Flame rectifier not sure where to look for the flame rectifier, is it inside or outside the unit. not sure where to look to check it.
  • mopar440man May 11, 2010
    what kind of unit do you have & M# & S#
  • Ken Bledsoe May 11, 2010
    It is inside the flame box if you can look for a small bracket with two wires coming off it. If is inside looking for a flame. If you have a wiring diagram look for flame rectifier or something called a Cad Cell all they do is sense flame is present and it is okay to leave the circuit open to continue to heat. Your Cad Cell could be bad but they get dirty depending on the burner quality.
    Novelist:
  • 189 Answers
Flame rectification is referring to a flame sensor. The flame sensor can be located on a gas furnace in front of the burners. It will have one wire connected to it. It is located at the opposite end of the burners away from the hot surface ignitor which has two wires connected to it. These wires will be found under the burners. I hope this answers your question.
Good luck
Posted on Apr 03, 2009
My breaker trips when the outside unit tries to turn on. The inside furnace runs. I cut the inside unit off and the breaker doesn't trip. I manually turn on the outside unit by depressing the cont
Hello, there is a short to ground somewhere, check all the wiring from the inside un it to the outside unit and make sure nothing is touching metal.
Jun 10, 2012 | Goodman Heating & Cooling
I am getting an ignition lockout code on the digital readout. what would be the cause? it sparks and calls for heat and will fire for about 2 seconds and then the ignition lockout code is displayed as the...
Ignition Lockout on this unit means #1 that it is set up on propane. If you are low on propane, or were low on propane and just refilled, low/no gas pressure could be the issue. If you ran out of propane, thre is now air in the gas line that needs to be fully blead out.
If propane level is not the issue, replace the ignitor.
The ignitor on these units is also the flame rectifier (flame sensor). If the unit is firing up, but the computer thinks that it is not, then it is not sensing a flame. Replacing the flame rectifier/ignitor will fix the problem in this case.
Jul 07, 2011 | Rheem M206A 206K BTU Pool and Spa Propane...
Good day! I am running my Carrier A/C Model 38EYG and it is running fine...the outside unit is running fine and the air coming out of the ceiling vents is cool. However, the inside unit (the one in the...
No its not normal. Check and make sure there is no flame inside the furnace. If not , turn the pilot light off it is a gas furnace and see if this makes a difference. good day to you too.
May 10, 2011 | Heating & Cooling
My oil burner works fine while firing, but when it shuts off, there is fuel oil continuing to come from the nozzle. I get flames outside the combustion chamber when this happens, and I can find no...
The check valve is inside the nozzle. If you change your nozzle the problem will more than likely go away. Oil burners require annual routine mantainence to run properly. The part that bothers me is you said you are getting flames outside the combustion chamber. If the flame is outside the combustion chaber but still inside the furnace, you may very well have a broken heat exchanger which is very dangerous and could kill you with carbon-monoxide gas. I would suggest having this checked by a qualified HVAC contractor as soon as possible.
Jan 28, 2011 | Heating & Cooling
I have central air ( Dimond 80 York Heating Air conditoning Unit ) My air conditoning unit has stopped working. The board has checked out ok.but there seems to be a voltage problem some where from inside...
Try the following step.....
On a call for heat, the 24 volt thermostat sends a signal to the control module. The control module will indicate a call for heat with a light on the control either blinking or remain solid depending upon model. The inducer (exhaust) blower will purge all gasses from the furnace and pressurize a pressure switch. Once the pressure switch tells the module to continue, the electronic ignition will energize and send 120 volts to the igniter. The igniter will glow and you will be able to see it if viewed thru the small inspection port. Once the igniter gets hot enough, it sends a signal to the module opening up the gas valve (24 volts). Either a pilot will come on or the burner tube will ignite then spread the flame to all burners. Lastly a safety sensor will be looking for a certain temperature within a few seconds and the furnace will continue to operate and the room air blower will turn on in a minute or two.
