Question about Coleman Heating & Cooling
Luxaire by York Furnace,Model# G8T10012UHB11A,8 Red LED Flashes = Ignition lockout due to recycles,Has flame for a few seconds then goes off; does it around three times,Fan is working; blowing cold air
WHERE CAN I BUY REPLACEMENTS PARTS FOR THE SAME MODEL # G8T10012UHB11A
Posted on Dec 10, 2013
5 Suggested Answers
The HVAC Guy
  • 30 Answers
SOURCE: Coleman Evcon Furnace Model G8T10012UHB11A
you probably have a cracked heat exchanger which is causing the rollout switches to trip.even the tiniest of cracks will cause the fan to blow the flame back into the unit and cause them to trip. check the heat exchanger for even the tiniest of cracks if so replace it. and be sure to have a carbon monoxide alarm in your home.
Posted on Oct 30, 2008
  • 744 Answers
SOURCE: carrier furnace model # 58PAV090-14 fan runs but
See the link:
http://hvac-talk.com/vbb/showthread.php?t=77420
Posted on Mar 19, 2009
  • 534 Answers
SOURCE: Furnace blows cold air, ignitor won't glow.
ok this is going to sound funny but it seems as though the polarity is reversed going into your furnance. to correct this proiblem you first need to unplug the unit and where the cord goes into the furnance at that connection disconnect the two wires. Once theses are disconnected switch the wires .All you are doing is reversing the way the electricity flows into the circut board. I would wager that is the problem
Posted on Apr 16, 2009
shastalaker7
  • 1515 Answers
SOURCE: I have a ruud furnace/airconditioner
Hi, this motor is the inducer motor, which is the first thing to start on a call for heat. Everything seems to be going through its sequence of operation just fine, but then shutting down on a safety. Look on the panel for a chart that should tell you by the number of flashes and color of the leds what is wrong. It is locking out for some reason, could be several of many. Next to the pilot, you will have a flame sensor. The metal tip sets in the pilot flame. When they get dirty, they will cause the furnace to do just as you say, run and then lock out. You can take a piece of sanding cloth and sand the metal tip on this flame sensor. If this is the problem, it will start and stay running. Also, look for this chart I have told you about, as it is there to help you locate which safety is giving you the problem. My bet is the flame sensor. Please keep me posted, and rate me on my help to you. The flame sensor also has a electrical lead that is attached to it going to the board, so you will see it.
Sincerely,
Shastalaker7
A/C, & Heating Contractor
Posted on Jan 06, 2011
Error code= two red flashes, lockout/ no flame
Trane XV80 hard lockout, 2 flashes, Can't be reset - DoItYourself ...
www.doityourself.com > ... > Gas and Oil Home Heating Furnaces
Jan 10, 2013 - The only way I can get diagnostic Red LED light to reset is to switch ... a2 flash with absolutely no operation from the furnace does seem to ..... inducer gets a demand you should get a pressure switch error code 3. ... the flame sensor wire and giving the furnace a heating demand after resetting power twice. Luxaire Furnace Blowing Cold - 8 Red LED Flashes
Mar 1, 2010
Winchester furnace diagnostics
Feb 14, 2010
American Standard Freedom 80 - Cold Air - Getting Error Code 9 ...
Nov 20, 2009
York ignition lockout due to retries
Dec 29, 2008
More results from www.doityourself.com
7 Tips and Tricks to repair your Furnace DIY - YouTube
? 13:25
https://www.youtube.com/watch?v=rAtcvPqUsBA
Dec 18, 2012 - Uploaded by JRESHOW .
cause this fault. 2 RED FLASHES: This indicates that thenormally open pressure ... The furnace will lock out for one hour and then restart. 7 RED FLASHES: This fault code indicates that the flame could not be established. This no-light ... problem. Bothheating and cooling operations will be affected. Check
Jan 23, 2016 | Heating & Cooling
5 u code is on how to fix it
Gas furnace fault or error codes for common furnaces - Gray ...
www.grayfurnaceman.com/-ifc-failure-codes.html
Here are error codes found on many York, Trane, Luxaire, Lennox, Carrier, ... If younotice 5 red colored flashes on your York Furnace, it signifies that your
Oct 03, 2015 | Cars & Trucks
The furnace control on a York furnace is locking out due to unable to ignite flame
possibilities are many, no spark due to ng ignitor, if draft induced , fan not coing on or has blocked flue, if unit is condensing type might have condensate in drian line, if standing pilot type thermo couple bad so not sensing pilot. so you see not enough info of what type unit you have to help narrow down possibilities
Nov 12, 2013 | Heating & Cooling
It sounds like you have a dirty or bad Flame Sensor. They sometimes get a white coating on them. It's not detecting a flame so it shuts off. Sometimes you can clean them and they will work.
