I have a 4 year old furnace, my problem : the furnace shuts down after a while, and will not atart again ; it will start again maybe next day by itself, on the bord it hax the red lite blinking 3 times when the furnace does not work ; when works it has the red light on and a green-yelow light on at same time, a called 2, two specialist, and they could not figure out what is the peoblem . I dont want to buy another furnace, I need help to find out what is the problem? It is Winter and I have no heat!
  • 1 more comment
  • Scott Magill May 11, 2010
    Have you got your problem fixed yet if not reply back and i will give you a couple of things to try. Is this furnace a 90 or 80 % efficiency.What is the brand and model of the furnace.
  • msgshtgn May 11, 2010
    On most furnaces the flash pattern you are describing is a venting issue.. Either your vent is not properly sloped 1/4 inch per foot back towards unit , creating a trap that is collecting condensation from exhaust. or there is a blockage on the vents outside. Your intake pipe can frost up at night creating a blockage then melt in the morning eliminating the problem.. make sure the intake pipe and the exhaust pipe have the adequate distance from each other as specified in your service manual..
  • dwkcool May 11, 2010
    check on the back of the door panels and see if you can find the wiring diagram the flash code should be on it
  • 221 Answers
Defective combustion air switch. The 3 blinks are an error code. You didn't say, but I'm guessing you have a Coleman Evcon. They had alot of defective Combustion air switches. Your specialists were not that.
Posted on Dec 30, 2009
I had the same problem with my Coleman Furnace,code 3 combustion air switch failed to close. It was not the switch,it was the booster motor cover, the head made the plastic cover brittle and it cracked causing an air leak.They should make this cover out of metal!
Posted on Nov 19, 2011
Furnace is 7 years old. Will not stay running for more than 5 min. Will start up again after shutting off and then run for another 5 min. Suggestions?
Check the air filter. Jump out thermostat to see if it stays running longer, if so replace thermostat. Make sure all return air ducts are clear of debris. If furnace has a Fan/Limit switch, make sure tabs are set at 100, 140 and 200. Sounds like something may be heating up and shutting unit off till it cools back down.
Jan 03, 2011 | Ruud Heating & Cooling
In very very cold weather, our furnace is shutting down. Furnace is a lennox, about 17 years old The closest they've come to figuring it out appears to be that it's either overheating, or isn't starting...
I need a little more info I feel certain I can solve the problem I need to know a couple of things.
1- Model # of the furnace, take off the top door look to your right or left you will see a little metal data plate on the top of the plate you will see the model # If it is a horizontal furnace the data plate will be on the same side the controls are on .
2- Is the furnace a natural gas, LP gas, fuel oil or electric?
3- Does it do this when the temperature is above freezing?
4- If you could list the parts replaced it would be helpful.
A furnace properly maintained can last upwards of 25 years.
Dec 09, 2010 | Heating & Cooling
Garage furnace (standing Pilot) pilot stops after 30 mins.
it sounds like the afc the fan control not working could be dust on the afc
Jan 10, 2010 | Dayton Gas Furnace Heater
You will likely need to install an isolation relay in the W circuit from the thermostat. Some thermostats rob a small current through the W circuit to power the thermostat. This small current can be enough to start the fan circuit timer. You can test this by disconnecting W at the furnace and allowing the timer to shut down. If the fan shuts off with the W disconnected you can install a simple relay.
The relay coil will be connected to Common on one side and the W from the thermostat to the other. Then you will run a wire from R on the furnace to the relay and from the N.O. Contacts to the W terminal on the furnace. This will kill that signal that is starting the timer and the W can steal it's power through the coil back to common.
Dec 23, 2009 | Honeywell Electronic Programmable...
Lennox furnace 17 yeanrs old. flame comes on and the shuts down sometimes right away some times in a few minutes. We have the furnace go down to 58 at night. It takes all day to get back to 67.
Sounds like a dirty flame sensor.
Also 9 degrees is a large swing to recover. Most specialist will advise no more than a 5 degree set back, otherwise recovery time eliminates any savings you may achieve.
Dec 05, 2009 | Dayton (3E407) Heater
Furnace runs OK, but blower runs again a few seconds later
Could be a defective thermostat in the plenum.
When a gas furnace shuts down the fan(blower) will run until the plenum cools to the safe range. Usually 1 and 1/2 minutes.
Intermittent operation is a defective thermostat or relay.
Mar 11, 2009 | Carrier Heating & Cooling
Furnace starting
Hint number 1, get HVAC license. One mistake or misunderstanding and you could blow your house up.
Feb 21, 2009 | Heating & Cooling
Furnace burner turns off and on
The furnace is likely over heating and the high temp. safety is shutting it down. It then cools and starts again. Things to check: Filter, Blower wheel and indoor A/C coil. If any or all are dirty you are limiting air flow and need to clean them.
Jan 17, 2009 | Carrier 38CKC042 Air Conditioner
Furnace wont start when thermostat sends signal
by restart button you mean reset i believe,its located on top of oil burner and says only push one time .if thats the button your pushing it is the reset button or retry for oil burner if you are pushing this there is a problem with burner
Jan 04, 2009 | Honeywell Electronic Programmable...
Heating & Cooling Logo
1,380 people viewed this question
Top Coleman Heating & Cooling Experts
Bill Long
Paul Carew
Dan Webster
Dan Webster
Are you a Coleman Heating and Cooling Expert? Answer questions, earn points and help others