I have a weather king furnace and the furnace runs all the time.
After the thermostat was satisfied in the heating mode the blower motor kept running, check stat, blower, circuit board couldn't find cause.
    New Friend:
  • 10 Answers
First check your high limit switch find the white wire coming from your blower moter and unplug it hold down your door switch to see if your furnace will shut off if not replace it and your blower will run for ten to 20 min or until your heater has cooled down.
Posted on Jan 04, 2013
  • 182 Answers
SOURCE: GOODMAN CMA80905CXBA FURNACE. INDUCTION BLOWER
the pressure switch is closed before the draft motor closes it.the board is telling you that this is not right.pull the wire(either) off of the pressure switch to see if furnace tries to light.if it does,you should replace the pressure switch.
Posted on Oct 02, 2008
vanni7
  • 163 Answers
SOURCE: 3 amp fuse blows on a carrier 58mcb furnace board
Hi!!! Does your ac unit work fine?If not check your low voltage problem..You have a low voltage problem check the wire going out to your condensor make sure that they are not touching..Good luck..Check low voltage wires..short in progress..
Posted on Jan 04, 2009
pierre1811
  • 144 Answers
SOURCE: Model 58GS Carreir Furnace blower runs all the time
The blower relay on the circuit board is likely stuck closed. It looks like a black square on the board.
Posted on Jan 17, 2009
  • 4 Answers
SOURCE: Rudd Achiever Plus - Fan runs 24/7
it does sound like a limit switch to me as well. Make sure the fan switch on your thermostat is set to "auto" and not "on"
Posted on Mar 21, 2009
  • 16 Answers
SOURCE: Goodman forced air gas furnace not firing
if your power vent moter is not running you should not have have glowing ignitor.Frist the vent moter must close an air prove switch in series with the idnitor .seems you have a stuck air prove switch.Its the one with a hose attached
Posted on Apr 07, 2009
I have a coleman furnace model 4066A656
Make sure your air filter is clean. Is the thermostat satisfied? or is the room temp. still below the thermostat setting? When ever you have to turn the power off and then back on to a furnace that usually indicates that the furnaces ignition control locked out. The first thing that I would try is cleaning the flame rod.
Mar 02, 2017 | Coleman Heating & Cooling
Trouble shoot Dayton gas furnace model GG9S100C16MP11A fan is left on constant but in cold weather 10 or colder fan will go off and furnace will go thru a restart mode and run fine for awhile then will do...
Do not run contentiously during heat mode. the fan runs at a slower speed with heat and heat fires first then the fan cycles on during heat cycle then when heat satisfies the thermostat the heat will cycle off and fan will run for a couple more minutes and then cycle off. So set stat on fan cycle to auto.
Feb 03, 2015 | Dayton Gas Furnace Heater
I installed a run capacitor for my blower motor on my RUUD ac model UGPH10EBRJR. now it runs all the time. I even disconnected my thermostat and it kept running. is it my thermostat? or something else
An open limit switch may make the fan run all the time. Try disconnecting the Green wire @ the furnace...if that does the trick, then either the thermostat fan relay is stuck, or there is a short between the Red & Green wires somewhere in the thermostat wire.
Jan 18, 2015 | Ruud Heating & Cooling
Have an older Coleman mobile home furnace (Mdl 8665D766). Both blower fan and booster motor work fine; however, during heating, booster motor will keep constantly running after system cycles through
The booster motor? Do you mean the inducer motor that helps push the exhaust? If the inducer motor won't shut off when the thermostat is satisfied and everything else does shut off, it sounds like the contacts on the relay that powers the inducer are at fault
Feb 03, 2018 | Coleman Heating & Cooling
Carrier troubleshooting furnace
If the thermostat isn't selected for "FAN" then the relay is stuck. In heat mode the thermostat opens the gas valve and starts the igniter and the induction motor. If the induction fan isn't running, the flame will stop.
Jan 28, 2014 | Office Equipment & Supplies
WEATHER KING GAS FURNACE . BLOWER MOTOR COMES ON INSTANTLY ON CALL FOR HEAT AND WONT SPARK IGNITE.
You have a high temp safety open. The control board sends a signal through all safeties first. And if there is a safety open, the board believes the unit is overheating, so it engages the blower to cool it down. The safeties are normally on the blower assembly, near the burners, and near the heat exchanger. Hope this helps!
Sep 24, 2017 | Heating & Cooling
I have a Johnson aire ease ultra 90 gas furnance. I also have a outdoor wood furnance that has its own thermostat. On the original thermostat I turn the blower in the on position. I then set the outdoor...
I would first eliminate one furnace from the equation, the exterior wood furnace... turn its tstat down. Will the gas furnace then operate normally? Can you run the blower manually, as in summer mode? Make sure your filters are clean also... that can sometimes overload the blower.
Apr 12, 2017 | Heating & Cooling
I have a weather king model 90RJ - first time I've had hot air heat..When I turn on the heat, the blower turns on right away ( blowing cold air) - I understand that the ducts have to cleared of the cold...
When the furnace first comes on there is a induced draft motor that should come on first but that forces air up the exhaust or flue,not into supply air on ductwork. It is not unusual for cold air to be blown out when burner first turns blower motor on. This should last for a short period of time, no more than a min. or two. You can watch furnace cycle by removing top front cover, I should back up here and ask is this a gas or electric unit. If it is gas you should be able to watch burner flames for a short time before blower comes on. I really need more information so I can try to ascertain what is going on. Wish I could be more help. Thank you.
Nov 12, 2010 | Weather King 10AJA3001AH Air Conditioner
Outside heating unit runs all the time
Usually when the furnace blower motor runs all the time
The limit switch or rollout switch is usually open or bad.
The furnace board is seeing that one of those switches is open, so it brings the blower on to try to get the heat out of the combustion chamber area, so the switch will close. But if the switch is bad and won’t close, the furnace board will keep the blower running continuously.
Feb 19, 2010 | Heating & Cooling
I have a weather king legacy furnace the a/c
means the compressor is directly energised may be some one tried to repair but he jumped the thermostat.
Sep 05, 2009 | Heating & Cooling