Nov 06, 2012 | Coleman Heating & Cooling
I have goodman GMP series furance the furnance and gas comes on and fires up then goes out flame sensor is good what else could be wrong
Improper ground from control to burner.
Incorrect electrical wiring, check polarity.
Tubing partially clogged between inducer and proving switch.
A sampling of various failure codes on a furnace:
Read one LED flash that stays on continuously to mean your furnace has no signal coming from the thermostat and will not operate. Turn the power off and check the thermostat for improper settings or connections.
Interpret one LED flash that blinks on and off to mean your furnace has locked out because it could not ignite after three tries, and must be reset. Interrupt power to your furnace for 20 seconds or lower the thermostat so your furnace does not try to heat, then reset the thermostat to the previous setting. After one hour of lockout, your furnace will automatically reset itself and try to operate as usual.
Decipher two LED flashes to mean the draft blower is not working, or your furnace has a short in the pressure switch circuit. Turn off the furnace power and repair a short or replace the pressure switch.
Read three LED flashes to mean your furnace has an open pressure switch circuit or it has an induced draft blower operating. Check the pressure switch hose of your furnace for blocks or an improper connection. Also, look for blockages in the flue, and tighten any loose wiring.
Translate four LED flashes to mean your furnace has a primary limit circuit open, possibly from loose wiring or blocked filters. Check and clean filters, tighten wiring and check the flue for blockages.
Interpret five LED flashes to mean your furnace senses a flame without a call for heat. This could be from a gas valve closing slowly or a burner flame lingering.
Read seven LED flashes as a warning of a low flame sense microamp signal. This could happen with a coated flame sensor or a lazy flame from poor gas pressure. Turn off the power and adjust the gas pressure according to the information on the rating plate.
See eight LED flashes as meaning an igniter circuit problem due to a bad igniter or an igniter connected improperly. Replace the bad igniter or check the ground wiring, making necessary corrections.
Decipher nine LED flashes to mean the high-stage pressure switch circuit will not close during a high-stage-induced draft blower operation. Your furnace may have a pinched or blocked pressure switch hose, a blocked flue or loose wiring.
Read continuous flashing on the LED to mean your furnace has a reversed polarity of 115 volts. Turn off the power and correct the wiring polarity after reviewing the wiring diagram.
Oct 18, 2011 | Goodman GMS90703BXA Heater
My central heating is on lockout and the burner is with red light
A sampling of various codes on a furnace
Interpret five LED flashes to mean your Goodman furnace senses a flame without a call for heat. This could be from a gas valve closing slowly or a burner flame lingering.
Dec 02, 2010 | Heating & Cooling
What are the carrier 8000ts led error codes?
They are listed inside the front panel of the main unit.
LED CODE
EACH OF THE FOLLOWING STATUS CODES IS A TWO DIGIT NUMBER WITH THE FIRST
DIGIT DETERMINED BY THE NUMBER OF SHORT FLASHES AND THE SECOND DIGIT BY
THE NUMBER OF LONG FLASHES.
STATUS
11 NO PREVIOUS CODE - Stored status code is erased automatically after 72
hours. On RED LED boards stored status codes can also be erased when power
(115 VAC or 24 VAC) to control is interrupted.
12 BLOWER ON AFTER POWER UP (115 VAC or 24 VAC) -Blower runs for 90
seconds, if unit is powered up during a call for heat (R-W closed) or R-W opens
during blower on-delay.
13 LIMIT CIRCUIT LOCKOUT - Lockout occurs if the limit or flame rollout switch is
open longer than 3 minutes.
- Control will auto reset after three hours. - Refer to #33.
14 IGNITION LOCKOUT - Control will auto-reset after three hours. Refer to #34.
21 GAS HEATING LOCKOUT - Control will NOT auto reset.
Check for: - Mis-wired gas valve -Defective control (valve relay)
22 ABNORMAL FLAME-PROVING SIGNAL - Flame is proved while gas valve is
de-energized. Inducer will run until fault is cleared. Check for:
- Leaky gas valve - Stuck-open gas valve
23 PRESSURE SWITCH DID NOT OPEN Check for:
- Obstructed pressure tubing. - Pressure switch stuck closed.
