Compressor relay keeps cycling on and odfdf on my Rheem Heat Pump
It happens only when it is in heat mode. I had to replace the relay because it burnt the contacts. But while running for heat, after about 15 minutes of running, the relay starts to cycle on and off quickly.
  • 3 more comments
  • kbar166 Jan 11, 2009
    The relay is only a week old. Brand new. I checked the incoming power to the relay and it is dropping out. Thanks.
    There is no relay on the side of the compressor.
    Here is another thing to think about. When I first switch over from the electric calrods to the outside compressor, it sometimes takes hours (could be as much as 24 hours but can be as low as 1 hour) before the fast cycling starts. Maybe this will help.
    I am using a Fluke meter right now recording the highs and lows of the relay coil. I will let you know after the cycling starts where it is.
    Checking voltage right now.
    Sergeant:
  • 378 Answers
It is possible if it gets noisier as it gets hotter outside that the condenser coil is dirty or there is a problem with the fan.
To get some idea if this is so you could feel the smaller of the two lines going to the indoor coil.
The smaller line should be in a range of about 100 degF. This would feel like the surrounding temp. If hotter you may have a problem.
Could also be several other things.
Might need to call a tech to install a set of guages to diagnose it for you.
Posted on Jan 11, 2009
    Genius:
  • 1,199 Answers
This sounds like a voltage problem! and that is what is tricking the relays! check voltage input witha meter!
    Sergeant:
    Novelist:
  • 326 Answers
Its the voltage problem on the connections that r tripping the relay and its misfunctioning.just check out the voltages and make it proper.if it finds more complicated a technician at your place is advisable. thanks.
    Genius:
  • 1,239 Answers
Hi
You would need to start by putting system in A/C mode and using a voltage tester check to see if you constant 24 volt at the fan relay COIL ,while calling for A/C.If you lose the 24 volt then your fan relay is OK ( if you have constant 24 volt at the fan relay and motor drops out, replace fan relay.Also check line voltage of the motor ,make sure you have constant 120 or 220 volt (whichever one it is while it's running)also  go to where your getting the 24 volt , and check to see your getting constant 24 volt. Check at the Circuit board next to make sure you have constant 24 volt going to the fan relay . You would need to look at the wiring diagram closely to see what is in series with the fan relay. Also the control board.
In closing look at wiring diagram and start with  fan relay and board.Basically start at fan relay and work back to the board looking for any switch that may open in the fan circuit.
  • ABHISHEK.C
    ABHISHEK.C Jan 11, 2009
    What I would do is check to see what the fan control is doing. Remove the front furnace panel where the burner is located. In the upper right or left corner is the fan control, it has a silver cover that you remove by squeezing the sides and pull out. you will see a dial marked in 10 deg increments starting at 50 degs and up to 250. There are 3 adjustments tabs , #1 fan off setting, #2 fan on setting and #3 overheat shut off. #1 is normally set to 90 deg, #2 -110 deg, and #3- 190 deg. With the cover off watch the dial to see what the fan control is doing. Not sure about the 2 zone, I assume it’s control dampers.
  • 10,515 Answers
It sounds like the compressor relay mounted to the side of the compressor is out. Very common problem on these units. The replacement relay is supposed to be stronger and less likely to give a problem. Remove the relay and shake it. If you hear it rattling inside it is definately burned out.
Do not replace it with a 3 in 1 or kickstart relay. It will work fine for a few months and burn the compressor out. Get the correct replacement part.
Post back to let me know what you find
Thanks.
    Genius:
  • 2,920 Answers
You need to replace that relay,,,,if its cycling that fast its going to be the relay or the thermocoupler one or the other but in your case i believe its the relay
Compressor relay switch
What temperature is this heat pump being run at? If it is low ambient temp outside this may be running in what is called defrost mode to where the compressor will run without a call for heat. This seems normal to me as long as the setpoint temperature is being reached.
Dec 25, 2013 | Honeywell Heating & Cooling
Heat Pump Blowing Cold
Unless you just installed or had the thermostat installed recently, I would not point at the thermostat as the problem. With what you have described I would suggest have your units serviced as it sounds like a loss of charge, or failed defrost control board. The "Aux" comes on when the unit is using secondary heating (electric heat strips). That occurs when the demand temperature (what you set it to) in Heat mode is more than the current room temperature, usually ~2-4 degrees higher. Also happens in defrost mode. Defrost is a heat pump cycle that melts any build up of ice on the condenser unit (outside unit). That process is simply the unit running in cool mode which will heat up the outside unit to melt any ice. Defrost cycles vary with manufacture but usually you can tell if is in defrost by looking at the outside unit, during defrost the unit will be warm or hot sometimes there is steam and the compressor will be running but not the fan. Defrost only happens on heat pumps in "Heat" mode. Rheem has a 10 yr compressor and parts warranty, so call the installer or Rheem authorized service company.
Nov 11, 2013 | Honeywell RTH7600D Touchscreen 7-Day...
Heat pump fan will not stop running
could be a heat sequencer. if the stat was bad it would run constantly in both modes.
Nov 12, 2012 | Heating & Cooling
Replaced Thermostat and now Blower Motor will not run
Sounds like a set up issue on the tstat. You say this is a packaged unit, inside the machine you should find where the tstat wires hook up. Typically red is power yellow is compressor orange is reversing valve white is emergency heat green is blower. Put red and green together, test blower. Then red green and yellow, make sure blower works again. If blower runs both ways it's either the tstat wire or tstat itself. Make sure you are landing wires on dedicated heat pump terminals, make sure in settings you are set up for heat pump with back up electric heat and TSTAT CONTROLS THE FAN. Good Luck. Also if there is a switch on the tstat for gas or electric on the back you want electric.
May 12, 2017 | Heating & Cooling
I have a Rheem heat pump/air handler; it draws 2.9amps with only the fan running, 13amps when the heat pump is running and 38amps with the heat strips on. My question is why the unit draws that many amps...
Sounds like it must be about a 2.5- 3 ton system. The 13amps has to be the compressor draw -normal. and 38 on the strips- normal. 2.9 fan -normal.
You may want to check your wiring to see where the outside unit gets its power. Theres nothing inside that can draw 13 amps. That almost has to be the compressor power wire.
Jan 27, 2011 | Heating & Cooling
Heat PumP: Rheem Two Stage Heat, One Stage Cool Thermostat Replac
R = R with jumper to RC hot side of transformer
B = Reversing valve
Y = Compressor relay
G =Blower
C = common on transformer (X on old t'stat)
W2 = Auxillary heat
E = Emergency heat
Mar 04, 2010 | Heating & Cooling
Rheem Heat pump 5 ton heat strip 10KW what
I would say this is around 75 amps of draw at max for both the compressor and heat units. . Therefore--at least 90 amp breaker, and probably 100 amps for good measure, and at least #4 or #2 wire to the unit.
Oct 09, 2009 | Heating & Cooling
Reversing valve installed backwards on goodman heat pump have a simple comfort 2000 thermastat the defrost cycle doesn't work . can the reversing valved be wired on the terminal board to accomadate this...
You should be able to move the reversing valve wire from O terminal, (the changeover relay), on the thermostat to B terminal. I deal mostly with York
which O on the t'stat is normally open and B is normally closed.
Oct 01, 2009 | Goodman PHKJ048-1 Air Conditioner
Heating & Cooling Logo
53 people viewed this question
Top Heating & Cooling Experts
Paul Carew
Dan Webster
Dan Webster
Tim Whalen