How to re-gas a Panasonic Airconditioner with R410a Gas
3 Suggested Answers
  • 587 Answers
SOURCE: gas pressure
It depends on the indoor and outdoor temperature and humidity. The low side pressure can be in the area of 135# to 145# with an indoor temperature of 80° and 50% relative humidity, and the outdoor pressure can be in the area of 300# to 330# on a 95° day depending on effeciency rating.
If your asking this to charge your a/c this is not how to charge your a/c.
Charging AC by superheat and subcool
First charging a unit by superheat, this is only for Acs with an orifice or capillary tube.
Optimum superheat is 12° to 15° at the compressor or suction line outside the unit.
Hook up your gages and put a thermometer on suction line (large line), start the AC. Measure the temperature of the suction line and read the pressure on your gages. Theres a temperature scale on your gages for R-22 or R-410A the needle will show you the pressure on the outer scale and if you follow it down to the R-22 or R-410a inner scale that is the saturation temperature for that refrigerant, (you can also use a temperature pressure chart), now read the thermometer, let’s say the suction temperature( the thermometer) is 67° and the saturation temperature (the gages or temp. press. Chart), is 55°, subtract the saturation temperature from the suction temperature, 67°- 55° = 12° superheat.
Charging by Subcooling, this is for Acs with a thermostatic expansion valve, it’s common to see a sight glass on the liquid line (on these units with a sight glass just clear it, when, indoor room is at approximate set point of the thermostat). Optimum sub cooling is 12° to 15° at the outdoor unit.
Hook up your gages and put a thermometer on liquid line (small line), start the AC. Measure the temperature of the liquid line and read the pressure on your gages. Theres a temperature scale on your gages for R-22 or R-410A the needle will show you the pressure on the outer scale and if you follow it down to the R-22 or R-410a inner scale that is the saturation temperature for that refrigerant,(you can also use a temperature pressure chart), now read the thermometer, let’s say the liquid temperature( the thermometer) is 100° and the saturation temperature (the gages or temp. press. Chart), is 114°, subtract the liquid temperature from the saturation temperature, 114°- 100° = 14° subcool.
Posted on Dec 28, 2009
Testimonial: "thx"
hvac1960
  • 2133 Answers
SOURCE: How can I get a
Go with following site i which you will find products, click and select your product and click down load.
www.fujitsugeneral.com.au/products/air-conditioning
Is it helpful?
Posted on Dec 27, 2010
How do i know if the Freon has leaked our of my roof top ac
no cool air from vent or connect a manifold gauge set to machine and read suction pressure should be at 400KPA on R22 gas or 700KPA on R410A gas.
Jan 26, 2016 | Heating & Cooling
My panasonic inverter 410a has remote control problem. we already change indoor unit pcb . but doesn't work.so what to do?
SERVICE MANUAL Inverter Split system Air - Thermospace ...
www.thermospace.com/shinco/Inverter_Service_Manual.PDF Panasonic(rotary type. DC INVERTER). Refrigerant. R410A(pre-charged). R410A(pre-charged). R410A(pre-charged). R410A(pre-charged). Cooling. Capacity.
Jul 12, 2015 | Panasonic Heating & Cooling
Panasonic power light flashing air not cold blowing
hi there you need to see where you bhave a gas leak thats all the flashing light indicates that your gas pressure is to low to activate your compressor
Dec 09, 2013 | Panasonic Heating & Cooling
How do you shut off airconditioning pipes?
How do you shut off airconditioning pipes? to keep gas in unit when moving to different location.
Mar 15, 2013 | Cfm Daikin R410a Split System Air...
Help me please have a R410a 12000 btu mini split airconditioner heat pump that lost gas how do l regas it have closed all the leaks and have the R410a refregerant with the adapter.i have not charged a...
Mini splits need to have the refrigerant weighed in. First, ( if the system is already empty ) pull a vacuum down to 500 microns. Second, add the amount of refrigerant listed on the mfg. tag. Hope this helps!
Jun 07, 2012 | Heating & Cooling
What is the proper setting for Danby R410A?
R410A is refrigerant gas. I think you wanted to know, what humidity extraction level the controls should be set on. If it is really hot and humid in your area, set the humidity extraction level between 35 & 40%. If you have a mechanical control, turn the knob to Maximum.
Hope this helped you, Bradleyjo. Thanks for choosing FixYa.
Aug 06, 2011 | Danby DDR4588EE Dehumidifier
How can I get a manual for a Fujitsu ducted airconditioner R410A
Is it helpful?
Dec 27, 2010 | Heating & Cooling
Compressor unable to run and amp high. this compressor gas is R410A
Compressor high due to one or more of the following:
1. Running Capacitor weak.
2.Condenser coil block
3.Over charged gas.
4.Condenser fan motor RPM less.
Dec 08, 2010 | Mitsubishi MS15TN Air Conditioner
Heating & Cooling Logo
55 people viewed this question
Top Heating & Cooling Experts
paulcarew
Dan Webster
Dan Webster
Donni Steen