SOURCE: Trane Heat Pump
What caused the power outage? Check the outdoor disconnect to the condenser unit. The fuses may have blown, causing the heat pump to not function and depending on the aux. heat to carry the load.
Posted on Dec 18, 2007
  • 252 Answers
SOURCE: need wiring for honeywell pro 3000 in trane xe1200
the pro 300 is a single stage thermostat and can not be wired to control 2 heat stages seperately
Posted on May 16, 2009
Therinnaiguy
  • 1420 Answers
SOURCE: Hello We have a Trane central air
Bad thermostat, improper wiring or bad circuit board in furnace. Turn off the disconnect outside.
Posted on Dec 30, 2009
hvac1960
  • 2133 Answers
SOURCE: My Trane thermostat (TCONT600AF11MAA) is
Friend! All thermostat is calibrated to cut in and cut off at the end of - or + 1 degree end.
Example: If you set 23 degree, it will cut off in 21 degree and cut in @25 degree. So accordingly you set the temp.
Secondly, don't set temp near to your room temp.Minimum difference should be 3 degree. If your room temp 12 degree, set at least 15 degree for heat and if room temp 28, set at least 25 degree for cool.
Hope it's helpful?
Posted on Jan 02, 2011
What should the heat anticipator be set at on the thermostat?
The purpose of a thermostat heat anticipator is to "de-sensitize" the thermostat so that when actual room temperature is hovering close to the set temperature on the thermostat, the thermostat switch won't keep switching the air conditioner or heating system on and off too often - which can damage the equipment.
If you are replacing an existing defective thermostat with a new one, simply, set the anticipator to the same setting as the old one- as long as they are of the same manufacturer and model.
If you don't have the old one to match the new thermostat settings to, then you need to measure the thermostat's circuit using an ammeter.
In order for the thermostat to operate properly- you must adjust the heat anticipator resistor to match the current of the gas valve or relay on an oil-fired burner..
Another option is to install the T-stat using the factory default setting.
Since you did not mention the make and model number of the T-stat you are using, I cannot be more specific.
Feb 12, 2017 | Heating & Cooling
Tip
How do I Set the Thermostat Anticipator
If you have an older thermostat that has a heat anticipator in it then there are some things that you need to know about setting it and what it actually does.
First the function of the heat anticipator is to fake the thermostat into feeling the room temperature as hotter than it really is. The heat anticipator is actually a variable output heater inside your thermostat. The amount of heat that it actually produces is very, very small. This heat does, however, make a difference in how the room temperature feels to your thermostat.
If no extra heat is made inside the thermostat it will not react quickly enough to shut off the heating source. This will make the room “overshoot” the set point of the thermostat.
By heating the thermostat up very slightly it then shuts down the furnace or heat source before it actually reaches the temperature set point. This will allow the left over heat to go into the room and raise the temperature to the set point by the time it is all used up.
If you are experiencing wild temperature swings or the room temperatures are either not getting to the set point or going over the set point then the heat anticipator either is not adjusted right or it is burnt out and not working at all.
There are a couple of different types of heat anticipators. They will usually look like one of these.
If your heating is running too long then you will need to adjust the setting to a lower number. If you are not getting enough heat then go to a higher number. All you are changing when you do this is the amount of the heat coil you are using. Make small adjustments to the anticipator and then give it at least a half day before making more adjustments. Small changes can have a big effect if the heat anticipator is working correctly.
You also can set the anticipator by checking the current draw of the system. To do this you need to use an amp meter and measure the current draw of the heating unit when it is running. Then set the heat anticipator to the corresponding number of the current draw. This will at least get you a good starting point and some fine small adjustment can be made from there.
For more advanced digital thermostats there are cycle change features that do what this heat anticipator does in older thermostats. These often incorporate many things in determining the cycle length of the heating. These thermostats will not have a heat anticipator setting.
Like many things when it comes to your comfort, all people feel things a bit differently. You need to make the changes to the thermostat so that YOU feel comfortable. There is no right way it has to be done. Make it work for you and adjust the thermostat so that you are the most comfortable!
http://www.fixya.com/support/r3892721-programmable_honeywell
http://www.fixya.com/support/r3623083-thermostat_wiring_terminal_designations
http://www.fixya.com/support/r3584298-air_conditioning_programmable_thermostat
http://www.fixya.com/support/r3898732-lux_thermostat_500
on Jan 30, 2010 | Heating & Cooling
Bryant Furnace starts up then shuts off
If you have a standard thermostat and not a digital stat, the problem could very well be the 'heat anticipator' setting on the thermostat sub-base. It is a variable resistor that has to be adjusted to match the amp draw of the heating control circuit. In the heat mode, the heat anticipator 'warms' up the thermostat because of the heat generated through the system controls and causes the thermostat to 'anticipate' room temperature setpoint just a little before it really gets there.
If set too low, the result is a short cycle, if set too high, the result is an overshoot in setpoint temperature. The average setting for the anticipator is .4. You should see a very thin 'wire wound' flat resistor under the cover with a thin metallic pointer that physically slides from left to right or right to left. The pointer is pointing to its 'setpoint'. Adjust it up .1 or .2 from its current setting and observe operation for a week or so to see if any appreciable change has occurred.
Mar 22, 2015 | Bryant Heating & Cooling
How do I adjust the heat anticipatory to its proper settings
Look on the gas valve. Or post the make and model
Mar 21, 2013 | Heating & Cooling
My themorsat stop working,and I replaced the batteries.
see this causes and fix it. God bless you
Furnace Produces No Heat Possible Causes
Possible Repairs
  • Remove cover of thermostat and loosen screws holding unit to wall. Level the thermostat. Re-tighten screws and replace cover.
  • To adjust the heat anticipator, please see Heat Anticipator Adjustment.
  • Furnace Turns On and Off Frequently ("short cycling")Possible Causes
  • Dirty thermostat components
  • Heat anticipator not set correctly.
Possible Repairs
Sep 30, 2012 | Honeywell Programmable Thermostat Heater
My Trane thermostat (TCONT600AF11MAA) is supposed to have 1.5 degrees of heat pump "rest" above the desired setting before turning on the heat pump. The thermometer reading does not change yet...
Hope it's helpful?
Jan 02, 2011 | Heating & Cooling
Heater days on for secondary n turns off...stays off for too long...how do I set it to stay on longer periods...
Match the thermostat heat anticipator with your furnace gas valves amp draw. For instance, look on you gas valve and the amp draw is .02 look on your heat anticipator dial and set it for .02
Most wall thermostats do not come preset. The heat anticipator wire is miro thin and can be severed by simply touching 2 24 volt thermostats wires together to check for voltage.
Oct 23, 2010 | Heating & Cooling
The furnace shuts off before set temperture is reached
This could be normal. Some thermostats are designed with a heat anticipator. The anticipator takes into consideration heat that will remain within the system after the burners shut down, it anticipates the "left over" heat will be enough for the thermostat to reach it's setpoint. If it did not have this function the setpoint would be overshot.
If you are suggesting it shuts off well below the desired setpoint please clarify.
Dec 01, 2009 | Honeywell Electronic Programmable...
Programmable T stat
your trane heat pump energizes the reversing valve with O - orange y - is to turn on the unit make sure you have your orange wire hooked up and the tstat programming set to heatpump otherwise your reversing valve might be bad
Jun 30, 2009 | Honeywell Electronic Programmable...
Where does the T Wire go on the RTH7400
the t wire is for an outdoor anticipator reset. If you dont have a terminal on your thermostat it does not have to be used. Just tape it off.