Question about Goodman GMS90703BXA Heater
Main burner will not ignite Tempstar(NTC5075BFD1)
When my furnace tries to turn on, the pilot light will light but the main burner will not ignite unless I blow lightly towards the pilot light to help it out.
  • Goodman Master
  • 2,840 Answers
Try cleaning the pilot oriffice it sounds like the flame is weak
Posted on Jan 17, 2009
PILOT LIGHT COMES ON BUT WHEN YOU TURN THE KNOB TO ON IT DOES NOT LIGHT UP THE CIRCLE PLATE IN THE HEATER. IT JUMPS AND THE FIRE COMES OUT THEN IT GOES OUT.
I'm not sure what unit you are troubleshooting but if the main burner is igniting and that main burner flame is blowing out the pilot flame, it's possible the pilot flame orifice needs to be cleaned. The orifice can get stopped up and produce a weak pilot. And I've seen a pilot lite, but be blown out by the combustion of the main burner igniting. Now you stated IT JUMPS. If you mean the pilot flame jumps, as if it gets large then weak and goes out, then the gas valve is giving you trouble and may need to be replaced.
Mar 09, 2017 | Heating & Cooling
How do I light pilot light?
There should not be a pilot on a direct vent furnace. When you turn up the thermostat for heat the 1st thing to happen is a venter motor should start, it should vent for approximately 45 seconds, the air switch will verify a vacuum in the burner box, then a spark igniter should start clicking to start the pilot, then the flame rod will verify the pilot, the igniter will stop clicking, and the main burner will ignite and remain on until the thermostat has satisfied the set point. These guideline steps must be satisfied before the controller advances to the next step. The 1st step is the venter motor running, sometimes the motor will stick over the summer months, spin it manually to unstick it. PS, nothing runs if the fan door cover is open, as that shuts down the power to the whole furnace.
Oct 02, 2015 | Coleman Gas Fired Mobile Home Furnace,...
When I try to use my Thermolaire model SU402E, the pilot lights( and stays lit), but the main burner will NOT ignite.. any suggestions as to what could cause this if the pilot stays lit?
Bad igniter? When you 1st try it the gas valve will give enough gas that you would get the burner lit if the igniter was glowing red. If you're desperate you can light the igniter area w/ an aim n flame, but you definitely want to do that w/ caution and crank up your t-stat so the furnace stays on awhile Cuz you'll have to do it again for heat or buy an igniter($40 or so)
Jan 14, 2015 | Heating & Cooling
Old anthes gas furnace with pilot light. burners will not light.blows cold air
Have to think that the thermocouple has failed if the pilot is on but the furnace main burner doesn't ignite
Apr 05, 2014 | Cozy (W352E) Heater
Gas wall furnace pilot goes out when burner turns off.
When the main burner turns off, does it make a whoosh or pop? If so, this would be the issue causing the pilot to be disturbed. And have you tried to adjust the pilot/thermopile strength, if possible? A stronger pilot may help. Now if the main burner slowly goes out, and the pilot also slowly goes out, and also slow to ignite, and you've replaced about everything else, it may be the gas valve itself that has/is giving up. Gas is impure and causes a sticky residue. And if the main burner is "slow to act", this tells me the piston that's inside the valve is slowly opening or closing, and may be the reason the pilot is acting up. Make sure you check the outlet to your flue pipe also for obstructions. If the unit doesn't vent properly it can have more heat in the flue. That heat can have a downward rush when the burner goes out, kinda like forcing air through a clogged tube. And when you quit forcing the air, some of it comes back at you. Before condemning the valve try to check all else as you have done with the thermopile and such. Please work safe and I hope this helps.
Oct 09, 2017 | Williams Heating & Cooling
Janitrol GUPS075-3 Furnace burners will not stay lit
The first thing I would do is make sure the flame sensor is clean, this is a metal rod immersed in the burner flame on the opposite side of the igniter. If too much oxidation builds up on it, it will not allow the burner to stay lit. To clean, just turn off furnace and remove flame sensor and clean with steel wool and then reinstall. If this does not solve the problem there may be a problem with the gas valve.
Nov 08, 2012 | Heating & Cooling
My heil furnance comes on but no hot air or air at all
see this causes and fix it. God bless you
o light the pilot on a standing-pilot (always on) ignition system, follow the lighting instructions located near the control. Otherwise, try these steps: Light the pilot:
  1. gasfurnace1.jpg Press and hold the pilot control knob to start the pilot. Set the control knob to the pilot position. Hold a long match under the pilot gas port.
  2. Press the control knob; the pilot should light. Hold the control knob down until the flame is burning brightly (about 30 seconds). Release pressure on the knob, and turn it to the on position.
  3. If the pilot goes out when you release the control knob, try relighting, holding the control knob down longer. If the pilot again goes out, check the thermocouple (below).
Adjust the pilot:
  1. Remove any cap covering the pilot adjusting screw on a combination control.
  2. Turn the adjusting screw counterclockwise to increase the flame or clockwise to decrease it. It is correctly adjusted when the flame envelops the thermocouple bulb by 1/2 inch and appears dark blue with a small yellow tip.
