Replaced Thermostat and now Blower Motor will not run
Greetings, I replaced an original rheem 41-20804-15 thermostat for our rheem heat pump. With a Honeywell RTHL3550D, the cooling worked fine. When I tried the heater, the blower ran for 2 minutes then shut off. I put the original thermostat back and now the blower still does not come on. The whole unit (blower and heat pump) are outside. I checked the fuses and that the unit is getting power. The squirrel cage for the blower turns freely and if i push in on the relay the heat pump fan kicks on. Any suggestions? thx, Rocky
  • Heating & Co... Master
  • 1,655 Answers
Sounds like a set up issue on the tstat. You say this is a packaged unit, inside the machine you should find where the tstat wires hook up. Typically red is power yellow is compressor orange is reversing valve white is emergency heat green is blower. Put red and green together, test blower. Then red green and yellow, make sure blower works again. If blower runs both ways it's either the tstat wire or tstat itself. Make sure you are landing wires on dedicated heat pump terminals, make sure in settings you are set up for heat pump with back up electric heat and TSTAT CONTROLS THE FAN. Good Luck. Also if there is a switch on the tstat for gas or electric on the back you want electric.
Posted on May 12, 2017
  • 1420 Answers
SOURCE: Rheem RHQA Heater:Blower works but no heat.
Is there a setting on the thermostat for Auto or Fan? If so, make sure it is in the Auto setting. You will have a contactor that turns on the elements and a relay for the fan. Follow the wiring diagram to see which relay energizes the fan then unplug it to see if the fan stops.
Posted on Nov 03, 2009
  • 1515 Answers
SOURCE: Honeywell thermostat TH6110D1021. Blower comes on
Hi, You are right, fan is on a time delay in the heating cycle, and after burners fire that is when this delay comes into play. You have a preset factory temperature that determines the cycle on time for the fan, and the off time after the burners shut down also. This will not be in the thermostat, but in the fan/limit control the is mounted on the face of the furnace, with a probe inserted into the fire box.Depending on how old or new this unit is, will depend on the type control you have.It may be just a high limit switch, or the 1st I mentioned.If so, It rotates in the burner as the temperature rises, to turn the fan on and off.Disconnect power, remove cover, and 2 screws.Slowly remove the control and gently clean the probe. Turn the dial if this one has it and you will be able to hear it click. This click is contacts closing to start fan operation.Reinsert and try again. If problem continues, you will have to replace it.They do tend to stick closed/on, in the heat cycle from time to time and a cleaning sometimes will solve this problem. Not knowing how old this furnace is and type, make it difficult to give you a correct diagnosis, so check this fan control as I have explained, and if your system is of a different type, please let me no so I can correct this problem. Sincerely,
Posted on Dec 11, 2009
  • 3162 Answers
SOURCE: Furnace blower fan problem
Hi check out the fan control switch could be dirty itsounds like this is nit cutting to let fan run also check setting fan off fan on , temp rise and fall
Posted on Feb 06, 2010
  • 588 Answers
SOURCE: Outside heating unit runs all the time
Usually when the furnace blower motor runs all the time
The limit switch or rollout switch is usually open or bad.
The furnace board is seeing that one of those switches is open, so it brings the blower on to try to get the heat out of the combustion chamber area, so the switch will close. But if the switch is bad and won’t close, the furnace board will keep the blower running continuously.
Posted on Feb 22, 2010
  • 588 Answers
SOURCE: Heat PumP: Rheem Two Stage Heat, One Stage Cool Thermostat Replac
R = R with jumper to RC hot side of transformer
B = Reversing valve
Y = Compressor relay
G =Blower
C = common on transformer (X on old t'stat)
W2 = Auxillary heat
E = Emergency heat
Posted on Mar 16, 2010
Honeywell com yourhome
Yes, it should work. Old thermo has 4 wires, follow instruction with new thermo.
Jul 22, 2014 | Honeywell Universal Digital...
Will a th5000 work with a ruud dual fuel
Are you talking about a pro 5000 Thermostat??? if so then NO it will not work.With this stat you do not have a temperature lock on the heat pump. Say you don't want the heat pump to run below 25 degrees. it won't shut the heat pump. And you don't want the heat pump to run at the same time as the furnace. With the Pro 8000 3 heat and 2 cool thermostat you can lock out the heat pump at 25 degrees outside an turn the furnace on. You will have to install an outdoor thermostat hooked up to the pro 8000 it usually comes with the stat. Honeywell products.
Nov 29, 2013 | Rheem 3.5 Ton 14 Seer / Ruud 100K Btu 80%...
