason is dirty filter.
The pressure switch is located in the upper side of cabinet has a rubber hose connected to it. They very rarely go out though. So find your vent fan the first fan that comes on and follow the rubber hose to the switch.
Posted on Feb 11, 2009
  • 3250 Answers
SOURCE: my goodman gms80703 has three blinking lights
you can blow through it or put a drill bit down it to clean the conections where the tubes push on
Posted on Feb 28, 2009
Witch blower is running, the inducer or the systems blower?
System blower could mean the the high limit is opening and shutting down the systems gas train, I would check this out first.
The other problem could be with the pressure switch for the gas train, it is supplied from the inducer motor, check to see if it is operating fully.
HSI boards do go from time to time, this sounds more like a system control problem.
Jan 24, 2008 | Goodman GMS90703BXA Heater
Furnace problems
On - OK
1 Blink - Ignition failure. Check Gas flow, gas pressure, gas valve, flame sensor.
2 Blinks - Closed pressure switch. Check pressure switch (stuck in closed position).
3 Blinks - Pressure switch - failre to close. Check venter, pressure switch, vent blockage.
4 Blinks - Open limit switch. Main limit or aux limit are open. (My comment - Means overheating in chamber. Often result of blocked intake air. Bad filter. In my case, plastic wrap had been sucked into the intake. )
6 Blinks - False flame sensed. Check sticking gas valve.
Rapid continuous blinking - Incorrect twinning, incorrect primary polarity. Reverse transformer secondary leads, reverse primary wires.
Closed pressure switch can be from dirty combustion vents, bad chamber pressure - like missing screws, maladjusted gas pressure, failing pressure switch, loose hoses, moisture in the hoses or fan blades The switch need to be closed to ge the unit to work
Jan 23, 2008 | Goodman GMS90703BXA Heater
Goodman gas furnace high limit switch
A volt/ohmmeter is only $3 at a place like Harbor Freight. Goodmans are known for overheating. Often the overheat switch is a one shot item that needs to be replaced every time it throws.
Think if it more like a fuse that melts.
Nov 10, 2011 | Heating & Cooling
My Goodman GMP 125-4 furnace has 4 blinking lights and we currently are unable to get it to come on. What might be wrong?
if this is an error code and you mean that the light blinks 4 times then it is the limit circuit. This could mean either the high limit or a roll out switch is open. the limit switch is right in the center of the furnace above the burner and roll out switches are probably somewhere around the opening of the burner. Follow the wires from the limit to find a roll out switch cause they are in line with each other and the rool out switch could have a button to reset it. However if the roll out is not tripped then you could need to change the limit. Only way to know is to check for continuity.
Dec 04, 2010 | Goodman GDS80904BNA Open Flame Heater
I installed a new goodman unit this past spring. It seems to work ok to good in the day time but the tempature is warmer so we do not need as much heat. At night I know the thermostat is coming on. I...
Heating Mode (Goodman Service Manual)
· The furnace control checks for an open main limit (this
limit is normally closed). If the limit is open, the furnace
will remain inoperable until the limit is closed. During
an open limit the circulating air blower will be
energized. The status light will blink four (4) times.
· The room thermostat reacts to a demand for heat.
· The control will then check to insure that the vent
pressure switch is open. If, at this point, the vent
pressure switch is closed the control will blink two (2)
times and will remain inoperable until this situation is
corrected.
· The venter blower is energized.· The vent pressure switch will close when it detects a
pressure in excess of its setting. If the pressure switch
fails to close the status light will flash three (3) times.
The sequence cannot continue until the pressure switch
closes.
· After a pre-purge of about ten (10) seconds the electronic
ignition device will be energized.
· After a slight delay the gas valve will open.
· The burners will ignite and the flame sensor will detect
the presence of flame. The ignition device will
deenergize. If the sensor does not detect the burner
flame, the gas valve will close and the ignition cycle
will be repeated for a total of three attempts. If, after
the third attempt, the presence of flame is not detected,
the furnace will go into a lockout condition for one (1)
hour. It will then repeat the ignition cycle. This one (1)
hour lockout and retry will occur indefinitely.
· Thirty (30) seconds after the main valve is energized
the circulating air blower will be activated.
· The furnace will remain in operation until the demand
for heat is satisfied.
· Once the demand is satisfied the venter will shut off,
and the circulating air blower will shut off after the field
selectable time off is attained.
· The furnace will remain dormant until the next demand
for heat.
Dec 03, 2010 | Goodman GMS80903BNA Heater
Heat does not work when thermostat calls for heat...
This is a safty limit switch. Find two wires that are going to the inducer or combustion blower that terminates to a small disk about the size of a penny. In the middle of those two wires should be a small button. Push firmly down thus reseting the switch. This should do it. It could also be the pressure switch but I have never heard it called that before. If the first doesn't fix the issue. Remove the small tube that runs from the inducer to a black or silver disk, blow out and draw in air until you hear clicking noises. Sometimes they can become stuck. If that doesn't work, remove the other end of the tube from the pressure switch and blow through it. Sometimes debris can clog the entrance to the pressure switch as well. Hopefully this will solve your problem. You can have a bad limit or a bad pressure switch. In this case you will probably have to call someone out.
Apr 08, 2009 | Goodman Heating & Cooling
Ray
Dec 01, 2008 | Goodman Heating & Cooling
Goodman gmp075-3 led blinks 5 times
Oct 22, 2008 | Goodman GMS90703BXA Heater
Heating & Cooling Logo
197 people viewed this question
Top Heating & Cooling Experts
Paul Carew
Dan Webster
Dan Webster
Tim Whalen