Question about Goodman GMS90703BXA Heater
Goodman Furnace Lights But Won't Continue to Run
The ignitor/glow light comes on, the flames/burners light, the glow light goes off and then the burners run for maybe 10-15 seconds and the flames go out. Then the process starts over. What is the most likely trouble spot?
The flame sensor is dirty. You can not see the build up on the sensor but enough build up will change the resistance and the furnace thinks there is no flame.
To clean the sensor, first you need to locate it. it will be a sensor located in the path of one of the flames. Once you locate the sensor, open the bottom panel to turn"off" the furnce. After the panel is removed, unscrew the sensor from the frame above the jets. Use a clean rag and gently wipe the sensor several times. Place back in the cut out and close the lower panel.
The furnace should cycle on and the flame stay on for the normal cycle.
Posted on Jan 18, 2009
Heater does not come on gms80703an
There are too many reasons for this to happen so we would have to narrow it down. The sequence of operation on a Goodman furnace is usually:
1: Inducer draft motor comes on
2: Hot surface ignitor comes on and glows
3: Gas valve opens, lights burners
4: Flame sensor detects flames
5: Blower comes on
If the inducer motor never came on, then you start looking at power to the unit, thermostat issues, or inducer motor issues. Just a few places to start. Hope this helps!
Dec 05, 2013 | Goodman Heating & Cooling
I have a Goodman gas furnance. The furmance kicks on the glow rod lights and then the furnance shuts down after about 60 seconds it goes through the same cycle. The burners never come on. What's wrong?
Let's trouble shoot a few possibilities:
Can you confirm that your gas pressure/ supply is correct-- by lighting all of the range top burners at the same time-- Do they all light quickly, and burn to full height, without much of any yellowing at the flame tips? That should indicate you have god gas pressure and supply.
Now-- in the Oven itself-
When you light the BROIL burner-- does it's glow ignitor light up, and does that burner light off OK?
If it is only the main oven burner that is not lighting, are you able to remove the cover plate that covers it, and watch it light off? -- Any clues on whether or not the gas valve even open?
If NO gas flow, likely you need a new Main Oven Gas Valve-- Probably need to call your Gas Appliance service person.
Let us know if this helped
Mack B
Jan 23, 2011 | Goodman GMS90703BXA Heater
Inductor blower comes on and runs then the ignitor glows flame comes up and burns for approx. 10-15 sec then goes out then fan comes on. Model number is PBKMLB12N0B0F I believe this is a goodman furnace.
I cleaned the sensor that was at the the right further most burner on my Goodman and it worked. got the answer to my problem here at fixya. My burner flame only lasted 5 secs before it shut off. Thanks to all who took the time to send me a response.
Nov 13, 2010 | Goodman Heating & Cooling
No blinks normal running igniter glows gas comes on wont run
Check for 24 volts across the gas valve when Ignitor is glowing. If no, bad board. If yes, bad gas valve or blockage.
On a call for heat, the 24 volt thermostat sends a signal to the control module. The control module will indicate a call for heat with a light on the control either blinking or remain solid depending upon model. The inducer (exhaust) blower will purge all gasses from the furnace and pressurize a pressure switch. Once the pressure switch tells the module to continue, the electronic ignition will energize and send 120 volts to the igniter. The igniter will glow and you will be able to see it if viewed thru the small inspection port. Once the igniter gets hot enough, it sends a signal to the module opening up the gas valve (24 volts). Either a pilot will come on or the burner tube will ignite then spread the flame to all burners. Lastly a safety sensor will be looking for a certain temperature within a few seconds and the furnace will continue to operate and the room air blower will turn on in a minute or two.
What could go wrong? The unit will not run if there is no signal from the thermostat (bad thermostat or broken wire), the control module does not sense a signal from the thermostat (bad control), the inducer does not energize (bad motor), the pressure switch does not close (blocked vent piping, bad switch, plugged condensate hose), the igniter does not energize (bad control, bad igniter), the gas valve does not open or there is no gas (bad gas valve, broken wire, no gas), the pilot does not light (dirty pilot), the burner does not light (bad burner, plugged orifice, not enough combustion air), the flame does not spread to each burner (bad flame spreader, dirty flame spreader, more bad burners), the flame safety sensor does not detect flame (dirty or bad flame spreader, bad flame sensor, broken wire, bad control), or the room air blower does not energize (bad fan motor, bad control).
Mar 05, 2010 | Goodman GMS90703BXA Heater
Furnace tries to light but misfires
Check the air filter.
