Question about York Furnace Draft Inducer Blower Fasco # A224
York 90 gas heater blower keeps coming on and off
Heater comes on but the blower shuts off after 30 seconds and then 15 seconds later it comes back on after 30 seconds it shuts off again . After three tries I get a error code 4 blinks then the heater comes on and the same thing happens all over again.After 10 minutes of this the blower will come on and stay on.I turn the heater down at night and when I turn it up in the morning the same thing happens all over again.
5 Suggested Answers
SOURCE: Blower and ignitor work and then kick off but will
I had the identical problem with my York. Problem was the burners. The heating element would light the first burner but the flame wouldn't move to the other burners. The flame sensor didn't detect a flame on the last burner so the gas valve would shut off. I removed and cleaned the burners then reversed the first and last.
Posted on Dec 17, 2009
  • 3173 Answers
SOURCE: gas furnace
Hi check out the pressure switch clean the air filter and check out the fan control see if this is clean
Posted on Feb 16, 2010
  • 52 Answers
SOURCE: My York Stellar PLUS furnace (Model
Check gas pressure, inspect manifold & make sure there is not a blockage.Make sure gas is present and main gas shut off valve to furnace is on also check the knob on the 24 volt gas valve and see if it is in the on position , check the MV terminal on the gas valve to 24 volt common with a volt tester to see if you have 24 volts present, if you do have 24 volts at gas valve, replace valve. if you do not have 24 volts at gas valve check high limit control & roll out limits for a open circuit, Good luck.
Posted on Mar 04, 2010
  • 39 Answers
SOURCE: i have a York Diamond 90 furnace and when i try to
The furnace is not sensing the flame. Turn off the power.
There is a metal rod in front of the last burner to light. It is corroded and needs to be cleaned. Its the flame sensor .
take the 1 screw out holding it in to the bar and scrub it with some steel wool till shiny. replace and turn on furnace. all should be fine.
Posted on Apr 04, 2010
The heater runs for a few minutes and then it turns itself off it's on stable ground and everything
My furnace keeps shutting off, only runs for about 5-10 mins ...
? 5:19
Dec 15, 2013 - Uploaded by shannon122005
My furnace shuts off before reaching the set temperature on the... and then i turn switch back on , the furnace running about 4-5 hours and then ...
Furnace starts, then shuts off. - Home Improvement ' DSLReports Forums > ... > Home Improvement
Dec 1, 2009 - 30 posts - ‎18 authors
[HVAC] My gas furnace cycles off every 6 minutes. ... This cycle will repeat a fewtimes, then usually after the second or third time everything ... How long is it after the big blower cuts on that the gas shuts off? ... Turn the furnace on, once the inducer blower is running you should read 0 volts (switch is closed).
Jan 03, 2016 | Heating & Cooling
How do i check the limit and fan switches on a williams model 4007732 gas furnace
if you have the f/l combination that look like a rounded dial. it will keep doing that till on a very cold day unit it warn up then you unit should normal
Jan 17, 2015 | Williams Heating & Cooling
Have a Goodman GMT070-3B which the vent motor seems to be sticking. I took apart and cleaned the brushes and reassembled. The furnace will come on only after what seems like the vent motor comes up to...
The whole assembly must be replaced.
The sequence of operation is -
Combustion fan purges the heat exchanger. A pressure switch verifies combustion air fan is running. Usually a 30-45 second purge before the hot surface ignitor glows, or the spark ignition starts.
Gas valve opens after 10-15 seconds and main burners light. Control board monitors for flame and shuts gas valve after 2-3 seconds if main burner does not light.
If burner does not light, some boards repeat this for 3 tries, then locks out and is reset by cycling power.
Air blower comes on after another 30-45 seconds after main burner ignition.
Times may vary based on the specific controller board. A flow chart and timing sequence should be located somewhere on the unit, usually in the fan compartment.
Dec 16, 2009 | Goodman GMS90703BXA Heater
Blower opperation on gas furnace
How long does the burner stay on before the limit takes it out. The board has a delay for the fan in heat and it may be to long. If your unit had cycled on high limit to much it may have a bad limit switch. The limit is so low it cuts out before the fan has a chance to come on. See on the board if has an adjustable time deley. Should 30 60 90 set to thirty. Keep in touch rus
Dec 12, 2009 | Heating & Cooling
I have a goodman gmp100-4 gas furnace and the gas comes on but shuts off in around 30 seconds, then tries again and the same thing... can i get some help please?
On the last gas venturi tube there should be a flame sensor located in the flame to prove it exsists, if its coroded the spark can,t jump back thru the moisture molecues in the gas to prove it has a flame to tell the circuit board to keep the gas comming. Just reomve the flame snsor and sand itand replace itback. T. Y. V. M.!
Dec 01, 2009 | Goodman GMS90703BXA Heater
A 1979 Colman RV furnace. Blower shuts off shortly after burner shuts off leaving a hot heat exchanger. After 15 seconds blower comes on again blows for 10 seconds shuts off comes on in 15 seconds blows...
The fan limiting switch is acting up. It should stay running until lower temp is reached. It will cycle until the temp stays below or at the low setting. Limit switches are adjustable.
Jun 09, 2009 | Coleman Propane Forced Air Heater...
Pentair Heater shuts off prematurely when warming spa
check gas pressure could be running out or overheating
Mar 06, 2009 | Pentair MINIMAX NT TSI IGNITER
I have a problem with my heating system. It is about 10 years old and has had the ignitor, combustion blower motor, and programable thermostat replace in it's lifetime. The system worked great last year....
sounds like its not proofing flame. it has a sensor usually like a needle sticks out into the flame that tells the gas valve the flame lit and is burning so its ok to keep sending gas, if its fails to proof flame then burner shuts down, then it tries to relight 3 times then locks out on fail safe. the blower will sometimes run continually once that occurs to highlight a failed condition. every time you reset it will try again 3 times then shut down. lp gas is very dangerous, even i do not work on it as the gas acts like gasoline and lays around. not like natural gas that disperses well. if you see the flame sensor try gently cleaning it with a little emory cloth. also a loose ground can cause this. check tio be sure any green wires are snug , they actually flow volts to ground through the flame on some to proof, thats why no ground no flame. if that fails then the board is most likely problem. change wire for wire , or get generic replacemant and follow directions exactly. good luck.some ignitors act as a flamre proofer as soon as they are done igniting! rarely do they fail to perform both funtions.
Nov 20, 2008 | Heating & Cooling
Mobile home miller propane gas heater
Sound like the blower motor is burning out. after it has run for a while, shut off the power to your furnace, then fell the motor. if the motor is really hot(be careful) then its starting to burn out. This is a very common symptom of this.
Nov 25, 2007 | Heating & Cooling