Question about Carrier 38CKC042 Air Conditioner
Model 58GS Carreir Furnace blower runs all the time
I have disconnected the thermostat Red & Green wire and the blower motor still runs when power is applied.
  • George Fann Jan 21, 2009
    I found my problem to be the 24V Control Transformer. It was open.
    Scholar:
  • 144 Answers
The blower relay on the circuit board is likely stuck closed. It looks like a black square on the board.
Posted on Jan 17, 2009
I installed a run capacitor for my blower motor on my RUUD ac model UGPH10EBRJR. now it runs all the time. I even disconnected my thermostat and it kept running. is it my thermostat? or something else
An open limit switch may make the fan run all the time. Try disconnecting the Green wire @ the furnace...if that does the trick, then either the thermostat fan relay is stuck, or there is a short between the Red & Green wires somewhere in the thermostat wire.
Jan 18, 2015 | Ruud Heating & Cooling
Model sf35f furnace wont quit heating after reaching thermostat setting
Sounds like the heat anticipator in your thermostat is either bad or out of adjustment. Turn of the furnace power. Remove the thermostat wires from the thermostat. Turn the power back on. Connect the white and red wires together. The furnace should start up. Let it run a couple of minutes. Then disconnect the wires. The burners should shut off immediately. The blower will continue to run for 60 to 360 seconds then shut off. If this happens replace your thermostat. If the burners continue to burn, then your problem is either the furnace or the thermostat wires.
Sep 12, 2014 | Heating & Cooling
What causes insufficient air flow across evaporator coils
Dirty filters is number one, other blocked ducts.
Bad or slipping blower motor
Slipping belts , if you model has it/ them.
Jul 20, 2014 | Ruud RGTC07ERBGS N/A Achiever 75000 BTU...
Goodman furnace a36-20 fan runs non stop
is green wire from thermostat or from outdoor. retrace and change as needed. If not Goodman has a tech support number you can call while looking at unit.
Jun 21, 2014 | Goodman Heating & Cooling
Bryant furnace
1) Shut power to furnace off, take panels off furnace.
2) Bottom part of furnace find the thermostat wires and make sure they are not touching each other where they connect control boards. You Should see Terminals R,G,W and Y.
3)This is a typical wiring if done by technician.
R=Power-should be red wire
W=Heat-should be white wire
G=Fan-should be green wire
Y=Cool-should be yellow or blue wire.
4) Disconnect the G terminal which is the fan leg and move it out of the way. Turn power on and turn thermostat up. The fan should not turn on until after the burners turn on. The fan should cycle off about 60secs. after the burner turns off.
5) If all of this happens make sure the wires at the thermostat are wired the same at the furnace Red to R and Green to G.
The color of wires you have may be different. But if the same colors are connected at the same terminals at the furnace and the thermostat, that is all that matters.
6) If you recently changed the thermostat, make sure the Rd or R terminal wire is not touching the G terminal wire at the thermostat.
Nov 02, 2013 | Heating & Cooling
I am trying to install a RTH2310 but I do not know where the wires go. Brother in law took old Thermostat off and did not write down where they go. I have a white wire, a red wire and a green wire. Back at...
In most cases, the wires are used as this: Red=Power, White=Heat, Green=Fan/Blower Motor, Yellow=A/C. The other wires, like the one hooked to the yellow will be the condenser wires going outside. The thing I'm not sure on, is that Honeywell Thermostats usually have the terminals marked with R,W,B,G,etc. If it does, then the wires will be as color coded and just hook them back up that way. You can also test to see if those wires are what they are supposed to be by jumping the wires. You can start with red since that is supposed to be your 24v power. Jumper red and green, you should get the blower motor on, jumper the red and white, you should get the heat to come on. Same goes for a/c as explained above. Any other questions, I will be glad to help.
Jan 23, 2010 | Honeywell Focus 6300B 5-2 Days...
