Turned off gas by accident and now cant turn it back on
Pilot light went out on furnace followed instructions but when it wouldnt work the gas valve wont turn to get it back on
  • 2 more comments
  • briannagrove
    briannagrove Dec 01, 2012
    it is not turning at all
  • briannagrove
    this happened a couple of years ago and cost a lot of money to have someone turn it with a certain tool. since it is so close to xmas dont have the extra money to call person again
  • Robert Dec 02, 2012
    What is the model # of yoir Furnace?
  • briannagrove
    briannagrove Dec 02, 2012
    DGRT075DCA
    Genius:
  • 1,033 Answers
Is the knob on top of the valve not turning when you press it down to light the pilot light?
Posted on Dec 01, 2012
hotuna
  • 288 Answers
SOURCE: cozy wall heater lights fine then goes out after 3 or 4 minutes
Make sure all the wire connections are good and tight. Next lift off the cover and look for a little thermal disc mounted up by top of the heat exchanger. Most have a re-set button but not all. If you have this ,by-pass it ,see if that solves the problem, if so it may be defective, or doing its job and you have a venting problem. If you don't have this and have changed the thermocouple (was it a copper tube with a fitting that screwed into the gas valve, or did it have 2 wires, that is a pilot generator, kind of same thing) make sure the probe is set correct, with the pilot flame heating the top 1/3rd of the probe. The only thing left is the gas valve.
Posted on Dec 25, 2007
SOURCE: Pilot will not light
The Pilot indicator will appear to line up with the arrow on the base, and even push in as though allowing gas to flow, but if it is just 1mm out of alignment, no gas will flow. So the solution is to move the valve in the Pilot mode slightly in one direction or the other to see if/when gas flows.
Posted on Nov 07, 2008
  • 53 Answers
SOURCE: My coleman floor furnace will not stay on
Have the thermocouple replaced, ensure the pilot flame is blue - not yellow, yellow indicates blockage in pilot
Posted on Oct 08, 2009
billyvangogh
  • 108 Answers
SOURCE: Wall furnace shuts off after about 10-20 mins
sounds like its not venting properly...it likely is shutting off on a "Spill switch" or "Vent safety switch"....check the vent/chimney first off.....also the pilot could be dirty..,..a lazy pilot tends to blow out easily....pilot should be blue and sharp,,,big enough to fully envelope the thermocouple
Posted on Nov 01, 2009
Testimonial: "I checked the pilot light and it's clean. I will have to check the chimney next week but thanks!"
heatman101
  • 43501 Answers
SOURCE: Coleman Gravity Floor Furnace need millivolt gas valve & pilot ki
Go to www.grainger.com and look for a "power pile generator" this is a millivolt thermocouple that may be just what you need to make your heater work again
Posted on Nov 12, 2009
What do I need to do to lite my heater after a summer rest?
How to Light a Furnace Pilot Light Here, we'll explain the basic steps for re-lighting the pilot light of a gas furnace.
#1: Locate the Instructions Label on Your Furnace
Every furnace should have a label on it that tells you how to light a furnace. Sometimes, however, the printing may be small or the furnace area may be dark. In these cases, the label may be difficult to read. Keeping the following instructions near your furnace or in another safe spot where they can be located easily will make the task much easier.
#2: Find Pilot Light and Components
Near the bottom of your furnace is a switch that normally says "Pilot," "On" and "Off." Find this switch and turn it to the "Off" position. Wait at least five minutes. This is important because it gives the gas time to dissipate, which is necessary to avoid possibly starting a fire. While you are waiting, take note of the location of the reset button, which should be near the dial you just turned to "Off."
#3: Re-Light the Pilot Light
Once the gas has had time to dissipate, turn the knob to "Pilot." Then, hold down the "Reset" button and bring the flame of a long lighter close to the pilot light opening. This should light the furnace pilot light. Once you are sure the pilot light is on, release your pressure on the reset button.
Sometimes, seeing a job bein
Oct 28, 2017 | Heating & Cooling
I replaced the thermocouple and I can not get furnace to light.
turn to pilot to light pilot
hold and wait should be instructions on control
turn to on position if pilot goes out start again
Nov 02, 2015 | Heating & Cooling
Furnace Pilot Light Won't Stay Lit
Here is something similar that happened to me. I went through the same steps you went through and upon closer inspection, I found a spider had made a web inside the supply line only letting a small trickle of gas through. Have you verified there is nothing blocking the line?
