Question about Honeywell Programmable Thermostat Heater
The thermostat turns the heating unit off and the fan continues
The Thermostat model no. is TH3110D1008-0610
If I turn the thermostat to the off position for about 2 to 4 hours and turn it back on after that time, it performs nornal for several hours. Then the furnace goes of and the blower keeps blowing cold air. HELP
    Scholar:
    New Friend:
  • 70 Answers
Check your furnace filter to make sure the furnace is not over heating. what brand of furnace do you have and how old is it?Have you changed filter to a different kind last time you changed it?
Posted on Jan 17, 2009
I upgraded my thermostat to a digital one. when i removedd the old one only the red and white wires were used. i also replaced the thermostat wires. i hooked up all the wires according to color red to r,...
As your unit had just 2 wires, Red and White, you had just heat only with no AC and no fan on as described as you have no green circuit wired up at the furnace or thermostat, you can add a relay if not equipped but that would make your unit very old.
Oct 19, 2013 | Heating & Cooling
Have installed a new Honeywell thermostat. The fan does not turn off even when the room has reached the desired temperature. I originally replaced th ethermostat because the old one the fan ran forever and...
Most T-Stats have a On / Auto on a forced air system. On means the fan will run all the time even if it is not calling for heat. Auto only runs when calling for heat. Does the fan turn off in the auto mode at all? To test it...BE SURE THE FAN IS IN THE AUTO MODE ON THE T-STAT... Turn the thermostat all the way down and keep it there for appox 15 mins. If it is wired properly and the fan limit is set properly the fan should turn off. If it doesn't it is not the thermostat were the problem lies.
Most forced air units have a fan / high limit switch. There is a setting on the switch for the fan to turn on and a setting for the fan to turn off or it has a setting and a differental switch for it to turn off/on. Example - the fan comes on when the temp in the heat exchanger reaches 110 degrees F and will shut down at 95 degrees F after the thermostat is satified...this would hav a differental of 15 degrees F. It may be set to low and the fan continues to run long after all of the heat has been removed from the heat exchanger. This in turn will cause cool air to be coming out of the registers.
Mar 09, 2011 | Honeywell CT87B ROUND HEATING&COOLING...
Blower does not work and heating element heat with
Check for power to the unit. If power exists, check your low voltage. Do you have 24volts to R & C at your thermostat?
Feb 07, 2010 | Goodman GMS90703BXA Heater
Rheem Heat Pump outside fan seems to be running 24 hours per day. Outside temp 23 degrees. Is this normal? Model #RPKA-018JAZ
no this is not normal. the fan should stop running when the thermostat is satisfied or when the heat pump goes into defrost mode. if it is running nonstop, there is a contactor that operates the fan and compressor that if it sticks will get line voltage to it. you would have to take the cover off of the outside unit and turn the thermostat to off. If the fan continues to run, you need a new contactor.
Jan 13, 2010 | Heating & Cooling
I have an intertherm electric furnace FEH-A020, with multispeed blower installed when A/C added. My problem is blower operation. at the end of the cooling season with fan set to auto operation the fan ran...
The model of T-stat you gave comes up as a discontinued model on Honeywell's web site, but it looks to be a manual stat that type of stat would have to be wired with a summer winter switch with electric heat, allowing it to turn on the fan with a call for heat. If yours is a programmable T-stat you would need to select electric heat or in the installers set up change the default setting for fan from unit controls fan in heat to thermostat controls fan.
Oct 17, 2009 | Intertherm P3RA-048K Air Conditioner
My ducted heating continually blows cold air thru
Well, if need be, turn the breaker off. Turn it on when you need heat. Sounds like the fan relay is sticking or something if that sort. Is the tstat fan selector on auto?
Jun 17, 2017 | Heating & Cooling
Rheem heat pump. blower will not turn off
The fans are set to delay for 60-90 seconds to remove all heat from the heat exchanger/heater elements.
If the fan runs any longer than 3-4 minutes after the Emergency Heat shuts off, you may have a bad sequencing relay in the air handler.
Jan 27, 2009 | Heating & Cooling
Honeywell Thermostat
Make sure G from indoor unit goes to G on thermostat for fan continous fan, if that doesn't work and you have 24 volts to R and C then the t'stat is bad.
For 2nd stage heat or aux.heat, on the indoor unit you need to make sure the wire W2 from the indoor unit goes to W2 on t'stat.
You don't need any wires from W1on the indoor unit to W1 at the t'stat because with a York heat pump Y1 is the contactor which turns the compressor on and you will get 1st stage heat, and for cooling the t'stat will also bring on O which is the (reversing valve) or cooling changeover relay for the cooling mode.
C = common usually black wire
R = hot usually red wire
Y or Y1 = contactor
W1 = 1st stage heat not needed for heat pump
W2 = Aux. heat indoor heat
G = fan
O = Cooling changeover relay
B = Heating changeover relay
L = System monitor
E = Emergency heat relay
Dec 23, 2008 | Honeywell Electronic Programmable...
Hunter 44630 thermostat
Here is a link that will have wiring diagram it is for a similar model hunter. Also check your dip switch on the back of the stat to ensure it is set for gas (HG) or electric heat (HE) depending on your type of unit. Good Luck. Rule of thumb for most four wire systems is RED (power to stat) Yellow (Cooling) Green (Fan) White (heat)
Jan 12, 2008 | Hunter Fan Company 5/1/1 Programmable...
Air Conditioner malfunction
Hi, Sounds like you have a short in the control circuit to me. Turn off all power going to the unit. Write down or otherwise mark the wires leaving the control board going to the thermostat. Remove them from the control board. Replace the fuse. Turn power back on and see if the fan still runs. If it does, check and or replace the heat limit switch that brings the fan on during the heat cycle. It may just need adjusted. If the fuse blows, I would think that the control board is probably bad. If it doesn't blow, Remove the thermostat. Leaving all thermostat wires open check them with an Ohm meter. There should be no continuity between them. Twist all the wires together at one end and ohm them again at the other end. You should have complete continuity on all wires. If the wiring checks out, down power the unit. Double check your wire colors and rewire the control board. With all wires open at the thermostat, turn the power back on. Touch the RED wire to the YELLOW wire. The Condensing unit should come on. Touch the RED wire to the GREEN wire. The fan should come on. Touch the RED wire to the WHITE wire. The heat should come on. Down power the unit. Replace the thermostat. Test unit. If the fuse has lasted ok but blows now it is either wired wrong at the Thermostat or the thermostat is bad. I hope I have helped. NOTE: If you can not understand these instructions. Call a licensed Heating / Air conditioning company. kstfas
Sep 23, 2007 | Heating & Cooling
Heating & Cooling Logo
224 people viewed this question
Top Honeywell Heating & Cooling Experts
Bill Long
Paul Carew
vance jones
Are you a Honeywell Heating and Cooling Expert? Answer questions, earn points and help others