Fault code 6 flashes
I am a heating tech and i am just confussed. Well i think its the board but just looking for a second opinion. Call for heat and the ventor motor starts. after a few seconds the ventor quits and the main blower starts and the fault code states it is reverse wiring, something to do with the ignitor or low voltage. The power comming from the board to the ventor is 120 to ground and 168 volts to neutral. I also have a an amp draw of 10amps at the ventor but if i check the amps at the line wire coming into the furnace i only draw about 1 amp which is normal. I am pretty sure it is the board but i am not used to the american standard furnaces. It is a new american standard stage with reg motor. The main power coming in is good and polarity is good and properly grounded as far as i can see.
  • subzero_hc Jan 20, 2009
    The problem is that the ventor motor starts. and runs for like 5 seconds and shuts off. The voltage to the ventor is 168volts from line to the neutral in the plug connected to the ventor. when you go from line on the plug to ground on the plug you get 120volts. And if i am getting a 10amp amp draw on the ventor and only 1amp on the main power to the board, my experience would tell me there is alot of resistance in the circuts in the board that send power to the ventor. It just seems weird how i am getting 168vost when the power coming in is 120 and 1amps at the ventor and 1 amp overall. ..... i don't think the 24volt side has anything to do with this problem. it would however if the ventor was running longer and the fault code said the pressuse switch was not closing.
    Please explain how the 24volt system would cause the readings i am getting on the 120 side, ie. High amp draw and high voltage. again the ventor motor doesn't even stay running long enough( 5 sec, not even long enough to do a full pre-purge) for the pressure switch and the other compenents in the sequesnce of operation to get a chance to complete. If there were a break or faulty part in that loop the board would flash a different code. The code that is flashing indecates that it could be *a voltage issue, bad grounding, reverse polarity, ingnitor (resistance is good).. These all are properly hooked up. The furnace has been working for a month not and was installed by another contractor. The issue i am wondering about is how i would get 10amps only on the ventor and not on the main power to the board. would these boards sense that there is a high draw/high voltage to the ventor? I think a faulty relay in the board would cause the high amp draw to the ventor. Could it?
  • 334 Answers
Well, as you know the blower comes on because there is a control voltage (24V) failure.
I would trace out all the 24V wiring with the schematic to make sure someone didn't cross up a wire.
Then ohm out each component to make sure there is not a bad part in the 24V cycle.
Make sure you have voltage going to the ignitor from the board.
Obviosly the draft inducer motor is working, so thats not the issue. However the pressure switch could be having problems, thus interupting the 24 V cycle.
If you have power to the ignitor, and no ignitor op, then the board is OK. If the board is not sending power to the ignitor, after recieving signal from the pressure switch, then the board is bad.
Make sure the pressure switch is closing, and sending signal to the board.
Posted on Jan 20, 2009
  • Danny Clark
    Danny Clark Jan 20, 2009
    When you finally figure out what is wrong, and realize that there is indeed a 24V failure somewhere. Please repost here.
    To bad you won't be able to re rate then as well..
  • Danny Clark
    Danny Clark Jan 21, 2009
    Your potentially faulty relay could be the 24 problem I reffered to.
    I can't see how a relay would cause high amp draw, but a bad or restricted motor could.
    The 24 V system probably ISN'T causing the high amp draw. That sounds like a secondary problem to me. However a 24V failure WILL cause the blower to do as you described.
    I'd be looking for two problems not one.
    Personally, I'd jumper out/bypass the pressure switch just long enough to see if the ignitor starts to glow/spark. If it does then obviosly the problem lies with the inducer motor/pressure switch.
    Hypothetically, lets say that for whatever reason the inducer motor is going bad, or is all wrapped up with particlaes of that insulation pad that goes between the housing and mounting plate.
    That would cause a high amp draw right?
    Well then you also have the pressure switch pulling in a little, looks good visibly, but not enought to close the contact. You then have a 24V failure and the system shuts down and the blower motor comes on.