Oct 02, 2012 | Heating & Cooling
Cant figure out how to relite my furnace
on the bottom of the unit there is an access door remove it and behind it you will find a gas valve and a pilot find the piolot......turn off the gas valve and move the selector to piolot depress the switch and at the same time place the flame from a log lighter onto the pilot light after this lights turn the gas valve to run and the burner should light.
Mar 03, 2011 | Empire Direct Vent Wall Furnace;...
My screen is out on my chimney flute, a bird was trapped inside and worked it's way to the furnace and was killed there. The bird has been removed, now the furnace is not producing airflow throughout the...
The pilot is iside the burner compartment of the furnace. Remove the cover and follow the 1/8" tubing to an orifice. This is where you light the pilot. the gas valve must also be turned off for a couple of minutes before trying to light the pilot. After a few minutes, turn the valve to pilot and light the pilot. Hold it for 30 seconds and then turn the valve to "ON"
Jan 26, 2011 | Heating & Cooling
I have an amana furnace and it will not kick on. When the switch is turned on the furnace will try to run but won't warm up and blow. Does it have a pilot light?? or a reset button??
Try this----turn furnace off at stat and unplug furnace for 10 minutes. Plug it back in, the combustion and blower motor may both kick on for 2 minutes or so or not. Turn t-stat to heat and turn up stat to highest setting. Hurry out to furnace and you should hear the combustion motor(little motor piped to flue) kick on, then wait for a "click" next you should see a glow from the igniton element, then another click, next will be the gas valve opening. If no ignition, it will try 3 times and then lock ur *** out, and just turn on the blower just as a precaution. If you dont see the glow plug glowing after the first click, replace the $20 glow plug and you should be good to go. The glow plugs crack, and this is what breaks the connection. If you gas valve has a knob, and says pilot----turn the valve to pilot, push down on the knob, light the pilot and hold down knob for 2 minutes to heat up flame sensor. Make sure the t-stat is all the way down or off. After 2 minutes of holding pilot knob down, let go and your pilot should be still lit, if it is, then turn gas valve to ON and then turn t-stat up to kick on furnace. If ur pilot doesn't stay lit, get a new thermal couple and replace it-$12 bucks. Good luck and let me know how it went. azeddysac@yahoo.com
Nov 06, 2010 | Heating & Cooling
My gas tank ran empty after i filled it up i tried to relight the pilot the pilot wouldnt stay lit after rleasing the button now i cant get a pilot light at all
It sound like you need to purge the gasline. First check the fuel in the tank, be surtain that the tank is turned on. Go to the farthest gas appliance from the tank. Cut off the gas valve at that appliance, now you need to ventilate the area (open the doors and widows) go back to the fathest appliance and crack the supply nut open that is just past the shut off .Turn on valve, when you hear a higher pitch sound or smell gas, shut off the valve and reconnect the supply line. Turn the valve back on and wipe the supply nut with soapy water if it bubbles you have a leak turn off valve disconnect supply put some pipe dope on the male threads ,Reconnect and check for leaks .When there is no more gas in the area you can light that appliance. The gas line should be free of air now and you can light the rest of your appliances.follow these instructions to the letter or call a ..plumber. Good Luck
Dec 01, 2009 | Home
Gas Furnace Will not light
Hi, normally when you turn the gas off at the flex line valve and leave it off for awhile, the gas has to clear the gas valve and lines up to the pilot. Purge its self of air before it will light again. It will take the electronic ignition several clicks and more before there is enough gas to light the pilot and then open the main gas valve to fire the burners. Tell me, what kind of gas furnace is this when you speak of water? you say the site glass was full and you had to drain it and then the ignitor kept on clicking when it normally only took one click to light it. Please let me know the style as in a split system, a package unit, all in one, or what you have. I will wait to hear back from you. If the pilot does not light right away, then yes let it continue to click and see if it will light. On a heater with the electronic ignition control module on it or a circuit board, this is what tells the pilot coil to energize to light the pilot. It will send power to the pilot coil to open and let gas through to light and same for the main gas valve, will get a signal to open when the pilot is on. It will not open unless the pilot is lite for saftey. I will wait for you're responce.
Shastalaker7
Nov 27, 2009 | Honeywell CT87B ROUND HEATING&COOLING...