I have a coleman Evcon model AH16-0 . I am
Typical Thermostat Wiring for 4 or 5 wire Heat/Cool Thermostat (not heat pumps)
4 Wire Termostat
R = Red One Side of 24 volt Transformer
G = Green Blower
Y = Yellow Cool
W = White Heat
5 Wire Thermostat
with one transformer for both units
Rc One Side of 24 volt Transformer
Rh Jumper Rc to Rh
G = Green Blower
Y = Yellow Cool
W = White Heat
5 Wire Thermostat
With 2 transformers one for indoor unit
And one for outdoor unit
Rc = Red One Side of (outside) 24 volt (outside transformer)
G = Green Blower (outside transformer)
Y = Yellow Cool (outside transformer)
Rh = Blue One side of (inside) 24 volt (inside transformer)
W = White Heat (inside transformer)
COOLING ONLY Thermostat
G = Green Blower
Y = Yellow Cool
HEATING ONLY
R or Rh One Side of 24 volt Transformer
W = White Heat
Jan 06, 2010 | Heating & Cooling
Ruud furnace Model URKA A030jK08 Code opt 589
Flip the lower panel over and look for a wiring diagram. On that diagram there will be a diagnostic chart. Let me know what 5 blinks represent. Then I want you to read on.
On a call for heat, the 24 volt thermostat sends a signal to the control module. The control module will indicate a call for heat with a light on the control either blinking or remain solid depending upon model. The inducer (exhaust) blower will purge all gasses from the furnace and pressurize a pressure switch. Once the pressure switch tells the module to continue, the electronic ignition will energize and send 120 volts to the igniter. The igniter will glow and you will be able to see it if viewed thru the small inspection port. Once the igniter gets hot enough, it sends a signal to the module opening up the gas valve (24 volts). Either a pilot will come on or the burner tube will ignite then spread the flame to all burners. Lastly a safety sensor will be looking for a certain temperature within a few seconds and the furnace will continue to operate and the room air blower will turn on in a minute or two.
What could go wrong? The unit will not run if there is no signal from the thermostat (bad thermostat or broken wire), the control module does not sense a signal from the thermostat (bad control), the inducer does not energize (bad motor), the pressure switch does not close (blocked vent piping, bad switch, plugged condensate hose), the igniter does not energize (bad control, bad igniter), the gas valve does not open or there is no gas (bad gas valve, broken wire, no gas), the pilot does not light (dirty pilot), the burner does not light (bad burner, plugged orifice, not enough combustion air), the flame does not spread to each burner (bad flame spreader, dirty flame spreader, more bad burners), the flame safety sensor does not detect flame (dirty or bad flame spreader, bad flame sensor, broken wire, bad control), or the room air blower does not energize (bad fan motor, bad control).
Nov 23, 2009 | Heating & Cooling
What's the deal? Wont shut off or respond to thermostat. . .
Red= power........White=heat.............Green=fan.................(grey)-(yellow)=cool .....these are the connectons. Disconnect these wires from the thermostat and know that red/power is the only wire that send power to the thermostat, and the rest sends it back to the unit to call for whatever,, red--to . white for heat... red to green for fan .... &red to grey for cool! OK! Turn all your power on, and use a jumper wire from red / green for fan and see if the fan comes on! Then move the jumper wire from red to green , to red / to white for heat and the fan , wait for 3 minutes before removing and going to the next step. Then red /to grey for cool and check if the outside comes on. Either you have a wire touching past the insulations and making a connection, a bad thermostat ,oe excessive wire lead touching the next connection.Thank you very much!
Nov 05, 2008 | Intertherm Heating & Cooling
Furnace blower motor
I would check the "G" wire at the Thermostat and make sure that it has a solid connection. The other end screws on to a terminal in the furnace. Check this connection as well. This green(G) wire is what activates the 120v relay on the circuit board. You can test this by turning the thermostat to the off position and then jumping the 24v R terminal with the 24v G terminal at the furnace. if the fan comes on then the problem is in the thermostat wire or the thermostat itself.
Jul 08, 2008 | Goodman GMS90703BXA Heater
Carrier 38CKC042 Air Conditioner Logo
265 people viewed this question
Top Carrier Heating & Cooling Experts
Dan Webster
Dan Webster
Donni Steen
Bill Long
Are you a Carrier Heating and Cooling Expert? Answer questions, earn points and help others