Dacor wall oven
Your tech is making it easy on himself, either he makes bank on the 1300 dollar repair or you back-out and let him off the hook.... Heat/ Temp sensors are nearly universal, so just about any RTD sensor will work in the oven, they are easily replaceable as well. Second, the logic control module is $269.40 at RepairClinic, I would start there- while installing the logic board, pull out the relay board and give it a close look in the daylight to see if any of the solder joints on the back of the board are cracking, burned, or otherwise failing- it is probably fine. Install the logic board and observe operation, the rest of those parts are likely not necessary- your tech sounds like a "Parts Changer Monkey," the old PCM.
Apr 12, 2016 | Dacor EO130SCH Epicure Discovery Wall Oven...
Type 60870 not heating water!Have a wiring giagram for trouble shooting?
Could be: faulty power board (completly or only relay for heating element), faulty wiring between heating element and power board, faulty heating element (interruption, short circuit or current leakage,on some heaters faulty thermal protection).
Depending on the model, the display shows the i60 fault code or the LED end of the program will flash 6 times (only model without display).
Dado
Mar 17, 2015 | AEG 24 in. Favorit 60870M Free-standing...
My Dometic RV AC will not run. It will come on, then almost immediately go off, come on, go off again, most of the time with only seconds between
Error Code E-5 indicates an open or missing temp sensor circuit. Either the remote temp sensor is bad or they didn't plug it in when they changed the circuit board or plugged it in the wrong place.
Mar 16, 2015 | Dometic Heating & Cooling
Vision pro 8000
First check and see if a code of flashing lights on the fan board relay is flashing any number of flashes. If it is count the flashes and refer to owners manual for code of number of flashes for the problem with furnaces air handling problems. If not flashing any codes on the fan relay board I would think the thermostat is the culprit. I have had alot of these newer t-stats go bad as compared to the old mercury t-stats of the days of gone by.I have seen old Honeywell round T-87 stats as old as 60-70 years old still working when removed.
Oct 01, 2017 | Heating & Cooling
I have a Amana unit Model# PGA60C1152F that has a blinking light on the control board it blinks 4 times. That heat will come on then go off but the blower nevers comes on.
look on the inside of the door that you took off and there should be a diagram and on that there will flash code that will tell you what 4 flashes means.i think it is a flame rollout or high limit.
Nov 16, 2012 | Amana Heating & Cooling
The 4th green light on my Ariston dishwasher flashes. What does this mean?
You did not mention what model number that you had but this is what I found after a little digging:
From http://servicetechhelp.com/discus/messages/2801/6823.html?1205974228 :
For future reference, the technician who replaced the control board for me gave me a complete list of flashing LED fault codes for the Ariston LL65 (which are same as Ariston LL64):
001000 Float Switch: Water in Base Pan
001100 No Drain: Dranin Motor Disabled, Filters Clogged, Dramin Hose Blocked
001010 Main Motor Presure Switch Blocked Filter
100100 Control Board: Software of Control Board not Recognized.
000100 Water Valve: Water Valve Diabled <--- This one sounds like your error
000110 Fill Fault: Water Valve Disabled, Turbine Disabled or Control Board
000101 Heating Element disabled or High Limit Open or Control Board
000010 NTC defective or not positioned or control board
000001 NTC defective or not positioned or control board
KEY: 0 = LED off
1 = LED flashing
I also found this for a different model:
http://www.diybanter.com/home-ownership/89945-resetting-controller-ariston-dishwasher.html
No Program Code Fault condition
1 Heavy wash 1000 Operation of flood
protection system
2 Normal wash 0100 Heating
element/Thermistor/Thermostat fault
3 Rapid wash 0010 Drain pump fault or drain
blockage
4 Soak wash 0001 Not filling to correct
level within 6 minutes
Mar 02, 2011 | Dishwashers
We had a new Carrier Weathermaker Infinity Gas Furnace installed in our home on 9-21-99.The Carrier people said the furnace was in good condition this past October.But prior to that as of April 2010 the...
