I have a bryant out door unit heat pump 661cj030-a. I recently lost the 27vac transformer in the indoor unit. Replaced it and ran fine for 4 weeks. I lost the 27vac again but wasnt tranformer this time. Outside unti was holding the 27 volts down. I disconnected all outputs to logic bd on outside unit only leaving wires connected from inside unit. 27 volts held up. I started putting outputs back on. lost the 27volts when i connected defrost thermostat to logic bd. I ohmed out thermostat and it shows closed or s. first shorted. should this be closed even though outside coils are not frozen or cold.(unit hasn't been running for days and its warm outside). EVEN THOUGH ITS SHOWING CLOSED- THATS WHAT it dOES RIGHT -OPEN AND CLOSE-SHOULDN'T CAUSE 27VAC TO gO TO 0 volts.With defrost thermostat pulled off, i can run heat or ac ok. when i tell logic bd to speed up and go into defrost mode it wont but i have themostat discoonnected so not sure if that is stopping that. Right now i still think its logic bd but could be thermostat or maybe even reversing valve since cant get it to go into defrost. help. dont want to order 100.00 bd if it could be something else. Does coil defrost themostat normaly closed and it opens or should it be open and then close.
watugot
  • 290 Answers
SOURCE: Ruud heat pump outside unit trips circuit breaker
Check your wiring between the contactor and compressor for a short to ground, or check the compressor windings for short to ground.
With the Tstat off, the contactor should be open so the only way for the compressor to be trying to do anything is if the 110 volts from the unbroken side are traveling through the compressor to ground. Since 110v is not enough to run it, the overload is kicking it out, cooling off, and repeating the cycle. When you kick on the Tstat, the contactor is supplying voltage directly to ground without going through the resistence of the compressor windings and kicking the breaker.
Post back and let me know what you find.
Posted on Nov 20, 2007
SOURCE: Evaporator coils iceing over; warminhg on frig side of model 106....
As I said; the fan and compressor run fine but I cannot find the defrost timer. Is it integrated into the control board.
Thanks
Posted on Jul 30, 2008
farfield
  • 462 Answers
SOURCE: burning up transformers
YOUR the first person that has gave enough information to help in a WHILE THANK YOU SO MUCH!!
Start all over from first
I'm betting that you need a fuse in both sides of the transformer until you find the real reason they burn up.
A solenoid valve that sticks can cause the transformer to blow but so can a lot of other things, namely anything in the control circuit that uses the 24V power. A relay or contactor that doesn't pull in or a defective defrost control, a shorted wire from the thermostat.
I'm wondering if you have what we call a package heat pump meaning the both the indoor blower and out door compressor & fan are in the same section out side? OR is your a split system with an indoor section and an outdoor section?
I'm betting on the split section. In some miss-matched systems (like a Lennox indoor and a GMC out door for example) Some of the origonal Lennox heat pumps had an out door and an indoor transformer. If these trans formers were not "phased" together it could cause a problem like your having. Now you just have it in the heatign mode if I read between the lines correctly. So it makes snece that it's something with the heat. The out door unit can opperate withits own 24v but if you have back up heat inside (gas or electric Im thinking you have electric) the indoor section will come on atfter a few more degrees of heat loss (2-4'F). This is where the transformer inside will buck the one outside and somethjing has to give. The weakest point.
From what ive been told by some of the old hands I've been around if the high volt side burns out look for a low volt problem if the low volt burns out look for a line volt problem.
If this has 2 transformers like I suspect try the fuse on both sides but remember the one is hot and will remain hot all time on 220V or 1 leg of it or it might remind you. To phase these transfoprmers I believe you swtich the main lines L1 & L2 at either of the transformers. Now 1 more thing the indoor section may be using ground on the low volt side as a path for 1 side of the transformer. I believe you will ahve to do same for the other transformer too.
Hope this helps Id really like to know what you find and do.
Please ask more and you give such detail I can follow you with little trouble. Please rate me as high as you can and good luck.
Posted on Mar 30, 2009
  • 3197 Answers
SOURCE: Garage door opener (chain) motor runs in reverse. Trolley slides forward trying to close door, even though it is closed, instead of sliding toward motor to open door. Happened out of the blue - was
Loosen the chain enough that you can remove it from the sprocket. Run the opener until the sprocket turns counterclockwise and stops. With the door in the open position replace the chain. You will probably need to adjust your open and close limits per your owners manual.
Posted on May 29, 2009
SOURCE: AC Fan doesn't blow cold air, frozen coil noticed outside, resetting power resolves temporarily
You need to call a reputable service technician.  The freezing up usually is associated with a low refrigerant charge or low air flow.  Check your return air filter and replace as needed.
