Question about Carrier 38CKC042 Air Conditioner
Fan running but no heat
Carrier Furnace Model#40AQ030300BB
Any help is appreciated. Could it be the heat coil or relay?
    Problem Solver:
  • 11 Answers
Most likely heat sequencer. Fan relay will run even if this is out. check if you have continuity in the coils first.
Posted on Feb 14, 2009
    Scholar:
  • 144 Answers
It could be the circuit board, relay, heat strip coil or limit. If you have the fan switch at the t-stat in auto and the fan is running constantly it's probably a high temp limit that tripped. Was your filter clean or dirty? If you had a dirty filter and/or A/C coil it will restrict air flow and cause the furnace to overheat.
Posted on Jan 18, 2009
Why won't my carrier furnace come back on?model number 58rav095.It was running and heating,but makes a horrible noise on start up.Is it the motor going out?
If the noise is coming from the fan coil unit then it could be the blower motor. If the bearings are failing it will make noise on start up and run. But after a period of time it will overheat and the overload protection switch will lock it out to keep it from running until it cools down.
Mar 10, 2015 | Carrier Heating & Cooling
Have a carrier furnace model 58DHC095.it go thru its normal cycle for heat but the fan wont come on until the cycle end and furnace over heats. the fan works on all speeds and I have replaced the cont
There has to be a mechanical thermostat and it is sticking or other wise defective. I don't think that the control board is defective because it finally does turn the fan on. However the mechanical thermostat is there to prevent the fire box temperature from getting too high before the fan starts, but there must also be a over heat thermo disc that will shut the fire off when the fire box gets too high.
Oct 11, 2014 | Heating & Cooling
The line is frozen and the fan will not shut off. How do I turn the fan off?
Shut off the electric to your furnace.
the reason that the line is frozen is because of one two things:
First there is enough air passing over the A coil on your furnace.
Could be dirty filters - closed vents- furnace fan will not run/ stops and starts (bad motor).
Second the charge on your a/c unit is low.
John
Jun 24, 2014 | Carrier XHB123D X/Y Series Heat/Cool Air...
I have a Carrier 58PAV model furnace and the blower is not engaging when I turn either the furnace or AC on. It worked fine last weekend. I have powered the unit off and let it sit for 5 minutes and then...
The only thing you can do at this point is
  1. Hookup a volt meter to the power lines running to the blower motor
  2. Turn the a/c on
  3. You should have voltage on at least 1 wire.
  4. Most motors have multiple speeds so you must check (red - blue - black) wires. My suspicion is that your motor is done.
Jun 26, 2011 | Carrier 38CKC042 Air Conditioner
RHEEM OIL FURNACE MODEL ROBD 067 LBEA BLOWER
You will likely need to install an isolation relay in the W circuit from the thermostat. Some thermostats rob a small current through the W circuit to power the thermostat. This small current can be enough to start the fan circuit timer. You can test this by disconnecting W at the furnace and allowing the timer to shut down. If the fan shuts off with the W disconnected you can install a simple relay.
The relay coil will be connected to Common on one side and the W from the thermostat to the other. Then you will run a wire from R on the furnace to the relay and from the N.O. Contacts to the W terminal on the furnace. This will kill that signal that is starting the timer and the W can steal it's power through the coil back to common.
Dec 23, 2009 | Honeywell Electronic Programmable...
Furnace runs OK, but blower runs again a few seconds later
Could be a defective thermostat in the plenum.
When a gas furnace shuts down the fan(blower) will run until the plenum cools to the safe range. Usually 1 and 1/2 minutes.
Intermittent operation is a defective thermostat or relay.
Mar 11, 2009 | Carrier Heating & Cooling
3 amp fuse blows on a carrier 58mcb furnace board
Hi!!! Does your ac unit work fine?If not check your low voltage problem..You have a low voltage problem check the wire going out to your condensor make sure that they are not touching..Good luck..Check low voltage wires..short in progress..
Jan 04, 2009 | Carrier 52CQ-312-4 Comfort Series Heat...
Air conditioner/furnace squirrel cage fan remains running when th
Ensure you don't have a short in your therm wires. Disconnect them, if the furnace continues to run, you have a lockout problem at your furnace. When the motor on the fan fails, it wont run. Check for led codes on the control board. If you don't have led codes, turn off the power to the furnace at the breaker, and watch the unit. If nothing happens, connect the thermostat. If nothing happens still call for heat. Let the therm run through it's cycle, and if the bower runs continuous again, let me know we can walk through that situation.
Dec 05, 2008 | Ruud Central System Air Conditioner
Model number for Carrier furnace with issue for blower 5 minute off delay
I believe that this model number is for an air conditioner evaporator coil. This unit is probably directly attached to your furnace. The Model number for the furnace will be located in the compartment where the flames can be seen. It will be on a sticker or plate that contains lots of other information too like BTU/h, Volts etc...
The number you gave me gives me this info:
Cased air conditioning evaporator coil.
3 Tons
Horizontal application
Jun 27, 2008 | Carrier 38CKC042 Air Conditioner
Carrier 38CKC042 Air Conditioner Logo
456 people viewed this question
Top Carrier Heating & Cooling Experts
Dan Webster
Dan Webster
Donni Steen
Bill Long
Are you a Carrier Heating and Cooling Expert? Answer questions, earn points and help others