Goodman ar30-1 heat pump
Blower does come on. If i reset the c/b it runs in on but in auto only for a few seconds with heat then turns off.
    Problem Solver:
  • 12 Answers
Check the gas/electric switch on the back of the themostat digital, if not red,green and white call for heat,may be a bad stat
Posted on Jan 21, 2009
Goodman package heatpump blower motor contant running
check your themostat fan mode switch to see if it in on or auto. It should be in auto. If this does not stop indoor fan motor, (it may take up to 2 minutes for the fan to stop, preprogrammed shutoff in the thermostat and fan control cards may make you think the fan has not stopped ) If this does not stop the fan the fan control board in your air handler has a green wire shorting to 24 volt signal in the theromostat wire or the contact on the blower control card is stuck and will need replaced.
Feb 05, 2014 | Goodman Manufacturing Goodman GPH1348H41...
Furnance running all the time never shuts off
Turn the thermostats fan position to Auto instead of ON. If it already is in Auto, then there is a fan relay stuck in the board.
Dec 13, 2013 | Goodman Manufacturing Goodman AEPF313716...
When I turn the system on for cooling, everything sounds likes its running properly, but no air comes out of the house vents. The capacitor is good, fan comes on, coils are getting cold. Could it be the...
Its possible but you might try a little diagnostics first. Put your thermostat in the off position and the fan switch in the auto position. Make sure the switch on the air handler inside is on. Now have someone stand by the blower while you switch the fan switch back and forth from auto to on. If the person at the blower hears a clicking sound from inside the blower cabinet you probably have a bad motor. But if you hear nothing it probably means you don't have power. Check the blower door to make sure its tight and the safety switch is depressed. The wall switch should be tested. Don't have any easy ways to check for power without a volt meter. Hope this helps good luck.
Aug 18, 2013 | Goodman Manufacturing Goodman GPH1530M41...
I have a downdraft Goodman furnace. On only some occasions the blower will start, then after a few seconds I will see the igniter light up, but then I do not get the rush of gas and lighting of the...
It sounds like you got a tough one there.When you say the blower starts up and then the igniter comes on are you refering to induced draft motor or main blower. The proper sequence is for the thermostat to call for heat at which point the induced draft motor should come on and run for 30-45 seconds,then the igniter should heat up for a few seconds then gas valve should open and main burner should light. After limit switch reaches set point for fan on ,blower should come on till after heat has reached thermostat setting then burner should go out, and blower run until fan off setting is reached on limit switch. If your furnace is not following this sequence and then not always doing the same thing in the same order,I would recommend that you change out board again. I have had several problems similar to this with Goodman units and all but one time installing new board solved it. That time I did everything I knew to do and talked to factory service techs repeatedly and finally installed new furnace. As far as your question about insulation,. As long as it is fire proof I can't see where it would hurt anything. Sorry I'm not more help. Good luck and thanks.
Nov 12, 2010 | Goodman GDS80904BNA Open Flame Heater
My 5 ton Goodman Heat Pump won't go into heat or ac mode. Fan won't turn on. No noise from compressor. System is 1 1/2 yeras old.
Easy: Turn the "fan" switch to on at the thermostat and see if the blower starts. If no start, check breaker at breaker box. Check service disconnect at or near the air handler. With the breaker and/or service disconnect OFF check the 3 or 5 amp fuse inside the top cover in the air handler.
Not so easy: (You must know what you are doing for this part or let an HVAC Tech do it for you) Open thermostat and firmly jump the Y and R terminals to see if you get the compressor to start for no more than 30 seconds. (don't do it more than once.) Jump the G and R terminals to see if you get the blower to start. If so, u have a bad thermostat. If not, check the transformer inside the same cover in air handler for proper voltage. (24V. Make sure you also get 220 on the opposite side of the transformer)
If the blower comes on, but the heat pump doesnt start, open the side cover of the heat pump, with the thermostat on cool, and the temp. setting as low as possible for at least 10 minutes see if the contactor is pulled in. If so, check the capacitor and see if it's blown out. Be super careful these systems operate with 220v and the amperes are enough to kill you if you make a simple mistake.
May 20, 2010 | Goodman CLQ36AR49 Air Conditioner
Furnace ignites when thermostat calls for heat, runs for a few minutes and the burners extinguish, repeats... changed flame sensor, nodifference, saw 4 quick red flashes evry few seconds after burners...
You don't say if the blower is coming on, no blower would cause the limit to open. By the way, the limit is internal and auto-reset, not the manual reset roll out switches on the burner assembly.
Jan 11, 2010 | Goodman Heating & Cooling
GMPN 100-4 furnace. Blower motor runs when not calling for heat.
The board is bad. The unit thinks a flame is present, so it tells the blower to come on. Replace the board.
Oct 07, 2009 | Goodman Heating & Cooling
Goodman GMP075-3 ignition problem
bad board,i have had several board failures on goodman
Dec 18, 2008 | Goodman GDS80904BNA Open Flame Heater