Test and replace a thermocouple:
  1. Hold the control knob to pilot and light the pilot as above.
  2. Unscrew the thermocouple fitting with an open-ended wrench.
  3. Set a multimeter to the DVC (lowest voltage) scale.
  4. Clip one multimeter lead to the end of the thermocouple tube nearest the pilot and the other lead to the fitting on the other end of the tube.
  5. If the multimeter shows a reading besides zero, the thermocouple is functioning. Replace the thermocouple tube.
  6. If there is no reading, you will need to clean or replace the thermocouple following steps 7 through 11.
  7. Release the control knob and shut off the main gas valve on the gas-supply pipe that leads into the burner. Shut off power to the burner at the electrical service panel .
  8. Remove the thermocouple from its mounting bracket.
  9. Wipe the combination control clean and install a new thermocouple, tightening it by hand, then give it a one-quarter turn with a wrench.
  10. Insert the thermocouple into the pilot bracket, being careful to not crimp the tubing.
  11. Turn on power to the furnace and relight the pilot (above).
Adjust an adjustable burner air shutter:
  1. Set the thermostat to its highest setting to keep the burner running. Once the furnace has heated up, remove the burner access panel and loosen the locking screw.
  2. Open the shutter by turning it to the right until the blue base of the flame appears to lift slightly from the burner port surface. Then close the shutter until the flame reseats itself on the surface.
Clean removable burner tubes and ports:
  1. Shut off gas and power to the furnace.
  2. Unscrew or loosen and remove the tubes from the supporting bracket.
  3. Carefully clean the tubes with a brush or vacuum, making sure not to damage the burner ports.
  4. Use a stiff wire to clear any debris from clogged ports.
Oct 08, 2012 | Honeywell Icp Heil Tempstar Furnace Spark...
Tempstar pilot turns off
Based on your model number this furnace does not have a pilot light,instead it uses a hot surface igniter.typically it glows and when it gets hot enough the gas valve will open and the burners will light.When the igniter starts to go bad it will glow but not get hot enough to open the gas valve.If your furnace lights and the quickly goes out the flame sensor maybe dirty.
Oct 07, 2012 | Goodman GMS90703BXA Heater
Amana furnace main burner intermitent
Sounds like dirty flame sensor. You can either clean it orreplace it.
Apr 21, 2009 | Honeywell Power Humidifier: Furnace...
Oven has small explosion igniting and going off. says tj
A few years back I helped a neighbor with this same problem in a forced air, gas fired, "horizontal" furnace in his attic.
After having him cycle the thermostat a couple dozen times while I watched through the opening in the side of the furnace, I finally figured out what was happening.
First, there were about 6 cast iron burners [about 14 inches long with two rows of gas holes along the length]. These burners were parallel to each other and oriented perpendicular to the long axis of the furnace.
The gas was fed to the ends of the burners with a pipe manifold. The standing pilot light was at the center between burners 3 and 4. Due to the spacing distance between the burners, the pilot light was too far from even burners 3 and 4, the flame could not "jump" to ignite them, or any of the other burners. The manufacturer had installed a thin sheet metal "tent" which ran from the gas entrance end of burner 1 to burner 6, and was about 2 inches above the burner, AND the pilot light.
The standing pilot was on all the time. When the gas control valve turned on, gas began to come out of all the burners at the same time. Naturally it came out of the gas supply manifold ends of all the burners.
The "tent" captured that gas coming from the burners and "filled" up to over the pilot light which ignited the gas at that point, and the flame would propagate along the tent to ignite the gas coming out of all of the burners.
In my neighbors case, the tent had somehow become dislodged so that it did not cover all of the burner ends. For those burners which it did cover [including the pilot light] it caused the burners to light properly.
For those burners who's ends were not covered, and who's gas could not be captured, they would NOT ignite simultaneously with the others.
As these burners WERE feeding gas into the combustion chamber, the gas "envelope" would spread until it reached the nearest flame ignition source, at which time the entire "bubble" of gas would ignite with a minor boom [actually a low energy explosion]. Flame would momentarily shoot out of the burner chamber opening, and from that point the furnace would operate normally until the next restart cycle.
Although there could be several causes, I suspect that the symptoms you describe are the result of DELAYED IGNITION of some or all of the main burners.
IF this is the problem, then the solution is to clean all the burners [including the burner outlet holes in the ignition ends of the burners], clean out the burner compartment, AND properly adjust the orientation of whatever system [you have to evaluate how it works from analysis of YOUR furnace] your furnace has to ensure all burners ignite as close to the same time as possible.
When operating properly, the ignition should be a smooth transition, burner by burner, from the pilot to the farthest burners. In other words. the ignition will "flow" from the pilot outward to each adjacent burner until the farthermost ends ignite last. This usually doesn't take more than one or two seconds at the most.
Unless you are an experienced handyman, and understand this analysis and instructions, I strongly suggest that you engage the services of a professional furnace technician.
Feb 13, 2009 | Imperial Commercial Cooking Equipment...
Goodman GMS90703BXA Heater Logo
975 people viewed this question
Top Goodman Heating & Cooling Experts
Dan Webster
Dan Webster
Paul Carew
Tim Whalen
Are you a Goodman Heating and Cooling Expert? Answer questions, earn points and help others