Feb 26, 2010 | Goodman Heating & Cooling
No Heat Goodman GDS80904BNA
If the hot surface ignitor comes on and fires the burners, and then shuts back down, you need to take a look at the flame sensor. It is a ceramic rod with a metal tip that rests in the pilot flame. When heated from burners, it sends a signal to the main control module, circuit board, which ever this unit is equipped with to keep the burners on. It is a safety to shut the burners down if there is a problem. Take some fine steel wool to clean the metal tip on this and this should take care of the problem. If this does not do it, then 99% of the time you have a faulty control board or module. It will have to be replaced.It is where this flame sensor connects.It will continue to drop out of the circuit, and the fan will start and run. You're T-stat is good or the Hot Surface ignitor would not glow. You will need to take as much info you can from the unit, Goodman and the control, all numbers with you.You can purchase this part at a appliance parts house, or air conditioning parts house. Please keep me informed, I would like to hear back from you. I hope this has given you some direction to follow.Good Luck,
Shastalaker7
Dec 08, 2009 | Goodman GDS80904BNA Open Flame Heater
Hello I have a goodman gas furnace
On a call for heat, the 24 volt thermostat2.gif sends a signal to the control module. The control module will indicate a call for heat with a light on the control either blinking or remain solid depending upon model. The inducer (exhaust) blower will purge all gasses from the furnace and pressurize a pressure switch. Once the pressure switch tells the module to continue, the electronic ignition will energize and send 120 volts to the ignitor. The ignitor will glow and you will be able to see it if viewed thru the small inspection port. Once the ignitor gets hot enough, it sends a signal to the module opening up the gas valve (24 volts). Either a pilot will come on or the burner tube will ignite then spread the flame to all burners. Lastly a safety sensor will be looking for a certain temperature within a few seconds and the furnace will continue to operate and the room air blower will turn on in a minute or two.
What could go wrong? The unit will not run if there is no signal from the thermostat (bad thermostat or broken wire), the control module does not sense a signal from the thermostat (bad control), the inducer does not energize (bad motor), the pressure switch does not close (blocked vent piping, bad switch, plugged condensate hose), the ignitor does not energize (bad control, bad ignitor), the gas valve does not open or there is no gas (bad gas valve, broken wire, no gas), the pilot does not lite (dirty pilot), the burner does not lite (bad burner, plugged orifice, not enough combustion air), the flame does not spread to each burner (bad flame spreader, dirty flame spreader, more bad burners), the flame safety sensor does not detect flame (dirty or bad flame spreader, bad flame sensor, broken wire, bad control), or the room air blower does not energize (bad fan motor, bad control).
Most newer furnaces will have a diagnostic center or control built into the control module. You may be able to view it as it is running thru a small viewing port. Some models will require the removal of an access panel prior to finding it. On the reverse of the access panel, there will be a diagnostic chart that will aide you in understanding any error code recorded (usually a blinking light).
Oct 18, 2009 | Goodman Heating & Cooling
I have a goodman gmpn 100-4 REVB furnace that will not stay lit
If the igniter lights the burners the ignitor..... is not bad. Its like a light bulb.... it works or ot doesn't.
You are describing a dirty flame sensor. Dishonest contractors will sell you a new ignitor but clean the flame sensor when the are installing the ignitor. It is located at the opposite end of the burners than the ignitor. It has one wire going to it. Remove it and clean the rod with a piece of fine grit sandpaper. this should be done every year before heating season.
Good luck
Mar 28, 2009 | Goodman GMS90703BXA Heater
I have a Goodman air heat unit that will not come on.
On a call for heat, the 24 volt thermostat sends a signal to the control module. The control module will indicate a call for heat with a light on the control either blinking or remain solid depending upon model. The inducer (exhaust) blower will purge all gasses from the furnace and pressurize a pressure switch. Once the pressure switch tells the module to continue, the electronic ignition will energize and send 120 volts to the ignitor. The ignitor will glow and you will be able to see it if viewed thru the small inspection port. Once the ignitor gets hot enough, it sends a signal to the module opening up the gas valve (24 volts). Either a pilot will come on or the burner tube will ignite then spread the flame to all burners. Lastly a safety sensor will be looking for a certain temperature within a few seconds and the furnace will continue to operate and the room air blower will turn on in a minute or two.
Jan 27, 2009 | Goodman GMS90703BXA Heater
Goodman furnace blinked 1 time
Furnace attempted to start but failed after so manay tries. This may help you.
Sequence of operation, Gas Furnace.
This is why we technicians earn the big bucks!
Dec 05, 2008 | Goodman GMS90703BXA Heater