Bryant gas furnace model 350mav code 13 - Heating & Cooling
  • 659 Answers
SOURCE: my bryant gas furnace 4
One of your limit switches has tripped. You will find 2 wires terminating to a small disk about the size of a dime or penny. Between those wires is a small button, depress firmly to reset it. You will have anywhere from 2 to 5 of these and you need to reset all of them just in case. If that doesn't seem to be the issue, then it is probably a power failure of some sort. Is the unit getting power? Is the transformer working and the output rating will be 24 volts? If it is not getting power, check you power cord and make sure it is in good condition, check the switch that is located under the blower door, check for a 3 amp fuse on the control board. That just about covers most common problems with gas furnaces.
Posted on Apr 17, 2009
  • 360 Answers
SOURCE: Code #33 on Bryant 355MAV 90i Furnace
Make sure the unit is properly set up (jetted/orifices) for LP. It sounds to me like the unit is setup for natural gas and is being used on propane.
Posted on Mar 01, 2009
  • 96 Answers
SOURCE: Induced draft motor
The inducer motor is what takes the cabonmonoxide out of the house from the unit and should not be bypassed
Posted on Mar 08, 2009
flatech
  • 111 Answers
SOURCE: bryant programmable thermostat will switch on furnace
Turn the power off to the Air handler unit.
Remove the thermostat from the wall, (Just the face part).
Look on the back side of the thermostat and verify that the jumpers are set to electric and not gas, otherwise the fan will not run during heat mode, they come from the factory usually set for gas.
If this is a electric heater this will solve your problem, If it is gas then it will be more detailed. Once you put it back on keep in mind that most thermostats have a 3-5 minute delay so just give it a little time and the fan should then work once you have the jumpers in the correct position.
FlaTech
Thank you for using FixYa!
Posted on Nov 17, 2009
shastalaker7
  • 1515 Answers
SOURCE: bryant furnace codes
If you have a Bryant split system, that is gas fired, and you are having a problem with it because of a flashing led, you need to remove the panel to excess the glued on chart that will tell you what the code is according to the amount of flashes its showing you. You may have 2 long flashes and one long, or something different? Look at the chart inside, and it will tell you what is wrong.
Sincerely,
Shastalaker7
A/C, Heating Contractor
Posted on Nov 21, 2010
WIRING DIAGRAM FOR BRYANT 127ANA036-A
The blue wire from the Ac goes to the y2 on the board for the furnace the yellow and brown goes to c on the board for the furnace and the last wire goes to y1 on the board for the furnace
Jun 16, 2014 | Bryant 462AJC021BA Air Conditioner
Furnace error code 42
have to know the model and serial of the furnace.
locate code list usually inside or on the back of a door.
Operation sequence= call for heat--inducer blower motor--makes pressure switch--signals board to bring on hsi--after a set time gas valve opens and you have ignition--main blower motor comes on after a set time
Feb 12, 2014 | Heating & Cooling
Bryant Furnace 350MAV code 31
Probably a failure of the draft inducer fan motor, draft inducer blower, or the pressure switch that senses the operation of the draft inducer.
Oct 25, 2013 | Heating & Cooling
I have a Carrier model # 58MXA080-F-15112. I think my furnace is 30 plus years old. it isn't heating properly. The blower turns on and sometimes the flames come on, but sometimes they don't. As...
A 13 code means the furnace cycled on limit more than three times consecutively and is in a lockout for 3 hours. A 14 is ignition lockout. An ignitor does not intermittently quit working. I'm the service mgr at our shop, and I know that particular furnace model has a service bulletin out on bad secondary heat exchangers. If your lucky the filter is dirty, or the furnace condensate trap or drain is clogged. Most likely the secondary heat exchanger is plugged up and isn't allowing the pressure switch to make. Or the furnace is overheating due to it not being able to properly vent hot gas. Which would explain the high limit lockouts. Call an authorized carrier dealer so you can take advantage of the free heat exchangers and the $300 labor credit. You can also call an authorized Bryant dealer to perform the work for you. Only an authorized dealer can rectify this problem because the Bryant corp requires testing and paperwork in order to get your free parts and labor credit.
Good luck.
Dec 23, 2012 | Heating & Cooling
Control board
Hello, check to see if the board is receiving 120 volts at the L1 and neutral terminals, if you are then the board will need to be replaced, if you are not getting power then trace the wirimg back to where the voltage stops, for example could be a bad door switch, fuse, circuit breaker. If it is the board then just write down where all the wiring goes or sketch it out on a piece of paper and then remove the board and take it to a Hvac supply store, that way they can match it up for you and get the exact board you need.
May 08, 2012 | Heating & Cooling
I am trouble shooting a Bryant Hi-bred system that uses an air cooled heat pump with high efficiency gas furnace for backup and low ambient operation. How does the system decide whether to use the air...
Your t-stat should be set up so that the furnace is the second stage heat and also emergency heat. First stage (heat Pump comes on) sometimes they use Time to start 2nd stage, sometimes they use outdoor temp and this all bepends how bryant has set it up, without a model # I cannot tell you but send it and i will look in somebooks i have to tell you.
Mar 01, 2011 | Bryant Heating & Cooling
Bryant furnace plus 90 led code is blinking once then 3 times fast. What does it mean?
these codes are on the inside panel of the front cover of the furnace. lift off and look inside.there should be a code explain chart on the panel by the light. this panel will need to be replace correctly for the furnace to work as there is a door switch.
Jan 31, 2011 | Heating & Cooling
Induced draft motor
Mar 08, 2009 | Carrier Heating & Cooling
Heating & Cooling Logo
336 people viewed this question
Top Heating & Cooling Experts
Paul Carew
Dan Webster
Dan Webster
Donni Steen