Posted on May 30, 2009
Coleman eb23b, I canot get my ac unit to kick on, i just replaced the relay, sequencer, thermostat and transformer. i am not getting low 24 vac to my relay.
Gotta find where 24 stops. Possibly blown fuse, possibly losing your common. Check the 24 at relay to ground rather than both relay coil terminals to test common. Jump straight from transformer to relay to ensure that's what's happening.
Jun 12, 2017 | Coleman Heating & Cooling
Will goodman outdoor ac work with bryant indoor unit
This is true as long as it is not a heat pump. Make sure they replace the piston (metering device to match the outdoor units required piston size. Or if the indoor coil is metered via TXV, it will automatically meter the refrigerant flow. If you are mismatching a system, make sure an acid test is performed on the old refrigerant and take appropriate measures with the new system if the test shows positive acid. They need to definitely install a liquid line drier.
Apr 12, 2013 | Bryant 462AJC021BA Air Conditioner
I am replacing a four year old Bryant thermostat (7 wire) that runs a Bryant heat pump and gas furnace. I connected the Honeywell EIM to the old wires using the same colort codes: W = W (o/b); Orange =...
Well you are naming 6 colors, where is 7?? I'm guessing you don't have a constant 24 going to the heat pump and there is no transformer outside. Send model number of indoor and outdoor, double check your wiring, double check your setup.
Aug 13, 2017 | Heating & Cooling
I have a bryant AC/heat pump unit. Today I noticed that the air coming from the vents is just warm air, so i went out and the unit in not running condencer nor the fan. (it is the 661cj030-e unit).the only...
YES. It seems your capacitor is bad.
It must be replaced with the exact specifications as the original.
IE: MFD and VOLTAGE for the compressor and fan motor.
Example...35+5 370 vac.
Jun 27, 2010 | Heating & Cooling
I've a Bryant AC/Heat system. Model 661CJ030-A. It run cool okay but the fan kept to running even get to the point that has been set.The system seemed not auto stop. Any ideas,
Hi if the indoor fan continues to run after the unit is done cooling, you either have a fan relay located in the indoor unit that is bad or stuck, or a problem in the thermostat with the fan contacts not opening when its satisfied. Pull the cover from the thermostat to expose the wiring. Find the G/Green wire. This is the fan wire. Take a small screw driver and carefully loosen screw and take this wire off. Give it a couple of minutes to see if it shuts off. If it does shut off, the thermostat is faulty and you will need a new one. If it still runs, you will have to check the indoor unit and find the fan relay. If this system is gas fired for heat, it will have a combination fan/High limit control that is the problem, more then likely stuck. Look at the wiring diagram on the panel and it will show you the fan control. You can try tapping on it to see if you can un- stick it. If not, it will need to be replaced. If its just a fan relay, it will be black about the size of a wooded match box with around 5 wire terminals on it. If you have someone turn the stat on and you should be able to hear it click. Do the checks with the stat and let me no the out come and we can go from there.
Shastalaker7
Jun 03, 2010 | Bryant 463AAC008BA Air Conditioner
The transformer on my central AC/heater (luxaire model # A236A344T LH) keeps going out. There are 4 settings on the wall. Cool, off, heat and EM. Heat. The setting switches to EM. Heat each time the...
You might have some thermostat wires that are touching meaning the insulation has been broke off and getting a direct short. Check the wiring going to the outside unit and replace any wire that is in bad shape. let me know okay. Ken
Dec 11, 2009 | Honeywell Programmable Thermostat Heater
Is the Bryant 661CJ030-A heat pump single- or multi-stage?
Single stage heat pump. But you must have a two stage tstat for backup electric heat. You single stage cool two stage heat. The second stage brings on the electric heat in case the heat pump can not keep up. Wiring goes r y w1 on most heat pump tstats are switchover valve or o terminal. W2 second stage heat or emergency heat. g is fan c is common terminal.Rus
Nov 11, 2009 | Bryant 463AAC008BA Air Conditioner
Have a Bryant AC/Heat pump. Model# 661CJ030-A. Problem: Air conditioner not cooling,fan comes on,there is a click and a hum but compressor doesn't come on to cool. Does thermostat have anything to do with...
Found charge capacitor top ballooned replaced with a universal capacitor found at a local appliance repair shop system works like a champ capacitor is located behind the interior electrical panel after removing the side panel
Aug 19, 2009 | Bryant 463AAC008BA Air Conditioner
Burning up transformers
Mar 30, 2009 | Goodman Heating & Cooling