I have a GMP100 gas furnace. I need the diagnostics table that provides the meaning of the status light states. I get flame for 20 seconds and then the gas is shut off and LED on control board blinks 3 times. The flame sensor looks clean. I wired the flame sensor lead to ground as a quick test but then the gas goes out in 6-7 seconds. Any thoughts?
  • fh_coach Jan 05, 2009
    Thanks but any help on the diagnsotics codes? The table is supposed to be on the back of the furnace access panel but it's missing.
    Seems like it's either a bad sensor or bad control board. Having the diagnsotics table would help me further troubleshoot and would be great to have for future reference.
  • 163 Answers
Hi!!! you just answer your question.change your flame sensor cleaning it wont work..
Posted on Jan 05, 2009
  • lorenzo banks
    lorenzo banks Jan 05, 2009
    change flame sensor..
Error code= two red flashes, lockout/ no flame
Trane XV80 hard lockout, 2 flashes, Can't be reset - DoItYourself ...
www.doityourself.com > ... > Gas and Oil Home Heating Furnaces
Jan 10, 2013 - The only way I can get diagnostic Red LED light to reset is to switch ... a2 flash with absolutely no operation from the furnace does seem to ..... inducer gets a demand you should get a pressure switch error code 3. ... the flame sensor wire and giving the furnace a heating demand after resetting power twice. Luxaire Furnace Blowing Cold - 8 Red LED Flashes
Mar 1, 2010
Winchester furnace diagnostics
Feb 14, 2010
American Standard Freedom 80 - Cold Air - Getting Error Code 9 ...
Nov 20, 2009
York ignition lockout due to retries
Dec 29, 2008
More results from www.doityourself.com
7 Tips and Tricks to repair your Furnace DIY - YouTube
? 13:25
https://www.youtube.com/watch?v=rAtcvPqUsBA
Dec 18, 2012 - Uploaded by JRESHOW .
cause this fault. 2 RED FLASHES: This indicates that thenormally open pressure ... The furnace will lock out for one hour and then restart. 7 RED FLASHES: This fault code indicates that the flame could not be established. This no-light ... problem. Bothheating and cooling operations will be affected. Check
Jan 23, 2016 | Heating & Cooling
Goodman gmp100-3 furnace The furnace will not start when I turn power on. It will hum but no click. The status light is solid red. Could the ignitor be bad? And what color should it be?
You should hear the ignitor pop. If you don't hear that pop sound, then the igniter is bad. They are easy to change, just make sure you turn the gas off and the pit-cock into the appliance and take a photo of exactly where the igniter tip is oriented so you can put the new one in the same spacing to have it ignite properly. The status light should be green when the furnace is 'On.'
May 09, 2015 | Goodman Heating & Cooling
Goodman GMP100-3 home furnace status lite is constant red
check continuity of hot surface igniter....open loop means replace igniter
Nov 04, 2012 | Goodman Heating & Cooling
I have a goodman furnace GMP100-4 REV B..about a year ago it was not working. The fan would start but it would not ignite. We found out we need a new ignitor and it was a good quick easy fix. Now a ye
Any light flashin on the control board? If not then look for a small fuse blown on the board. See lights a flashing count them flashes
A sampling of various failure codes on a furnace:
Read one LED flash that stays on continuously to mean your furnace has no signal coming from the thermostat and will not operate. Turn the power off and check the thermostat for improper settings or connections.
Interpret one LED flash that blinks on and off to mean your furnace has locked out because it could not ignite after three tries, and must be reset. Interrupt power to your furnace for 20 seconds or lower the thermostat so your furnace does not try to heat, then reset the thermostat to the previous setting. After one hour of lockout, your furnace will automatically reset itself and try to operate as usual.
Decipher two LED flashes to mean the draft blower is not working, or your furnace has a short in the pressure switch circuit. Turn off the furnace power and repair a short or replace the pressure switch.
Read three LED flashes to mean your furnace has an open pressure switch circuit or it has an induced draft blower operating. Check the pressure switch hose of your furnace for blocks or an improper connection. Also, look for blockages in the flue, and tighten any loose wiring.
Translate four LED flashes to mean your furnace has a primary limit circuit open, possibly from loose wiring or blocked filters. Check and clean filters, tighten wiring and check the flue for blockages.
Interpret five LED flashes to mean your furnace senses a flame without a call for heat. This could be from a gas valve closing slowly or a burner flame lingering.
Read seven LED flashes as a warning of a low flame sense microamp signal. This could happen with a coated flame sensor or a lazy flame from poor gas pressure. Turn off the power and adjust the gas pressure according to the information on the rating plate.
