Question about Goodman GDS80904BNA Open Flame Heater
Lockout retries and recycles exceeded - Goodman GDS80904BNA Open Flame Heater
2 Suggested Answers
boanhtgclg
  • 34 Answers
SOURCE: When i turn on my
check to make sure the gas is on and the flu pipe is clear.  does the draft motor come on at all?  if not, you may have a failed control board.
Posted on Nov 30, 2008
Goodman Furnace gms91155dxa not staying on. The system ignites, but shuts off after 3 minutes. 1 blink LED system light
100% sounds like an electrical problem, something is not allowing it to go into a duty cycle.
Dec 04, 2016 | Goodman Heating & Cooling
What is a 1F code on the hayward pool heater
The code you are referring to is actually IF, not 1F. It stands for ignition failure.
If the control exceeds the maximum number of ignition retries or recycles the heater will shut down and go into lockout. Automatic reset is 60 minutes.
Aug 09, 2014 | Hayward Pool & Spa
Why does my hayward heater have a if error code
the code is IF. it stands for ignition failure.
Aug 08, 2014 | Hayward Pool & Spa
Why does my hayward h250fd have and if error code? it is a brand new heater
There are a few reasons that this might be happening. They range from air in the gas line to inadequate gas flow. Start by checking the installation
Aug 08, 2014 | Hayward H250FDN Low NOx Natural Gas Pool...
Trane xv95 converted to propane is on system lockout
worth checking over heat temp sensors (klixon ) sensors can cause heater to go into a cool down purge Through an open circuit heat exchanger (Klixon ) temp sensor Ive seen before good luck
Nov 25, 2017 | Honeywell Electronic Programmable...
There is either a problem with the ignitor or the flame sensor.
Nov 18, 2013 | Honeywell Electronic Programmable...
Amana Air Command 90 furnace LED light blinks 3 times pause 3 times
TRI-COLOR (DSI LED) DIAGNOSTIC TABLE
No. of Red BLINKS
1 Flame sensed when no flame should be present
Verify the gas valve is operating and shutting down properly. Flame in burner assemble should extinguish promptly at the end of the cycle. Check orifices and gas pressure.
2 BLINKS Pressure switch stuck closed/ inducer error
Pressure switch stuck closed. Check switch function, verify inducer is turning off.
3 BLINKS 1st-stage pressure switch stuck open/inducer error
Check pressure switch function and tubing. Verify inducer is turning on the pulling sufficient vacuum to engage switch.
4 BLINKS Open limit switch Verify continuity through rollout switch circuit.
5 BLINKS Open rollout/open fuse detect Verify continuity through rollout switch circuit, check fuse.
6 BLINKS 1st-stage pressure switch cycle lockout If the first stage pressure switch cycles 5 times (open, closed) during one call for heat from the thermostat the control will lockout.Check pressure switch for fluttering, inconsistent closure or poor vacuum pressure.
7 BLINKS External lockout (retries exceeded) Failure to sense flame is often caused by carbon deposits on the
flame sensor, a disconnected or shorted flame sensor lead or a
poorly grounded furnace. Carbon deposits can be cleaned with
emery cloth. Verify sensor is not contacting the burner and is locatedin a good position to sense flame. Check sensor lead for shortingand verify furnace is grounded properly.
8 BLINKS External lockout (ignition recycles
exceeded where flame is established and then lost)Check items for exceeded retries listed above and verify valve is not dropping out allowing flame to be established and then lost.
9 BLINKS Grounding or Reversed polarity Verify the control and furnace are properly grounded. Check and reverse polarity (primary) if incorrect.
10 BLINKS Module gas valve contacts energized
with no call for heat Verify valve is not receiving voltage from a short. If a valve wiring is correct and condition persists, replace module.
11 BLINKS Limit switch open - possible blower
failure overheating limit Possible blower failure, restricted air flow through appliance or duct work. Verify continuity through limit switch circuit and correct overheating cause.
12 BLINKS Module Ignitor contact failure Fault code indicates the module ignitor contacts are not functioning
properly. Replace module.Solid Module - internal fault condition Module contacts for gas valve not operating or processor fault.
Reset control. if condition persists replace module.
3 double 2nd-stage Pressure Switch Stuck Open/Inducer Error
Check pressure switch function and tubing. Verify inducer.
Nov 11, 2013 | Patton Electric Patton PUH680-U Electric...
When i turn on my furance it starts up later it will try again and the system will lockout with one flash on the board indicating retries recycles exceeded any ideals?