Blower fan does not cutoff in gas mode after burner cuts off
    Genius:
  • 1,033 Answers
Hello, sometimes the fan relay will weld shut and cause the motor to run continuesly, in this case the the control board must be replaced since the relay is part of the board. Another possibillity is the thermostat wires shorting togethur between the G and and R terminal. Easy way to check is to unhook the G wire from the G terminal, if the blower stops there is a short, if it does not stop te relay is the problem
Posted on Nov 09, 2012
Problem with Kitchenaid Electric Range Stove Top Burner
there may be a loose connection in either the pipe or on the burner rings on the surface. Some stoves have a safety cutoff if gas supply is interrupted to avoid prolonged gas supply.
May 12, 2012 | KitchenAid KERA807P Electric Kitchen Range
Showing F1 on display boiler makes a thudding noise then goes to F1 mode. Smell of gas.
Hello
Sounds like a low water cutoff switch is stoping burner from lighting.
Check that you have at least 15psi of water pressure on the boiler guage.
Try to reset the cutoff switches.
Nov 08, 2010 | Heating & Cooling
Fan comes one, should hear whooshing of ignition,
On a call for heat, the 24 volt thermostat sends a signal to the control module. The control module will indicate a call for heat with a light on the control either blinking or remain solid depending upon model. The inducer (exhaust) blower will purge all gasses from the furnace and pressurize a pressure switch. Once the pressure switch tells the module to continue, the electronic ignition will energize and send 120 volts to the igniter. The igniter will glow and you will be able to see it if viewed thru the small inspection port. Once the igniter gets hot enough, it sends a signal to the module opening up the gas valve (24 volts). Either a pilot will come on or the burner tube will ignite then spread the flame to all burners. Lastly a safety sensor will be looking for a certain temperature within a few seconds and the furnace will continue to operate and the room air blower will turn on in a minute or two.
What could go wrong? The unit will not run if there is no signal from the thermostat (bad thermostat or broken wire), the control module does not sense a signal from the thermostat (bad control), the inducer does not energize (bad motor), the pressure switch does not close (blocked vent piping, bad switch, plugged condensate hose), the igniter does not energize (bad control, bad igniter), the gas valve does not open or there is no gas (bad gas valve, broken wire, no gas), the pilot does not light (dirty pilot), the burner does not light (bad burner, plugged orifice, not enough combustion air), the flame does not spread to each burner (bad flame spreader, dirty flame spreader, more bad burners), the flame safety sensor does not detect flame (dirty or bad flame spreader, bad flame sensor, broken wire, bad control), or the room air blower does not energize (bad fan motor, bad control).
Jan 27, 2010 | Goodman Heating & Cooling
Unit not producing heat but fan cuts on and off
Most newer unit the fan comes on if the limit is tripped. The limit is located in the blower section and in the burner section.
Jan 05, 2010 | Heating & Cooling
Blower opperation on gas furnace
How long does the burner stay on before the limit takes it out. The board has a delay for the fan in heat and it may be to long. If your unit had cycled on high limit to much it may have a bad limit switch. The limit is so low it cuts out before the fan has a chance to come on. See on the board if has an adjustable time deley. Should 30 60 90 set to thirty. Keep in touch rus
Dec 12, 2009 | Heating & Cooling
Heater Burner ignites but main blower motor will not turn on.
it sound like the blower motor may be seizing up. try spining the blade by hand to see if it feels free or not. the motor could be trying to turn but can then tripping itself out on overload. (most motors have built in safety overloads which will trip during an overcurrant event. aka too many amps.) you may have to replace blower motor
Mar 16, 2009 | Mr. Heater Natural Gas Garage Heater -...
Rheem gas furnace pilot lights, but no burners or fan
If the burners do not fully ignite, the sensor will shut the furnace down. The lack of sufficient burner flame is a gas valve or gas pressure problem within the valve.
Replacing the gas valve with the original one may get you going. I surely suggest a professional service company for safety reasons and a thorough inspection. A 20 year old furnace is past it's normal life span.
Jan 06, 2009 | Heating & Cooling