I have a goodman gmp075-3 furnace, blower and igniter are working fine but not getting any gas to get furnace going
When i turn on furnace the blower is working good and the igniter is lighting up but not seeming to get any gas flowing.
    Genius:
  • Goodman Master
  • 1,033 Answers
Check if 24 volts is being sent from the board to the gas valve, if not the board is nad and will need to be replaced, if there is 24 volts at the gas vlave terminals then the gas valve must be replaced.
Posted on Nov 28, 2012
  • 108 Answers
SOURCE: goodman gas furnace power vent motor and housing replacement
You need to type GOODMAN GAS APPLIANCES into you browser to find you local servicecenter. I must tell you that Goodman only sells to authorized service companies in my experience. So you become EgKraft Company.
Posted on Nov 07, 2008
SOURCE: Heater element ignites, but turns off before gas begins flowing which stops the process.
clean your flame sensor with a piece of wool
Posted on Feb 27, 2007
aries_67
SOURCE: 1993 goodman status light 4 times blinking
I have a goodman GMP075-3 that won't turn on. I think it is the pressure switch since I do not have a vent blockage. What is a venter and where can I find it??
Posted on Dec 30, 2008
SOURCE: my goodman gmt090-4 shuts off about 10 sec. after burners ignite
Clean the sensor with a piece of fine sand paper. It gets a coating on it after a few years of service. I had my cleaned for $160, it took five minutes.
Posted on Feb 03, 2009
SOURCE: goodman gmnt100-4b wont ignite
I had the same problem. I had to remove a return air duct filter that i had installed and it worked just fine. The system needs plenty of air flow to operate.
Posted on Jun 17, 2009
My goodman GMVC95 furnace circuit board is flashing On 6 I replaced the flame sensor but it's still flashing. Does it have to be manually reset?
Alright, have you checked the low voltage fuse on the circuit board in the blower compartment? Make sure you check the roll out switches as well. If all of these issue appear to be fine then you may have a bad circuit board. There has been a bad batch of circuit boards going around many of the popular furnace brands this winter. Trane Gas Furnaces and Goodman Gas Furnaces have been effected. We sell both brands and have had to replace many circuit boards on new furnaces. Trane Gas Furnaces Installed Goodman Gas Furnace Installation Gaithersburg
Feb 03, 2018 | Goodman Heating & Cooling
Working on furnace. igniter not working even after replacing.
Check flame sensor , check hoses to pressure switch not split etc
Oct 24, 2015 | Goodman Heating & Cooling
I have a Goodman GMS9 furnace. When the furnace starts the induction fan runs for about 15 seconds, the ignitor turns on but thats as far as it goes. The burners do not light and I don't think the gas...
The igniter heats a thermocouple to turn on the gas valve. From your description, the thermocouple may have failed. The noisy stack blower probably needs to be replaced but its controller may be in need of replacement as well.
Nov 01, 2013 | Goodman GMS90703BXA Heater
Gmp075-3 furnace wont stay lit
Sounds like an airflow issue. Is the return air clean? System is not tripping the limit switch with the door off because it's getting all the air it can handle, with door on its not getting enough air???
Aug 15, 2017 | Goodman Heating & Cooling
I have a downdraft Goodman furnace. On only some occasions the blower will start, then after a few seconds I will see the igniter light up, but then I do not get the rush of gas and lighting of the...
It sounds like you got a tough one there.When you say the blower starts up and then the igniter comes on are you refering to induced draft motor or main blower. The proper sequence is for the thermostat to call for heat at which point the induced draft motor should come on and run for 30-45 seconds,then the igniter should heat up for a few seconds then gas valve should open and main burner should light. After limit switch reaches set point for fan on ,blower should come on till after heat has reached thermostat setting then burner should go out, and blower run until fan off setting is reached on limit switch. If your furnace is not following this sequence and then not always doing the same thing in the same order,I would recommend that you change out board again. I have had several problems similar to this with Goodman units and all but one time installing new board solved it. That time I did everything I knew to do and talked to factory service techs repeatedly and finally installed new furnace. As far as your question about insulation,. As long as it is fire proof I can't see where it would hurt anything. Sorry I'm not more help. Good luck and thanks.
Nov 12, 2010 | Goodman GDS80904BNA Open Flame Heater
Thermostat calls and from time to time won't ignite
I would first look at any wire connections both at the furnace and the thermostat. Then I would replace the thermostat. Check the units control board when it does not start for an error code. There should be a small viewing port to look into the furnace cabinet to see the control board.
On a call for heat, the 24 volt thermostat sends a signal to the control module. The control module will indicate a call for heat with a light on the control either blinking or remain solid depending upon model. The inducer (exhaust) blower will purge all gasses from the furnace and pressurize a pressure switch. Once the pressure switch tells the module to continue, the electronic ignition will energize and send 120 volts to the igniter. The igniter will glow and you will be able to see it if viewed thru the small inspection port. Once the igniter gets hot enough, it sends a signal to the module opening up the gas valve (24 volts). Either a pilot will come on or the burner tube will ignite then spread the flame to all burners. Lastly a safety sensor will be looking for a certain temperature within a few seconds and the furnace will continue to operate and the room air blower will turn on in a minute or two.
What could go wrong? The unit will not run if there is no signal from the thermostat (bad thermostat or broken wire), the control module does not sense a signal from the thermostat (bad control), the inducer does not energize (bad motor), the pressure switch does not close (blocked vent piping, bad switch, plugged condensate hose), the igniter does not energize (bad control, bad igniter), the gas valve does not open or there is no gas (bad gas valve, broken wire, no gas), the pilot does not light (dirty pilot), the burner does not light (bad burner, plugged orifice, not enough combustion air), the flame does not spread to each burner (bad flame spreader, dirty flame spreader, more bad burners), the flame safety sensor does not detect flame (dirty or bad flame spreader, bad flame sensor, broken wire, bad control), or the room air blower does not energize (bad fan motor, bad control).
Feb 12, 2010 | Goodman Heating & Cooling
I have a goodman furnace model#GMT045-3A. when I turn it on the electronic pilot works fine and the furnace will start and run about 30-45seconds then shut off. I followed the insructions for restart but...
Jan 26, 2010 | Goodman Heating & Cooling
When I turn my furnace on, the purge blower starts as normal, then after 15 seconds the ignitor starts to glow but when the gas valve should turn on it only turns on for a split second and then you can...
Nov 19, 2009 | Goodman GMS90703BXA Heater
Goodman GMP075-3 ignition problem
bad board,i have had several board failures on goodman
Dec 18, 2008 | Goodman GDS80904BNA Open Flame Heater
Blower works but no heat
If in fact you have the above listed furnace, you do not have a pilot but electronic ignition. You will need to remove the front cover on the furnace, tape down the door safety switch and then have someone help you by turning up your thermostat to a very high setting. Watch and listen inside the furnace. There should be some blinking going on at the control board followed by a small blower fan starting up. Then after 10-15 seconds there should be a click followed by an orange glow viewed thru the viewing window to the burner section. In a few seconds the gas valve should click and the burners will ignite. There is a safety switch that will sense flame and then keep the gas going to the burners. If it does not sense it, it will shut it off within 10 seconds. If all is well so far, your blower will turn on in about 90 seconds after flame. There is a diagnostic code chart on the back side of the access door if you get an error code (blinking) on the control board.
Always check little things like air filter, condensate drain and broken or loose wires.