I have a york diamond 90 furnace and it is making a really loud noise.
The furnace control diagnostics blinks red 4 times. What can I do to fix it?
milten1
  • 1304 Answers
SOURCE: I have a york diamond 90 diagnostic 1 flash lock
open the top of your unit so that you can see into the burner box
what your looking for should be an orange wire that leeads up to a metal rod
that metal rod should be in the way of the flame when unit is on
this is your flame ground,,, or more commonly known as the flame sensor,,, take this out and goive it a good brush with some steel wool
and reassemble,,
this should clear up you problem
Posted on Nov 04, 2009
Therinnaiguy
  • 1420 Answers
SOURCE: York Diamond 80 furnace (propane conversion),
Check for 24 volts across the two terminals on the gas valve when the ignitor glows. If yes, bad gas valve or blockage in the gas train. If no, bad ignitor or circuit board. Even if the ignitor glows, it still may be bad and not sending the proper signal to the board. If you jump the R and G terminals on the circuit board, does the fan still only run for 90 seconds? If so I would say replace the board.
Posted on Dec 28, 2009
Therinnaiguy
  • 1420 Answers
SOURCE: York Diamond 80 Furnace: blows cold air after
There may be more than 1 limit switch. Look at the wiring diagram and follow it to all switches. Or jump out the complete circuit.
Posted on Jan 21, 2010
  • 2550 Answers
SOURCE: York, diamond 90 heating issues, on & off
try cleaning the flame sensor with some steel wool if not could be pcb
Posted on May 23, 2010
  • 2550 Answers
SOURCE: i have a york high efficiency furnace, which i
try oiling the fan motor
Posted on Sep 01, 2010
12 year old HE York diamond 90 furnace burners ignite for a few seconds but won't remain lit. Hot surface igniter then glows and burners again light momentarily. Cycle repeats several times before blo
The flame sensor can still be faulty, replacing that is the cheapest. Other issues could be a faulty control board (if available), a faulty gas valve, thermostat lossing call, or a safety/pressure switch problem. There are alot of variables and it really helps to have a meter to check voltage and continuity through-out the system.
Dec 07, 2013 | Heating & Cooling
York diamond 90 furnace burners won't ignite ... igniter glows for a few seconds then clicks off, no burner ignition. Tried resetting the furnace by powering off and then setting thermostat to call for...
The thermocouple could be defective. If this is a high efficiency York furnace, the stack blower should start and run first. If it doesn't the blower controller may have failed.
Dec 06, 2013 | Heating & Cooling
York Diamond 90 furnace blows cold air
There maybe a few issues. They have multiple safeties on furnaces. With this in mind this process to find the problem would take a Technician to check these safeties. It could be a flame sensor or thermocoupler each senses a flame or heat to keep the gas going. Also the damper for the flue must open for the gas to stay on. There may be more safeties on this and each safety sends a 24 volt current back to control module in order for the gas valve to stay open. If these aren't being met it will try around three times and go into a lock out mode which will keep gas shut off entirely.
Feb 21, 2012 | Heating & Cooling
I have a York Diamond 90 furnace and when i try to start it, the pilot light goes on then it shoots the flame into the furance, but will shut down a minute or so after that. It sounds like the blower is...
The furnace is not sensing the flame. Turn off the power.
There is a metal rod in front of the last burner to light. It is corroded and needs to be cleaned. Its the flame sensor .
take the 1 screw out holding it in to the bar and scrub it with some steel wool till shiny. replace and turn on furnace. all should be fine.
Mar 30, 2010 | York Furnace Draft Inducer Blower Fasco #...
York "high Aux or spill limit switch open"
how can I fix the spill limit switch, also how do I found it
Mar 05, 2010 | York Furnace Draft Inducer Blower Fasco #...
and reassemble,,
Nov 04, 2009 | Goodman GMS90703BXA Heater
York
I have an old York outside compressor/coil/fan unit, CDHF36-6A, that I need to replace as it is no longer repairable. What is the capacity of this unit and what Carrier unit would be a good replacement?
Adair