Question about Fasco Furnace Draft Inducer Heil Quaker 610672 115V A064
Combustion blower motor starts to run and i have to tap the gas valve to fire off on a heil furnaceit has a gas valve / ign. module in it
Thermostat call for heat and the comb. blower motor starts up then should self ignite but i have to tap on the gas valve to start working
    New Friend:
    Problem Solver:
  • 5 Answers
There is a small hose that verifys vacuum when the fan comes on. Check it and it;s connections for blockage.
Posted on Dec 31, 2012
Heil epm36f19a1 runs but no heat
Fan relay is stuck among other things. The thermostat turns on the combustion air fan and puts power to the spark unit. If the burner comes on after the temperature in the heat exchanger rises the indoor fan will then come on. After the thermostat comes to temperature the power to the gas valve which shuts off the burner. Then after the heat exchanger cools a bit the indoor fan will stop. That's the sequence of events. look at the switches that control the fans. There is a wiring diagram somewhere on one of the panels that access the unit for service.
Mar 06, 2013 | Electronics - Others
No blinks normal running igniter glows gas comes on wont run
Check for 24 volts across the gas valve when Ignitor is glowing. If no, bad board. If yes, bad gas valve or blockage.
On a call for heat, the 24 volt thermostat sends a signal to the control module. The control module will indicate a call for heat with a light on the control either blinking or remain solid depending upon model. The inducer (exhaust) blower will purge all gasses from the furnace and pressurize a pressure switch. Once the pressure switch tells the module to continue, the electronic ignition will energize and send 120 volts to the igniter. The igniter will glow and you will be able to see it if viewed thru the small inspection port. Once the igniter gets hot enough, it sends a signal to the module opening up the gas valve (24 volts). Either a pilot will come on or the burner tube will ignite then spread the flame to all burners. Lastly a safety sensor will be looking for a certain temperature within a few seconds and the furnace will continue to operate and the room air blower will turn on in a minute or two.
What could go wrong? The unit will not run if there is no signal from the thermostat (bad thermostat or broken wire), the control module does not sense a signal from the thermostat (bad control), the inducer does not energize (bad motor), the pressure switch does not close (blocked vent piping, bad switch, plugged condensate hose), the igniter does not energize (bad control, bad igniter), the gas valve does not open or there is no gas (bad gas valve, broken wire, no gas), the pilot does not light (dirty pilot), the burner does not light (bad burner, plugged orifice, not enough combustion air), the flame does not spread to each burner (bad flame spreader, dirty flame spreader, more bad burners), the flame safety sensor does not detect flame (dirty or bad flame spreader, bad flame sensor, broken wire, bad control), or the room air blower does not energize (bad fan motor, bad control).
Mar 05, 2010 | Goodman GMS90703BXA Heater
Glow bar starts, gas valve opens, gas start burning in all four ports, glow bar turns off and gas valve closes. no flame roll-out is it the board bad?
Depending upon how long the burners stay on it could be a bad or dirty flame rod, read on.
Jan 16, 2010 | Goodman Heating & Cooling
My york diamond 80 fans come on and I can see the glow then it fires before cutting off after 5 seconds, is this a bad ignitor
Bad or dirty flame rod or burners.
Jan 09, 2010 | Heating & Cooling
I have an americanaire ultra sx 80 furnace that if it does start up the 1st time, the induction motor continue to run and it will not start
Jan 04, 2010 | Heating & Cooling
Intalled an overhead 130K BTU Mr. Heater last
Dec 01, 2009 | Mr. Heater Heating & Cooling
When I turn my furnace on, the purge blower starts as normal, then after 15 seconds the ignitor starts to glow but when the gas valve should turn on it only turns on for a split second and then you can...
Nov 19, 2009 | Goodman GMS90703BXA Heater
HEIL 80% furnace T-STAT calls for heat, Inducer runs and nothing else happens, Ohm meter reads 4.9 on ignitor. MDL#NTGM100EHA2....Any help with this?
Nov 03, 2009 | Heating & Cooling
Furnace gas valve wont open (roll out switch failure)
Sequence of operation, Gas Furnace.
On a call for heat, the 24 volt thermostat sends a signal to the control module. The control module will indicate a call for heat with a light on the control either blinking or remain solid depending upon model. The inducer (exhaust) blower will purge all gasses from the furnace and pressurize a pressure switch. Once the pressure switch tells the module to continue, the electronic ignition will energize and send 120 volts to the ignitor. The ignitor will glow and you will be able to see it if viewed thru the small inspection port. Once the ignitor gets hot enough, it sends a signal to the module opening up the gas valve (24 volts). Either a pilot will come on or the burner tube will ignite then spread the flame to all burners. Lastly a safety sensor will be looking for a certain temperature within a few seconds and the furnace will continue to operate and the room air blower will turn on in a minute or two.
What could go wrong? The unit will not run if there is no signal from the thermostat (bad thermostat or broken wire), the control module does not sense a signal from the thermostat (bad control), the inducer does not energize (bad motor), the pressure switch does not close (blocked vent piping, bad switch, plugged condensate hose), the ignitor does not energize (bad control, bad ignitor), the gas valve does not open or there is no gas (bad gas valve, broken wire, no gas), the pilot does not lite (dirty pilot), the burner does not lite (bad burner, plugged orifice, not enough combustion air), the flame does not spread to each burner (bad flame spreader, dirty flame spreader, more bad burners), the flame safety sensor does not detect flame (dirty or bad flame spreader, bad flame sensor, broken wire, bad control), or the room air blower does not energize (bad fan motor, bad control).
Most newer furnaces will have a diagnostic center or control built into the control module. You may be able to view it as it is running thru a small viewing port. Some models will require the removal of an access panel prior to finding it. On the reverse of the access panel, there will be a diagnostic chart that will aide you in understanding any error code recorded (usually a blinking light).
This is why we technicians earn the big bucks!
Dec 04, 2008 | Goodman GMS90703BXA Heater
Coleman furnace blower runs continuously
You should be seeing 120 volts to the igniter. Anything less requires either a replacement of the transformer, start relay or control module.
Dec 19, 2007 | Coleman Propane Forced Air Heater...
Fasco Furnace Draft Inducer Heil Quaker 610672 115V A064 Logo