My furnace wont come out of lock out mode
I have a Heil furnace and when it tries to come on within a second or two of trying to come on it goes into lock out mode. The computer board, limit and roll out switch have been replaced what is causing this problem
  • carl carpenter
    carl carpenter May 11, 2010
    check to see if your pressure switch is working, should see a rubber tube coming from induced draft motor to the switch make sure opening at motor is clear
    President:
  • 1,304 Answers
Check your exhaust and your inducer
if your inducer cant not sence proper air flow
either positive or neg depending on your set up
it will shut down and lock out on safety
Posted on Oct 06, 2009
    Problem Solver:
  • 14 Answers
Pressure swithc stuck closed? try undoing on of the wire going to the pressure switch and see if it stays on longer. Make sure you tested all limit switches there are usually at least 3 and up to 5
Posted on Jul 27, 2009
2 Suggested Answers
Accurate Joe
  • 61 Answers
SOURCE: furnace burner ignites then goes out
Sound like a thermocouple, or flame sensor.
If it has flame sensor make sure you check micro amps to verify operation, because it might be the board that controls the sensor.
Posted on Dec 01, 2008
The pilot light on my heil quaker furnace won't stay lit. I replaced the thermocouple (man was that a task, between the design of the furnace, and its placement in my attic) but that didn't change...
Make sure the thermocouple is clearly in the heart of the flame. Make sure the thermocouple is securely and properly connected to the gas valve. Obviously make sure it is the correct thermocouple. Gas valves do go bad, so it could be that but that is fairly rare. Good luck.
Apr 30, 2017 | Fasco Furnace Draft Inducer Heil Quaker...
I have a Heil furnace (Temp star 9000 I believe) model number NUGS075BG03 that is not working properly. The inducer motor runs fine and I can see a blue flame through the sight glass but the circulating...
you need to check to see if blower motor runs in ac mode, if not then the first thing you want to check is the capaciter for that motor. if capaciter is good, motor may be locked up, you can check the amps of the motor by putting an amp clamp around wires going to blower motor, all ratings should be listed on motor
Oct 17, 2013 | Carrier Icp Heil Tempstar Furnace Blower...
Heil furnace lights but wont stay lit 1990 model
Here is a tip that will help you try to figure out why your furnace is not working.
Basic Furnace or Heating System Troubleshooting
heatman101
Mar 04, 2011 | Honeywell International Heil Quaker...
1990 heil furnace wont light pilot,but air induction fan comes on but unit will work in cool mode
The gas valve is bad and this is a common problem for these furnnaces. I have the same problem. Let me guess its a DC90?
Nov 11, 2009 | Heating & Cooling
Furnace wont start. heil gas furnace. on initial
Yes, inspect the air intake, exhaust pipe, filter and condensate piping for blockage or moisture. Also check for a hole in the hose that goes from the small exhaust blower to the pressure switch or a bad connection on the switch or control board. You may be able to temporalily jump the switch for diagnostic purposes only.
Oct 17, 2009 | Heating & Cooling
Furnace burner ignites then goes out
Dec 01, 2008 | Cross Furnace Draft Inducer Blower 115...