Hi I am having a problem with a main fan overload alarm on this 30 ton crac unit,i did not look into the problem that much (didnt have time) but now that i think about it i did not see a reset button on the Contactor, all i know is that i am not getting 24 volts to the Contctor,transformer is fine have power on it but like i said didnt go any further with the troubleshooting.it is my first encounter of this sort,Please if you can help it will be greatly appreciated.. Thanks in Advance Pete
  • 234 Answers
SOURCE: AC Control Transformer keeps failing.
well it has blown the fuse on the transformer, then you have coil switch bad.It could be the coil on the contath in for cooling.But can check by taking the yellow wire a loose and see if the don't blow. The red wire is one side of the transformer and the com could be any color.But look at the red wire because it is the main wire that travel the voltage throuhg the unit.
Posted on Mar 26, 2009
manhandy
  • 146 Answers
SOURCE: i have a split system air conditioner. the inside
contactor working means fan might be bad can you feel any resistance from fan or bad capacitor.
Posted on Jun 24, 2009
  • 26 Answers
SOURCE: I replaced the contactor and the unit still doesn't work
Are you getting 24 volts at the contactor coil? If not check your control voltage wiring to the unit. If all is good check refrigerant charge, you will need gauges for this, compressor can be held out due to low pressure, also unit can be out by the high pressure safety switch which is normally reset manually.
Posted on Jul 14, 2009
t1m130
  • 86 Answers
SOURCE: Blown Transformer heat pump
blown transformers are usually from a low voltage short the first thing i would do is wire a automotive or resetable 3amp fuse in line with the transformer so you dont blow transformer after transformer the wire coming off the transformer that say 24v take that wire a couple of inches down and cut it and install the fuse in series there
24v----------------
24v----------x----------
24v--------{3ampfuse}----------
now you can go through your low voltage wires one by one and test them unhook all the wires to your outdoor condenser at your indoor unit(furnace or airhandler) and try turning it to cool now if you blow the fuse the short is between the tstat and the indoor unit if the fuse is still good leave it on cool and hook up one wire at a time to your outdoor unit starting with R a lot of times your contactor or your defrost board will short out on you also look for pinches in wires wires with cracks in the insulation and wires touching metal this situation can be a real pain sometimes i would recommend calling a hvac company if you start to get stumped
hope this will help you
Posted on Jul 26, 2009
  • 1033 Answers
SOURCE: Condenser unit will not run. has 240 volt at
Hello, check the tstat wiring going to the unit for any breaks in or if it has come loose between the indoor unit and outdoor unit. Also, chevk if you are getting voltage from tje control board between the y and c terminal, if not the control board is bad. Last thing to check is remove tstat and jump the y and r wires there if this starts the unit then you have a bad tstat.
Posted on Apr 30, 2011
I have a 150 hp Ingersoll rand aircompressor It is showing "Main motor overload. We have checked the motor and there is no issue with the motor. The computor has locked up and we can not clear the fau
Most faults on the main motor have to be cleared by resetting the main motor overload in the control panel first. Simply push the reset button the overload. Then reset the alarm on the controller. If the controller is locked up pull the main power disconnect for 15 to 20 minutes. Power the unit back up and try the process again. if no luck you will need to replace the controller and maybe the over load or aux contacts. If controller is truly locked your only option is to replace the controller.
Oct 20, 2014 | Ingersoll Rand Air Tools & Compressors
How I can fix g.e airconditioner
Motor is getting hot and going on thermal overload when it cools off it will work again replace the motor that will fix your problem
Sep 02, 2014 | Heating & Cooling
Have a SSR-EP100 air compressor that shows
Try to reset the main motor and fan motor over loads by pushing the reset on the overload it self, Then reset the controller. If the error resets, before starting. put a clamp on amp meter on to L1 or L3 motor lead which is located in the compressor electrical box . Then start and observe amps when unit is making air fully loaded. Once you know how many amps at full load the unit is pulling ,look at the overload setting on main motor overload and see if it is approxmately 10 amps above the max amps being pulled.If not set it about 10 amps above your max load amps.
Nov 26, 2011 | Ingersoll Rand Air Tools & Compressors
HAIER HWR12XCA. Main fan stopped working. Condensor kicks on then kicks off after a few minutes. Any suggestions.
I would replace the fan capacitor. This is a split system and from the symptom you
describe, it would be the first thing I would look at since the compressor will go into
thermal overload and shut down if the fan is not running.
Fan caps are available online, Or you can get a substitute from a local appliance
parts store. Just be sure the value of the replacement is the same. Make sure power
is off at all sources feeding this unit before servicing. :)
Jul 31, 2011 | Haier HWR12XCA Air Conditioner
On my window unit the compresser only runs for 15 sec. and shuts off for 4 min. the fan stays running.. its not cooling the room
possably a problem with the outside condensor fan motor. Pls check
1.) when unit is running is the outside fan motor also runnng. My guess is the outside fan is locked bad motor ect. Unit would only run maybe 30 seconds before cycling on its overload
May 04, 2010 | Whirlpool ACE244XS Air Conditioner
Unit is 5 years old. came home and could smell a faint oder. there was a loud click sound then 30 seconds a softer click sound...3 minutes later it did it over until i unplugged it. the freezer area has...
could be overload and relay,if clicking is coming from compressor area could be start device {overload and relay} if not that ge has been having problems with main board,i'd check the start device first because the main board is expensive
Nov 06, 2009 | GE GTS18HCM Top Freezer Refrigerator
Inside fan wont run when outside unit comes on
hi there,
check the fuse or overload protection of fan motor on control panel circuit board,there is a
relay to reset the overload to put back the circuit connection.find the lever and push to reset.have a nicw day regards
Jul 10, 2009 | Heating & Cooling
Fan motor
Hi, the bearing on your fan must be stuck, have it checked by a technician. humming builds current in the motor and might overload.
I hope it helps
Jun 01, 2009 | Heating & Cooling
Air conditioner compressor keeps shutting down
This is due to thermal overload,Which can be caused by low oil in the compressor,the fan has stopped running on the unit outside,Dirty coils,or just a worn out compressor.Although this is thermal overload,It has nothing to do with outside temperature,But rather the internal temperature of the compressor itself.
May 19, 2009 | LG Heating & Cooling
What to do with the Total Blender when overload appears?
The product has a 3-year warranty:
A reading of “OVERLOAD” indicates an overload on the motor. Turn off
and unplug the unit. Plug in the unit and turn the motor on again to clear the
over-load condition. Check the blender jar for blockage. If overload condition
re-occurs, contact your Blendtec service agent.
Mar 25, 2009 | Blendtec ABC Work Top Blender
Heating & Cooling Logo
64 people viewed this question
Top Heating & Cooling Experts
paulcarew
Dan Webster
Dan Webster
Donni Steen