Question about Intertherm P3RA-048K Air Conditioner
Weak flame in intertherm furnace
We have a intertherm propane furnace. the yellow light that flashes indicates a weak flame. We have changed the circuit board, sensors, pressure switch, gas valve, and the yellow light still flashes, indicating weak flame. The furnace will ignite, but as soon as blower kicks on the flame goes out. can you give us any ideas as what would be causing this thanks
  • horsejad Jan 19, 2009
    it has an electric ignitor it is on a M1M series intertherm furnace
  • Danny Clark
    Danny Clark May 11, 2010
    What kind of ignitor does it have?
  • 334 Answers
Ok, so we can rule out the ignitor. (standing pilot systems can develop problems that will cause such symptoms.)
Check the gas pressure, make sure you are getting 11 to 14 PSI.
You need that after the regulator all the way to the manifold.
Also check for cracks in the heat exchanger, causing the wind from the blower to distort the flame pattern enough to cause improper contact with the flame sensor.
Make sure the burners and flame channels are clean of rust, and dibri build up, allowing the flame to properly contact the sensors.
Posted on Jan 19, 2009
Furnace won't stay lit. Intertherm Model M2RC-080A-16BN. Ignightor glows, flame starts and after a few seconds the flame shuts off. Then it starts the cycle again. It goes thru this cycle a fe
It sounds like the flame sensor is bad. If thats not the case you may need to replace the control board. You should make sure the flame sensor is directly into the flame.
Nov 20, 2014 | Intertherm Heating & Cooling
Hi :) I have the Trane Furnace that just turn on
on older tranes if 120v power is reversed it would do that try switching leads on pigtail to board. make sure to unplug first!
Oct 31, 2013 | American Standard Trane Ge Gas Furnace...
Intertherm mmha070
Hi, did he bypass the high limit to see if it was bad? Sounds like you are getting false codes and you have a problem in your module or main board, which ever you have. The way it is acting, saying the high limit is open but the tech says its not, I would change the board.
Shastalaker7
Nov 14, 2011 | Intertherm P3RA-048K Air Conditioner
Intertherm Furnace keeps shutting off as soon as it comes on. Model # G5RK072C-12
if its a fossil fuel unit meaning nat gas or propane and it lights then goes out in a few seconds try cleaning the flame sensor take out sensor then rub it gently with steel wool then replace should solve problem
Jan 24, 2011 | Intertherm Heating & Cooling
Meaning of rudd furnace trouble codes
Error Codes
A green LED indicates system faults
Steady On: System OK
Steady OFF: Board control fault or no power applied
1 Flash: Ignition failure (control in one-hour lockout)
2 Flashes: Pressure switch fault, fails open (switch is
stuck open)
3 Flashes: Limit switch open (main or auxiliary)
4 Flashes: Pressure switch fault, fails closed (switch is
stuck closed)
A yellow LED indicates flame status
Steady on: Normal flame is sensed
Flashes: As flame weakens, frequency of LED flashes
increases
Dec 12, 2009 | Heating & Cooling
Intertherm m1m furnace board says low flame yellow lite flashes 3 times Not getting enough heat
The system most likely just needs to be cleaned thouroghly. The burners, orifices, ignition assembly and flame sensors get diry, rusty, and contaminaterd. That causes low gas flow, and improper flame pattern. The othe possiblilty is a cloged or failing gas valve.
Nov 05, 2009 | Heating & Cooling
Intertherm propane furnace makes popping sound when running
It sounds like you have a possible hole in the heat exchanger. Turn the heat off and turn the fan on. If you feel any air coming back out of the heat exchanger, you have a hole. A yellow flame is not a good sign. I would even consider having a service professional come out and take a look.
Apr 05, 2009 | Intertherm P3RA-048K Air Conditioner
I have a goodman GMNT gas furnace Propane it lights off I have a blue flame for about 3 seconds I hear a click on the circuit board and the flame goes out this is doing it constantly. could you please help...
Hi!!! If the flame turns on then off and on then you should change your flame sensor on the gas furnace..YEs flame sensor is shorted..The flame sensor is located by the valve burners it has one wire and is white..Good luck..
Jan 03, 2009 | Heating & Cooling
Heater lights for about 5 sec and then goes out
One flash on a Ruud furnace indicates failure to ignite. There is a viewing port on the furnace where you can watch the flame. If the ignitor is igniting the burner and then 2 or 3 seconds later, the flame goes out; you most likely have a flame sensor that is dirty or not working. Check to make sure you are getting gas. Check the connections of all wires to the control board. If the sensor is not part of the ignitor, see if you can get to it to clean it with a small wire brush. Make sure there is a good ground connection between the board and furnace frame. If the flame is not traveling all the way to the flame sensor, clean your burners. If the flame burns inside the burners, you may have weak gas pressure. Good Luck.
Sep 29, 2007 | Heating & Cooling
Intertherm P3RA-048K Air Conditioner Logo
1,516 people viewed this question
Top Intertherm Heating & Cooling Experts
Dennis Boxerman
Dan Webster
Dan Webster
Bill Long
Are you an Intertherm Heating and Cooling Expert? Answer questions, earn points and help others