Goodman GMP 050-3 furnace runs well for 3 to 4 minutes then flame and gas shut down for 30 seconds then it cycles all over again, I cleaned the sensor seemed to work then ran through the same cycle as mentioned after one full cycle.
Try cleaning of the flame sensor infront of the flame comes out. carefull its fragile
Posted on Jan 16, 2009
Furnace was working fine and just stopped working...it reacts to raising the thermostat but doesnt actually flame on
This is probably a ignitor.
1. Thermostat calls for heat. 2. Draft inducer motor starts. 3. Pressure switch attached by a small plastic or rubber tube senses the negative pressure produced by the draft inducer and closes. 4. Draft inducer runs for 30 seconds to a minute before you hear a gas hissing sound. The ignitor did not glow, the flame sensor (a small metal probe about 1/8" in diameter, with a white porcelain base) does not sense the flame, so after 8 to 10 seconds the hissing sounds stops with no ignition of gas to heat your home. Your furnace shuts down and goes into a lock out condition until you turn your power switch back off and on again. Then the sequence starts all over again with no ignition of the gas. Solution:You probably need to purchase and install a new ignitor. I would suggest that you inspect your ignitor closely for cracks.Make sure you do not touch the ignitor with your bare hands. If you do not visually see a crack, then you could have a furnace control board problem or a limit, rollout switch problem. Please see "limits, rollout switches & furnace control boards" further down on this page. The furnace's control board might not be supplying the voltage to the ignitor. If your furnace lights and the gas stays on for 8 to 10 seconds, then shuts right back off, then you need to clean your flame sensor with light sand paper or steel wool. You might need a new flame sensor, but most of the time they can be cleaned an will work well after cleaning.
Please leave feedback... Thanks...
Jan 28, 2011 | Goodman GMS90703BXA Heater
The Goodman Heater was installed in 2004. Thermostat set at 75F, the fan that blows CO2 out was on for about 1 minute, then I could hear the sound of the gas blowing into the furnace, but the ignitor...
Problem: Your furnace will not ignite the gas to produce heat for your home. When a furnace has a bad ignitor what I see most of the time is the following sequence of operation:
1. Thermostat calls for heat. 2. Draft inducer motor starts. 3. Pressure switch attached by a small plastic or rubber tube senses the negative pressure produced by the draft inducer and closes. 4. Draft inducer runs for 30 seconds to a minute before you hear a gas hissing sound. The ignitor did not glow, the flame sensor (a small metal probe about 1/8" in diameter, with a white porcelain base) does not sense the flame, so after 8 to 10 seconds the hissing sounds stops with no ignition of gas to heat your home. Your furnace shuts down and goes into a lock out condition until you turn your power switch back off and on again. Then the sequence starts all over again with no ignition of the gas. Solution:You probably need to purchase and install a new ignitor. I would suggest that you inspect your ignitor closely for cracks. Make sure you do not touch the ignitor with your bare hands. If you do not visually see a crack, then you could have a furnace control board problem or a limit, rollout switch problem. The furnace's control board might not be supplying the voltage to the ignitor. If your furnace lights and the gas stays on for 8 to 10 seconds, then shuts right back off, then you need to clean your flame sensor with light sand paper or steel wool. You might need a new flame sensor, but most of the time they can be cleaned an will work well after cleaning.
Nov 30, 2010 | Goodman GMS80903BNA Heater
Goodman GMP Furnace problem. Original problem is
Good one! Is the flame getting to the flame sensor within the few seconds? Maybe a good cleaning of the burners or flame tray would help. 1.3 ma is enough for the flame rod to tell the board to stay on. Re-do all the ground connections both at the board and furnace cabinet to be safe. Check the polarity of the power going to the furnace. What are the chances the second board is bad?
Jan 15, 2010 | Goodman Heating & Cooling
Model #GMPN100-4 Goodman furnace. Vent fan
The sequence of events for furnace operation is -
Fan purge for 30-45 seconds. During this time, a pressure switch is actuated by the running of the purge fan, proving the control board the purge fan is running.
After purge and purge prove, the hot surface ignition and or spark begins. After a few second delay, the gas valve will open. The control board then monitors for flame prove through another sensor located near the burners. If there is no flame within 3-5 seconds, the gas valve closes. It will repeat this process, usually 3 times, before it shuts the system down, which requires a power down of the system to reset.
I have seen trash get into the hose between the purge blower and the purge switch. But you could be having other problems.
Dec 17, 2009 | Goodman Heating & Cooling
Goodman gmp075-3 gas furnace and the flame cycles for 4 sec
JUST SAND THE FLAME SENSOR LOCATED IN FRONT OF THE LAST GAS PORT.
Dec 02, 2009 | Goodman GMS90703BXA Heater
I have a goodman gmp100-4 gas furnace and the gas comes on but shuts off in around 30 seconds, then tries again and the same thing... can i get some help please?
On the last gas venturi tube there should be a flame sensor located in the flame to prove it exsists, if its coroded the spark can,t jump back thru the moisture molecues in the gas to prove it has a flame to tell the circuit board to keep the gas comming. Just reomve the flame snsor and sand itand replace itback. T. Y. V. M.!
Dec 01, 2009 | Goodman GMS90703BXA Heater
Furnace starts properly, then shuts down, led flashes 8 times
The first thing to look at is the flame sense rod.
Shut off power to the furnace, remove, clean sensor with steel wool or sandpaper then reinstall the sensor. Reapply power and it should run properly.
Jan 10, 2009 | Goodman GMS90703BXA Heater
Goodman Furnace GMP 050-03
You need to check for 24 volts across the gas valve as the ignitor glows. If you get it, it is a bad gas valve. If there is no voltage or strange voltage, replace the control board.
Dec 09, 2008 | Goodman GMS90703BXA Heater