Your Carrier guys more than likely are Carrier dealers. I would get a second opinion. Most qualified HVAC techs can work on any and all brands. It doesn't need to be a Carrier dealer to work on a Carrier. AND, if they replaced the control board and didn't test the heat, that's a fault on their part. Anytime we change a board or even a thermostat, we check ALL modes and functions. SECOND OPINION!!!
Mar 10, 2017 | Heating & Cooling
Armstrong upflow,unit works intermittent problem,call for heat nothing happens,error code of 5 blinks then 6 blinks. i have no manuel, and the panels dont have the codes on them. anyone have access to the...
Armstrong
FAILURE CODES
LED Status Fault Description
Off
No Power to the System Control
Steady Flash (11 or more flashes with no pause)
Normal Operation (Standby or call for heat)
2 Flashes
Pressure Switch Closed When It Should Be Open
3 Flashes
Pressure Switch Stuck Open 30 Seconds or Longer After Call for Heat (System in 5-minute delay mode before next call for heat). On/off switch in "off" position during a call for heat will generate this code.
4 Flashes
Open Limit Switch or Limit Switch Circuit
5 Flashes
Flame Sense Signal Sensed Out of Proper Sequence
6 Flashes - pause - 1 Flash (see Note 1)*
Soft Lockout Type 1 (Failure to light within 4 trials for ignition)
6 Flashes - pause - 2 Flashes (see Notes 1 & 2)*
Soft Lockout Type 2 (Flame sense lost during run)
6 Flashes - pause - 3 Flashes (see Notes 1 & 2)*
Soft Lockout Type 3 (Pressure switch opened during run)
6 Flashes - pause - 4 Flashes (see Notes 1 & 2)*
Soft Lockout Type 4 (Limit or limit circuit opened during run)
6 Flashes - pause - 5 Flashes (see Note 1)*
Soft Lockout Type 5 (Flame has gone away after Error Code 5)
6 Flashes - pause - 7 Flashes (see Note 1)*
Soft Lockout Type 7 (Self-check failure)
10 Flashes* - SV9520H8034 only
Line Input Voltage Polarity Reversed
Dec 12, 2009 | Coleman Heating & Cooling
American Standard Gas furnace acting weird
I am concerned of the readings you have given. 120 volts to ground, but 168 volts to neutral? And having 10 amps of current at the "ventor", but only 1 amp for the whole furnace worries me, because power for the "ventor" comes through the furnace.
You should not have 168 volts to anything! Unless somehow 240 volts is feeding the system, and there is a medium resistance short somewhere.
The controller boards are sensitive to AC polarity (if you will). Neutral should be tied to neutral on the board. You can check that by testing for voltage between the neutral terminal and chassis ground (assuming the chassis is properly grounded.). The hot leg of incoming power, which should be 120 volts, should be connected to the terminal that says 120 VAC.
If your getting 168 volts AC somehow, then something is wrong, and you need to disconnect power from this unit until you find the cause.
As a heat-A/C tech, you should know the sequence of operation for all furnaces is pretty much the same. The boards, while manufactured by different manufacturers, all operate pretty much the same way.
Let me know your findings in reply and I will attempt to help you more.
Jan 20, 2009 | Heating & Cooling
Fault light flashing 1 flash per second
Prior to writing the above fault I had asked the owner to turn the boiler temp controller , for the heating side, down just a fraction . I was phoned this morning to tell me that the boiler had stayed on allnight with no fault light . After consulting with the plumber who fitted the system it appears that there might not be a room stat ,
Nov 30, 2008 | Bosch Water Heaters
Heating & Cooling Logo
225 people viewed this question
Top Heating & Cooling Experts
Paul Carew
Dan Webster
Dan Webster
Tim Whalen