I am replacing an T8411R with RTHL3550 and I have the following wires. Original vs New G=G,R=R,Y=Y,O=O......? I have a W2 and an E wire that go into different screws on original but no seperate terminal...
C is actually a power wire; it provides power for some programmable thermostats. You don't have to connect it on the new thermostat; cover the end with electrical tape to avoid it causing a short. (If you keep that wire accessible, it will be nice for someone who wants to use another programmable thermostat. The ones which can talk to wireless networks require this wire.)
Do you have a heat pump? That is the only time a thermostat uses an E wire.
The W2 wire should go to AUX (third screw terminal from the left) and the E wire should go to E (second screw terminal from the left). See page 25 (27 on the pdf) of the Quick Installation manual for the RTHL3550. This manual is available from Honeywell at .
I hope this helps.
Nov 03, 2013 | Heating & Cooling
Replaced Bryant T-stat model TSTATBBNB001 with Honeywell t-stat
Your original wiring configuration seems to indicate that you have an air conditioner (not heat pump) and either a gas or electric furnace. If this is the case you may need a different thermostat for your application.
Apr 21, 2010 | Honeywell Heat/Cool Thermostat
B = Reversing valve
G =Blower
W2 = Auxillary heat
E = Emergency heat
Mar 04, 2010 | Heating & Cooling
Wiring diagram to connect programmable Thermo to Heat Pump
I don't know if this will be helpful or not, but I just installed a new Honeywell and the Honeywell customer service guy helped me get the wires done correctly. The number is 800-468-1502.
Jan 05, 2009 | Honeywell Programmable Thermostat Heater
My heat wont turn off
Whan your room is up to temp or room is set at 70 and your stat is at 70 do you hear the stat click off .if not its a bad stat. you will have a little flam on your stat that should go off also
Dec 28, 2008 | Honeywell CT87B ROUND HEATING&COOLING...
Thermostat auto-changeover mode unavailable
when you programed it did you go through all the setup #1-0 ,#3-0 ,#5-5 ,#12-1
Nov 24, 2008 | Honeywell Electronic Programmable...
I tried to replace my digital manual Honeywell thermostat that is only 6 months old (new construction) with a programable thermostat. I followed the instructions marking the wires and connecting them up...
Your "R" terminal is basically your "hot" and your "C" terminal is basically your "neutral" to simplify explanation. The Furnace supplies the "R" power to the thermostat and then depending on what wire the thermostat sends the power back on determines what the system does. The thermostat terminals are as follows "G" is fan, "W" or "aux" is elect heat, "Y" tells the outdoor unit to run, "O" or "B" tells the outdoor unit whether it is heating or cooling, and "E" is emergency heat. "G" should connect from the t-stat directly to the furnace and go no further. "W" or "aux" AND "E" should both connect to your "W" or "W1" terminal in the furnace, there should also be a "W" connection to the heat pump ( this allows the H/P to turn on the elect heat when the unit defrosts) "Y" and "O" or "B" may or may not connect to a terminal in the furnace, usually they just pass through the furnace from the t-stat to the H/P and get wire nutted in the furnace. Now, here is the key. As I mentioned previously "O" or "B", a system will only use one or the other. The entire industry (except for Rheem and Ruud) uses the "O" terminial which has 24v on it when you are cooling and no power when you are heating. Rheem and Ruud use the "B" terminal which is just backwards, 24v in heating and no power in cooling. This is all for a heat pump, If you do not have a heat pump, then disregard the references to "O", "B", "E", and "aux". You will have R-power on red wire, W-heat signal to furnace, G-fan signal to furnace, and "Y" cool signal to outdoor unit.
Jun 08, 2008 | Honeywell Heating & Cooling
Replace Carrier tstatccshp01 builders standard thermostat with Honeywell rth7500 series and wiring not matching Does O wire go to Aux..? fan working but no cool air.
No... Aux. is auxiliary heat strip. This is usually a white or black wire its up to the choice of the installers preferance. O or orange wire. is used to the reversing valve on a heat pump. If you do have a heat pump there is a programing section inside the Honeywell t-stat. which should say heat pump or straight cool, then another section that will ask if you want the reversing valve to energize in heat or cool. most Heat Pump brands energize in cool the exception is Rheem and Ruud they energize in heat.
May 17, 2008 | Honeywell Heating & Cooling
Heating & Cooling Logo
218 people viewed this question
Top Heating & Cooling Experts
Paul Carew
Dan Webster
Dan Webster
Tim Whalen