What could go wrong? The unit will not run if there is no signal from the thermostat (bad thermostat or broken wire), the control module does not sense a signal from the thermostat (bad control), the inducer does not energize (bad motor), the pressure switch does not close (blocked vent piping, bad switch, plugged condensate hose), the igniter does not energize (bad control, bad igniter), the gas valve does not open or there is no gas (bad gas valve, broken wire, no gas), the pilot does not light (dirty pilot), the burner does not light (bad burner, plugged orifice, not enough combustion air), the flame does not spread to each burner (bad flame spreader, dirty flame spreader, more bad burners), the flame safety sensor does not detect flame (dirty or bad flame spreader, bad flame sensor, broken wire, bad control), or the room air blower does not energize (bad fan motor, bad control).
Jun 08, 2010 | Heating & Cooling
Bosch SX 250 tankless water heater will attempt to fire 3 times then EA code. I have spark through viewing window. Read troubleshooting manual. Says Check ionization electrode. There is no part in the...
This is also known as a flame rectification sensor. It basically is what the computer board uses to detect if the pilot flame is lit. When it makes an attempt to fire is there any evidence of flame ignition? This error does not mean that the sensor is bad for sure. The error could be caused because the water heater is only making three attempts to fire and then shutting down. These water heaters are very complex and have many sensors,valves, ect that are all controlled by a computer board. Some of the basic things to check for are... Make sure that you have plenty of gas pressure. These units have a built-in pressure switch and will have issues if they are starved of gas. Most of these tankless water heaters are up to 400,000 btus and a half inch gas line or undersized connector won't work well. You can also check and make sure there is no pipe dope are debris stuck in the screen inside the gas line where it enters unit. Inspect the pilot assembly for debris or obstructions and try to blow out with compressed air. Also look for any loose electrical connectors on the board or to the sensors...one may have come loose.
Sep 07, 2009 | Bosch AquaStar Indoor Natural Gas Tankless...
Dryer not drying
First thing to check is the vent. Make sure you have sufficient air flow to the outside. If you are not sure if you have the proper rate of flow, disconnect the vent from the dryer, turn dryer on and see if burner stays on longer. Do this with a couple of damp, spun-dry towels inside the drum. If the burner short cycles again, you need to replace the coils on top of the burner assembly. These are the two black round coils.
Sep 03, 2009 | Dryers
I have a gas fireplace in my home. I've connected the gas tanks outside, but can't get the pilot to light. I can see the spark, but can't get it to catch. Any advise?
The fireplace probably has a thermocoupler. It produces current when engulfed by the pilot light flame. The small current produced (you can check for output with a votmeter) is enought to allow the gas valve to open when you turn on the switch to start the flame. The solid metal tube may not be properly connecting with the flame - repostion the pilot light and make sure surrounding air flow does not distort the pilot light pattern too much. OR the surface of the device may be slightly oxidized - very gently sand or wire brush it. Again check for small voltage output. If no volts - REPLACE THERMOCOUPLER.
Also: read this link;
http://answers.yahoo.com/question/index?qid=20081101104024AA43AJF
CB
Dec 22, 2008 | Leisure HOMEPRIDE Electric Fireplace...
Outside unit not working
If the heating and cooling is working O.K. and maintaining the proper temperatures it is possible that your outside unit is in its off cycle. If the inside unit is running and the outside unit is not with an elevated temperature inside check the power supply to the outside unit. Most units have a disconnect located near them. Check the disconnect and make sure it is set to the on position. Listen for a hum noise at the outside unit which could indicate that the control power is being supplied to the contactor.
Jun 15, 2008 | Samsung AS18A6RB Air Conditioner
Flame Adjustment
Make sure the unit is operating on the correct gas, Natural or Propane (LP). The sound you are experiencing is either not enough gas and the flame is burning inside the burner port(s) or too much gas and the flame is much larger than it has to be. At any rate, get a technician to check the gas pressure entering into the home. NOW!
Sep 17, 2007 | Goodman GDS80904BNA Open Flame Heater