See eight LED flashes as meaning an igniter circuit problem due to a bad igniter or an igniter connected improperly. Replace the bad igniter or check the ground wiring, making necessary corrections.
Decipher nine LED flashes to mean the high-stage pressure switch circuit will not close during a high-stage-induced draft blower operation. Your furnace may have a pinched or blocked pressure switch hose, a blocked flue or loose wiring.
Read continuous flashing on the LED to mean your furnace has a reversed polarity of 115 volts. Turn off the power and correct the wiring polarity after reviewing the wiring diagram.
Nov 29, 2011 | Goodman Heating & Cooling
Burner ignites but shuts off 2 seconds later?red light blinks 7 times in a row?no heat.
If your pressure switch has ever been replaced, make sure that it was replaced with an OEM pressure switch, because it can cause some strange behavior on your furnace. Check out this video, as this is touched upon in it: Amazon Furnace Parts: http://www.amazon.com/s/?_encoding=UTF8&camp=1789&creative=390957&field-keywords=gas%20furnace%20parts&linkCode=ur2&tag=amznelite-20
Feb 09, 2011 | Dayton Gas Furnace Heater
Currently there is no heat coming from my furnace. Checked my thermastat and it seems to be working fine. Looked at my furnace records,and it indaicated that in 2003 the note said, no heat, BRD, ( not sure...
Will need to know model and seriel of furnace - sounds like a dirty or defective flame sensor. Flame sensor can usually be cleaned by simply wiping it with a slightly abrasive paper, or 0000 steel wool. Most electronic ignition types have a diagnostic code generally located on the ignition control, and depending on the number of "blinks" from the diagnostic light it will tell you why the unit did not fire.
Nov 20, 2010 | Heating & Cooling
Gmp100-4 initer lows and I can hear gas for a few
The red blinking light just means that it went into lock out mode from to many attempts to start. If your igniter is glowing and you do hear the ''hissing'' sound, than your problem is there is no gas or not enough. When installing a furnace for the first time, you some times have to bleed the gas lines, other wise you get the exact same problem your having. If you have a flexible gas line, unscrew one side with the gas on to bleed off the air in the system, if it's all hard pipe, you will have to undo the union and bleed it that way. Hope this helps and good luck!
Mar 13, 2010 | Goodman GMS90703BXA Heater
Furnace tries to light but misfires
Check the air filter.
On a call for heat, the 24 volt thermostat sends a signal to the control module. The control module will indicate a call for heat with a light on the control either blinking or remain solid depending upon model. The inducer (exhaust) blower will purge all gasses from the furnace and pressurize a pressure switch. Once the pressure switch tells the module to continue, the electronic ignition will energize and send 120 volts to the igniter. The igniter will glow and you will be able to see it if viewed thru the small inspection port. Once the igniter gets hot enough, it sends a signal to the module opening up the gas valve (24 volts). Either a pilot will come on or the burner tube will ignite then spread the flame to all burners. Lastly a safety sensor will be looking for a certain temperature within a few seconds and the furnace will continue to operate and the room air blower will turn on in a minute or two.
What could go wrong? The unit will not run if there is no signal from the thermostat (bad thermostat or broken wire), the control module does not sense a signal from the thermostat (bad control), the inducer does not energize (bad motor), the pressure switch does not close (blocked vent piping, bad switch, plugged condensate hose), the igniter does not energize (bad control, bad igniter), the gas valve does not open or there is no gas (bad gas valve, broken wire, no gas), the pilot does not light (dirty pilot), the burner does not light (bad burner, plugged orifice, not enough combustion air), the flame does not spread to each burner (bad flame spreader, dirty flame spreader, more bad burners), the flame safety sensor does not detect flame (dirty or bad flame spreader, bad flame sensor, broken wire, bad control), or the room air blower does not energize (bad fan motor, bad control).
Feb 26, 2010 | Goodman Heating & Cooling
Model #GMP100-4 igniter glows but no gas
Your furnace does have the diagnostic light! Look for it on the control board. There is a small viewing port that you can look into from the outside of the furnace. The wiring diagram will have the codes to help you.
Feb 09, 2010 | Goodman Heating & Cooling
I have a goodman gmp100-4 gas furnace and the gas comes on but shuts off in around 30 seconds, then tries again and the same thing... can i get some help please?
On the last gas venturi tube there should be a flame sensor located in the flame to prove it exsists, if its coroded the spark can,t jump back thru the moisture molecues in the gas to prove it has a flame to tell the circuit board to keep the gas comming. Just reomve the flame snsor and sand itand replace itback. T. Y. V. M.!