Janitrol furnace. burners ignite then shut off, blower runs but no heat
    Genius:
  • 1,033 Answers
Sounds like a dirty flame sensor. On the opposite side of the Igniter will be a metal rod that is just above the burners, you need to remove this rod and clean it with a steel wool pad. Then reinstall it and turn Furnace back on. If this does not help let me know, it may also be a high limit switch tripping.
Posted on Nov 28, 2012
  • 5 Answers
SOURCE: Ruud Silhouette II Gas Furnace, purges, lights
Flame sensor needs to be cleaned. turn off the furnace power switch or breaker. pull the flame sensor located in the burner runner section of the furnace. It will be easy to locate because it has 1 wire running to it. pull the screw being very careful not to harm anything else. get the sensor out. inspect it for cleanliness. clean the sensor with light grade sand paper gently. re-install the sensor plug the wire back on. restart your furnace and this should fix the problem.
CookHVACR
Posted on Nov 19, 2010
Testimonial: "thanks cookhvacr, took 15 minutes and it seems to be back to normal operation."
carldc3
  • 82 Answers
SOURCE: question on a day and night gas forced air heater
it very well sounds like your fan switch , does your fan work at all, like in ac mode on by turning the fan on/auto switch on the thermostat to ON. If the fan does come on its the more and likely the limit switch. if it doesnt come on it could be the motor or the run capacitor. the limit switch has a dial on it that as it heats up it spins clicking on at a desired set temp ussually about 120 to 150 degrees F. turning on the fan if the fan doen't come in the the next setting clicks off the gas valve turning off the burners ussually set at about 220 degrees F. now if the fan is working when the heater is satisfied there is a setting at about 90 deegrees F. that shuts the fan off hope this helps
Posted on Jan 05, 2009
Therinnaiguy
  • 1420 Answers
SOURCE: Rheem RHQA Heater:Blower works but no heat.
Is there a setting on the thermostat for Auto or Fan? If so, make sure it is in the Auto setting. You will have a contactor that turns on the elements and a relay for the fan. Follow the wiring diagram to see which relay energizes the fan then unplug it to see if the fan stops.
Posted on Nov 03, 2009
  • 11 Answers
SOURCE: Ruud furnace Model URKA A030jK08 Code opt 589
sounds like the circuit running to your condenser powers your furnace. when u disconnect power to the furnace it will reset and run the blower on startup. check the tube connecting the vacuum switch to the induced draft motor. maybe a leak. good luck
Posted on Nov 24, 2009
  • 288 Answers
SOURCE: Goodman furnace burner ignites then shuts off in about 10 seconds
if you have replaced the flame sensor and it will not stay lit, the draft safety switch may be opening. It works on positive and negative pressure created by the inducer fan motor.You may have a restriction in your heat exchanger or if is a high efficiency furnace, it may not have the drain tube installed properly with a trap. The trap works just like the trap under your sink and if water isnt in the trap, the pressures can be effected enough to open the draft switch(some call it an air pressure switch)
Posted on Jan 07, 2010
What's wrong with my furnace?
The relay for the motor is stuck or the points inside the relay are arced closed. Replace the relay.
Apr 26, 2016 | Goodman Janitrol Amana Goodman Janitrol...
Goodman furnace a36-20 fan runs non stop
is green wire from thermostat or from outdoor. retrace and change as needed. If not Goodman has a tech support number you can call while looking at unit.
Jun 21, 2014 | Goodman Heating & Cooling
Burner shut off then there is a clicking sound, burner ignites again
this is normal the clicking sound you hear is the system starting another cycle for your furnace to ignite the burners, then turn on tbe fan blower.
Sep 27, 2017 | Heating & Cooling
Ruud 80 plus furnace
Make sure you give it time. Gas furnaces ignite first and then the fan comes on. It will run for a while to heat the exchanger first. If the fan comes on with the heat it will blow cold initially. The fan also continues to run after the burners shut off to expel the existing heat in the ductwork
Oct 19, 2013 | Heating & Cooling
Johnson air ease furnace blower motor getting hot
Check for correct voltage ,also would check capacitor and motor rotation.
Dec 08, 2017 | Heating & Cooling
Janitrol GUPS075-3 Furnace burners will not stay lit
The first thing I would do is make sure the flame sensor is clean, this is a metal rod immersed in the burner flame on the opposite side of the igniter. If too much oxidation builds up on it, it will not allow the burner to stay lit. To clean, just turn off furnace and remove flame sensor and clean with steel wool and then reinstall. If this does not solve the problem there may be a problem with the gas valve.
Nov 08, 2012 | Heating & Cooling
Draft Inducer problem
On the call for heat from the thermostat the inducer should come on first, a pressure switch proves that the inducer is moving enough air up the stack, closes and energizes the ignition and burners come on. 30 to 60 seconds later the blower comes on. Everything should stay on as long as the thermostat is still calling for heat. When the thermostat is satisfied the burner and inducer shut off and the fan will run to remove the heat from the heat exchanger and then shut off. Cycle complete. Some inducers have a post purge so when the thermostat is satisfied the burner shuts off, the inducer runs for 30 seconds or so and then shuts off. I am thinking that your furnace may be running on the limit switch and when the burner is off but the inducer stays on, maybe the limit is shutting of the inducer. Check your air filter and make sure all your heat registers are open and that the return air grill is not blocked.
Dec 06, 2017 | Heating & Cooling
Our furnace keeps shutting down soon after burner ignites inducer motor stays running wont heat until reset switch behind inducer motor is pushed
Sometimes a "Flame Sensor" gets carboned up and does not detect that the furnace has ignited, so it shuts down the fuel source. Might try cleaning that if so equipped.
Dec 05, 2010 | Goodman GPG152407041 15 SEER Packaged...
Flip the lower panel over and look for a wiring diagram. On that diagram there will be a diagnostic chart. Let me know what 5 blinks represent. Then I want you to read on.
On a call for heat, the 24 volt thermostat sends a signal to the control module. The control module will indicate a call for heat with a light on the control either blinking or remain solid depending upon model. The inducer (exhaust) blower will purge all gasses from the furnace and pressurize a pressure switch. Once the pressure switch tells the module to continue, the electronic ignition will energize and send 120 volts to the igniter. The igniter will glow and you will be able to see it if viewed thru the small inspection port. Once the igniter gets hot enough, it sends a signal to the module opening up the gas valve (24 volts). Either a pilot will come on or the burner tube will ignite then spread the flame to all burners. Lastly a safety sensor will be looking for a certain temperature within a few seconds and the furnace will continue to operate and the room air blower will turn on in a minute or two.
What could go wrong? The unit will not run if there is no signal from the thermostat (bad thermostat or broken wire), the control module does not sense a signal from the thermostat (bad control), the inducer does not energize (bad motor), the pressure switch does not close (blocked vent piping, bad switch, plugged condensate hose), the igniter does not energize (bad control, bad igniter), the gas valve does not open or there is no gas (bad gas valve, broken wire, no gas), the pilot does not light (dirty pilot), the burner does not light (bad burner, plugged orifice, not enough combustion air), the flame does not spread to each burner (bad flame spreader, dirty flame spreader, more bad burners), the flame safety sensor does not detect flame (dirty or bad flame spreader, bad flame sensor, broken wire, bad control), or the room air blower does not energize (bad fan motor, bad control).
Nov 23, 2009 | Heating & Cooling