Lighting the pilot light
The steps involved can vary slightly depending on your furnace model and pilot valve type, so if possible try and find the instructions inside the furnace door cover or in the instruction manual. This is for a gas fired furnace, but applies to any gas-fueled appliance including water heater. Two of the most common types of pilot valve body assemblies either have a red reset button and a gas valve or no reset button and a valve knob that can be depressed. But whichever type you've got, if you have an older model furnace with a standing pilot (flame is lit all the time) then this is the basic procedure.
  • Turn you thermostat to 80 degrees or to a setting that will demand heat. Make sure the thermostat is in "Heat" mode.
  • Go to the furnace and find the pilot valve. The pilot valve body is a box shaped device into which the main gas line will run and is located near the gas burners. It will usually have a gas **** or valve knob that reads "On, "Pilot" and "Off." Locate this gas **** or knob.
  • Turn the knob or gas **** to the "Off" position and wait about 3 minutes for any residual gas to clear away.
  • Find the pilot. It's located near the gas burner tube assembly in the furnace.
  • Get your match or lighter ready. Sometimes the pilot is hard to reach. If possible, try and use a long fireplace match when you light it. If you don't have a fireplace match then a butane BBQ grill lighter works well too. If you don't have that, then you can fasten a match to the end of a stick when you light the pilot
  • If you have a pilot with a red Reset button, turn the gas valve from "Off," to "Pilot."
  • If you have a pilot with no red button, turn the knob from "Off" to "Pilot."
  • Place the lit match or ignited lighter tip at the pilot and depress and hold the button or depress the knob as appropriate. Depress the button or knob for about 30 seconds. This maintains gas flow to the pilot until the thermocouple gets hot enough to open the main gas valve.
  • Once the pilot stays lit, slowly release the button or knob and turn the gas **** or knob from the "Pilot" position to the "On" position. This will ignite the burners and keep the flow of gas supplied as required for the burners as called for by the thermostat.
  • If the burners fail to ignite then it may be because the thermocouple did not get hot enough to open the gas valve. Wait a few minutes and then repeat the above procedure. This time hold the red reset button or depress the knob for about 45-60 seconds.
  • Once the main furnace burners ignite, adjust the thermostat to the desired setting.
  • If you've followed the previous steps on lighting the pilot and it still does not light after, or will not stay lit, then you probably have a problem with the thermocouple or an adjustment needs to be made to the pilot. You'll need a furnace service technician to replace or repair these parts. You may find that the pilot lights, but it is an anemic looking flame. That's a different problem we'll look at in the next section.
  • If the pilot lights but the flame is a weak yellow flame, it will not get hot enough to heat the thermocouple to its set point allowing the gas valve to open.
    A natural gas flame should be a bright blue with the tip of the flame having just a tinge of yellow. A propane flame should have a bluish green flame with a tinge of yellow at the tip. The flame should be strong enough to hit the thermocouple tip about 1/2 inch from the tip end. If the flame is weak or shaky looking, check to see that a breeze or draft is not blowing on it. Adjusting the Flame
    There is usually a small screw on the pilot valve body that will adjust the flame. You may have to refer to the manufacturer's instructions to find the screw. Turn the screw as needed to adjust the flame throw. Yellow Flame
    A yellow flame is caused by lack of air and incomplete combustion. It can be caused by a dirty pilot tube tip. Split Flame
    This is caused by dirt in the pilot tube. Take a needle or small nail and gently clean the tube. Flickering or Wavering Flame
    A flame that flickers is usually caused by a draft.
Thanks for using FixYa - a FixYa rating is appreciated!!
Feb 18, 2009 | Water Heaters
The pilot light for the oven went out.
Relighting Your Furnace's Pilot Light
furnace1.jpg - Turn off the gas at the main valve at your utility box - Wait five to ten minutes for gas fumes to waft away - Get a long match—yes, a fireplace match, not a standard match - Set the gas valve on your furnace to "pilot" - Press the red button as you hold the match to the pilot valve - Keep pressing the red button for 30-60 seconds so the pilot can heat the thermocouple. Release the button and see if the pilot remains lit - If pilot goes out, wait five to ten minutes and repeat the process - Once the pilot stays lit, turn the main gas valve back on - If the pilot light continues to go out, call a technician, who may need to adjust or replace your thermocouple or adjust your pilot
Jul 28, 2008 | Tappan 30IN ELEC IGNa Oven
Heating & Cooling Logo
54 people viewed this question
Top Heating & Cooling Experts
Paul Carew
Dan Webster
Dan Webster
Donni Steen