24 SECONDARY VOLTAGE FUSE IS OPEN Check for:
- Short circuit in secondary voltage (24VAC) wiring.
31 PRESSURE SWITCH DID NOT CLOSE OR REOPENED - If open longer than
five minutes, inducer shuts off for 15 minutes before retry. Check for:
- Excessive wind - Proper vent sizing - Defective inducer motor
- Low inducer voltage (115VAC) - Defective pressure switch
- Inadequate combustion air supply - Restricted vent
- Disconnected or obstructed pressure tubing
- Low inlet gas pressure (if LGPS used)
If it opens during blower on-delay period, blower will come on for the selected
blower off-delay.
33 LIMIT CIRCUIT FAULT - Indicates a limit, or flame rollout is open. Blower will
run for 4 minutes or until open switch remakes whichever is longer. If open
longer than 3 minutes, code changes to lockout #13. If open less than 3 minutes
status code #33 continues to flash until blower shuts off. Flame rollout switch
requires manual reset. Check for: - Restricted vent
- Proper vent sizing - Loose blower wheel - Excessive wind
- Dirty filter or restricted duct system.
- Defective blower motor or capacitor. - Defective switch or connections.
- Inadequate combustion air supply (Flame Roll-out Switch open).
34 IGNITION PROVING FAILURE - Control will try three more times before lockout
#14 occurs. If flame signal lost during blower on-delay period, blower will come
on for the selected blower off-delay. Check for: - Control ground continuity
- Flame sensor must not be grounded
- Oxide buildup on flame sensor (clean with fine steel wool).
- Proper flame sense microamps (.5 microamps D.C. min., 4.0 - 6.0 nominal).
- Gas valve defective or gas valve turned off - Manual valve shut-off
- Defective Hot Surface Ignitor
- Inadequate flame carryover or rough ignition
- Green/Yellow wire MUST be connected to furnace sheet metal
45 CONTROL CIRCUITRY LOCKOUT Auto-reset after one hour lockout due to;
- Gas valve relay stuck open - Flame sense circuit failure
- Software check error
Reset power to clear lockout. Replace control if status code repeats.
If status code recall is needed, briefly remove then reconnect one main limit wire to display
stored status code. On RED LED boards do not remove power or blower door before initiating
status code recall. After one status code recall is completed component test will occur.
Thanks for Choosing FixYa.
Kelly
Oct 05, 2010 | Heating & Cooling
Meaning of rudd furnace trouble codes
Error Codes
A green LED indicates system faults
Steady On: System OK
Steady OFF: Board control fault or no power applied
1 Flash: Ignition failure (control in one-hour lockout)
2 Flashes: Pressure switch fault, fails open (switch is
stuck open)
3 Flashes: Limit switch open (main or auxiliary)
4 Flashes: Pressure switch fault, fails closed (switch is
stuck closed)
A yellow LED indicates flame status
Steady on: Normal flame is sensed
Flashes: As flame weakens, frequency of LED flashes
increases
Dec 12, 2009 | Heating & Cooling
GMP050-3 heater, gas turns on and lights for 5-7 seconds and just as thr igniter goes dim the gas shuts off. after 3 cycles the erd LED flashes on/off at a 1.5 seconds on and 1.5 sec off Gary
After the gas turns on, it is the flame sensor's job to see that ignition took place and send 24v to the gas valve. If it does not do this, the gas valve shuts down as a safety precaution. After 3 tries, the furnace will go into "lockout" and will not let it attempt to start again. The lockout can be resolved by turning off the power to the furnace for a couple minutes and then turning it back on. Sounds like the real problem is a faulty flame sensor not sending 24v to the gas valve. Sometimes they can be cleaned with a piece of sandcloth. This will cure failure to recognize the flame due to carbon build up on the sensor. Otherwise, the sensor will need to be replaced. Hope this helps!
Dec 16, 2008 | Goodman Heating & Cooling
Oct 25, 2008 | Heating & Cooling
Heating & Cooling Logo
719 people viewed this question
Top Coleman Heating & Cooling Experts
Bill Long
paulcarew
Dan Webster
Dan Webster
Are you a Coleman Heating and Cooling Expert? Answer questions, earn points and help others