I have a good heatpump with goodman air handler. the air handler has a sequencer and a blower relay. the blower relay quit working and i replaced it with a supco 90340 relay. the problem now is in the switching. my understanding is the blue and red wires should be piggybacked on on side of the 24v coil and the white on the other side of the coil. if i do that the relay switchs and the blower starts but the compressor does not. Any Ideas?
  • 1,652 Answers
Your green wire from the tstat and the low voltage common should land on the relay coil. Your high voltage for the blower lands on normally open. Sounds like you are using your red (constant 24v) to energize your relay. Therefore your relay is constantly energized and your blower runs constantly. Let me know!!
Posted on Jul 01, 2017
SOURCE: replacing thermostat
Posted on Sep 12, 2008
  • 61 Answers
SOURCE: blower stays on with new themostat
Check to see if there is a short between the green wire and the red wire. Green is the fan control wire for AC. Sounds like some wires may be touching. How did the old t-stat get fried?
Posted on Jan 02, 2009
SOURCE: honeywell thermostat
I had the same problem and decided to take a chance and call honeywell customer support. I am shocked, they solved my problem! At least in my situation we found that the blue wire ran the compressor. Instead of hooking up to "blue" on the thermostat, we hooked it up to "white." It works wonderfully now.
Posted on Apr 25, 2009
  • 232 Answers
SOURCE: Wiring
red goes to RC and RH, White goes to W, Green goes to G and Blue goes to Y. iam assuming on the old tstat that Red whent to R White went to W Green went to G and Blue went to Y
Posted on Sep 20, 2009
Testimonial: "Thanks! Worked out great!"
  • 233 Answers
SOURCE: Old wiring looks like this
If you have a heat pump, the thermostat that will operate it most generally will have an "O' terminal for the orange wire, this is the circuit that energizes the reversing valve on the heat pump, be sure that the stat says heat pump on the box. hope this helps
Posted on Nov 07, 2009
Goodman package heatpump blower motor contant running
check your themostat fan mode switch to see if it in on or auto. It should be in auto. If this does not stop indoor fan motor, (it may take up to 2 minutes for the fan to stop, preprogrammed shutoff in the thermostat and fan control cards may make you think the fan has not stopped ) If this does not stop the fan the fan control board in your air handler has a green wire shorting to 24 volt signal in the theromostat wire or the contact on the blower control card is stuck and will need replaced.
Feb 05, 2014 | Goodman Manufacturing Goodman GPH1348H41...
Airhandler- the themostat is on auto/I understand cool,heat.emerg heat,The (G) terminal-then why heat mode or,emer heat fan blows?Only when i switch to cool mode the handler still want start up blowing...
the fan fill come on with the sequencer (stack switch you call it) it will also come on with the fan relay. on some goodmans the fan relay is the black box on the circuit board. use a jumper to jump red to green, this should bring the fan on sounds like you could have a broken green wire, try using a different wire instead of green
Sep 12, 2013 | Goodman Heating & Cooling
Not hot air
One of three issues
Thermostat not wired properly
failed heat sequencer in air handler
bad heat element in air handler
Feb 10, 2013 | Goodman Manufacturing Goodman ARUF182416...
HE heat pump won't talk with old air handler?
The fact is, the air handler supplies the voltage, blower, and electric heat. In order for the heat pump to work correctly, the wiring from the thermostat and heat pump need to be hooked up right to the air handler. The thermostat is what tells which component to come on. If the fan stops, but the condenser keeps going, you either have a faulty fan relay on the air handler, faulty thermostat or wiring, faulty wiring at the heat pump, or the contacts on the new unit are sticking, which is highly doubtful considering it is working now. I hope I have helped you understand this a little more. Good luck and don't let them push you around, get someone that knows what they are looking at.
Jul 18, 2012 | Goodman Heating & Cooling
Blower will not blow air with cover on unit when i take cover off air blows through vents on package heatpump
Sounds like return air supply clogged, check filter and duct work also some units have a filter at air handler at bottom some time the installer leaves them in
Jan 03, 2011 | Goodman CLQ36AR49 Air Conditioner
Indoor blower not running,capacitor is good,blower motor is good
have you check the 24 volt transformer in the air handler? you must have 24 volts from the thermostat to the tranformer in the air handler.
Jun 23, 2010 | Goodman CLJ30AR32 Air Conditioner
Wiring diagam for goodman heatpump and air handler to thermostate
On your t-stat you have Y, W1, W2, R, O, G, B or C or X. Y is your cooling circuit and will be the same in the air handler and heat pump unit, use the yellow wire for this circuit. W1 and W2 are your back up elec. or gas heat. Depending on how many kws or heat strips you have and t-stat wires you will put the white wire to W1 in both the t-stat and air handler. W2 is for your second stage back up heat if air handler calls for it, this will be a tan or brown or black t-stat wire and goes to W2 on t-stat and air handler. R is half of your 24v control power from the transformer and is the red wire and goes to the t-stat, air handler, and heat pump. O is for the reversing valve in the heat pump that switches it from heating and cooling. You guessed it the orange wire connect to t-stat and heat pump. G is for the blower and is the green wire to the t-stat and air handler. B or C or X is known as the common which is the other half of control circuit from 24v transform it is the blue wire and goes to the t-stat, air handler, and heat pump.