We just replaced the inducer blower motor unit on above model. Then water kept getting trapped in the pressure switch tube, which the repair man came out and put the pressure switch up higher, everything was working well until this morning. You can hear the blower motor running, and the air going through, but he furnace wont kick on and run. What else could be going on?
  • Anonymous May 07, 2009
    My problem is that the condesate pump is leaking and water is pooling up around the panel on/off control button and shuting off the power. Do I need a new conensate pump
    Problem Solver:
  • 4 Answers
Water should never reach the nipple for the pressure switch tubing on the IDM. Check the entire condensate drain system for obstructions. Verify water makes it from the furnace location to the outside drain. Flush p-traps and any anti-siphon devices thoroughly.
Posted on Apr 07, 2009
Need to find a replacement part
Here you go Angela
1149097 Draft Inducer Assembly - AllParts Heating
www.allpartsheating.com/1149097.html
  1. Cached
  2. Similar
Draft Inducer. 1149097 draft inducer for Heil, Tempstar, Arcoaire, Whirlpool & Comfortmaker brand model furnaces. This part replaces old part number 1008416.
Arcoaire Furnace Motor Parts: Fast Shipping RepairClinic.com
www.repairclinic.com/Shop-For-Parts/a36b389c53/Arcoaire-Furnace-Motor-Parts
  1. Cached
  2. Similar
Furnace draft inducer assembly. The draft inducer motor draws air into the burner and exhausts it out the flue. If the draft inducer motor is defective, the furnace ...
Arcoaire Furnace Parts: Fast Shipping RepairClinic.com
https://www.repairclinic.com/Shop-For-Parts/a36b389/Arcoaire-Furnace-Parts
  1. Cached
Direct Factory Replacement Inducer Blower Motor Used in 90 ...
www.americanhvacparts.com > ... > Oem Direct Replacement Models > Arco Aire
  1. Cached
  2. Similar
Direct Factory Replacement Inducer Blower Motor Used in 90% Furnaces. ... Comfortmaker, Intercity Products Snyder-General, Heil, Tempstar, Arcoaire Draft Inducer Blower Motor. ... Used in ICP Equipment Models: ... GUH125A016CIN
1149097 - Arcoaire Furnace Draft Inducer / Exhaust Vent Venter Motor ...
https://www.amazon.com/1149097-Arcoaire-Furnace-Inducer.../dp/B00FFBQRGA
  1. Cached
1149097 - Arcoaire Furnace Draft Inducer / Exhaust Vent Venter Motor - Fasco Replacement: Replacement Household Furnace Motors: Amazon.com: Industrial ... Draft inducer motor for arcoaire model guh125a016cin Google Search
Nov 27, 2016 | Heating & Cooling
Amana model ACS4250A (slide in). How do I remove the front panel?
[PDF]80-90 FURNACE SERVICE MANUAL.pdf - Johnstone Supply
johnstonesupply9.com/.../Amana/Gas%20Furnaces/GCCA%20Gas%20Fu...
Instructions. This manual is to be used by qualified HVAC technicians only. Amana .... Gas Furnace Upflow/Horizontal Induced Draft A Air Command 80 SSE.
Nov 06, 2015 | Kitchen Ranges
Model m1mc 090a bw furnace pressure switch open. inducer motor is pulling .45 w.c . the intake pipe above inducer is only pulling .1 w.c. . checked for venting and intake blockages found non. removed...
did you check the hose from the inducer to the pressure switch? HAVE you unplugged the unit from the wall outlet to reset the board? DO you have a voltmeter? If you do you can run voltage across the switch and if you get 24 volts you are open.
Oct 23, 2013 | Coleman Intertherm Nordyne Miller Furnace...
Bryant Plus 90 Furnace - Blower works fine and intermittently blows warm air but will not bring house to temp set on thermostat... Get a 1-3 error (one blink and then 3 quick blinks of the LED) Thanks
PRSSURE, DRAFT SAFGUARD, AUX-LIMIT SWITCH(WHEN USED)OR BLOCKED VENT
SWITCH(WHEN USED) DID NOT CLOSE OR REOPENED (DOWNFLOWONLY)
If open longer than five minutes, inducer shuts off for 15 minutes
before retry.
Check for:
* proper vent sizing
* defective inducer motor
* restricted vent
* excessive wind
* low inducer voltage(115VAC)
* defective blower motor or capacitor
* defective pressure switch
* inadequate combusstion air supply
* disconnected or obstructed pressure tubing
If it opens after trial for ignition period, blower will come on for
90 sec. recycle delay.
Check your air filter for blockage, check pressure switch for a buildup of moisture. Make sure your inducer motor is turning and creating a vacuum to the pressure switch. Make sure all venting is clear and free of water or debris. Make sure there is no water in inducer motor and all drains are draining.
Jan 28, 2010 | Heating & Cooling
Amana 90% model #GUCAO45AX30 SER# 0109143635 UNIT MAIN BURNERS LIGHT UP THEN SHUT DOWN IN A FEW SECONDS. DRAIN LINES ARE CLEAR, VENT PIPE CLEAR OF CONDENSATION. I BYPASSED T-STAT JUMPERED R-W NO HELP,...
check to see if the flame rod tip is in the flame(like the hot junction on a thermocouple). the pressure switches are a normally closed switch and a blocked flue could cause them to open. the circuit board should run through the safety switches and check them before the gas is opened at the valve. also the drain lines that you see at the inducer fan should be free of condensation but if the inducer fan has condensation in it, it will open the airflow safety switch. you will hear the crackling noise from the fan. also there should be a trap below the fan that should be full of water to keep the fan from pulling air from the wrong place. I would not suspect the board at this point
Dec 13, 2009 | Amana PTC074B25AE Electric Heat Air...
Induced Draft Blower Not Blowing- 3 Blinks on LED
Your doing well just right. When the call for heat is on the draft motor gets a call from the board to come on. When this happens if no voltage is present at the motor then you ahve abad baord. Replace it.
Nov 28, 2009 | Heating & Cooling
Noisy Amana furnace
Remove the flue pipe from the top of the induced draft motor. Check to see if there any obstructions in it. If so remove them. If not replace the motor assembly.
Jan 02, 2009 | Honeywell Power Humidifier: Furnace...
Furnace dont have heat
pressure switch stuck take off hose **** on it then put back on
Dec 21, 2008 | Amana PTC153B35AE Air Conditioner
I have 15 year old Amana horisontal furnace model gsc075a30a. it was working fine till the exhaust fan cracked and needed replacing. I have done that and the fan works good but I had to bypass the...
If there are markings on the pressure switch as to what pressure it closes at, you may be able to substitute another brand pressure switch. Amana is made by Goodman. Maybe you can cross reference the switch with a Goodman distributor. Try Amana parts at 1-407-699-5411.
Nov 25, 2008 | Amana Heating & Cooling