Rheem super quite 80 ignites and shuts off after 5 seconds or so, Here is what e have done: have 2 units so swapped the pressure sensor, flame sensor and manifold lit switch. all work fine in the other unit. checked ground and voltage ( 120 ) to the flame sensor. Checked poarity and everything else in the trouble shooting guide. Cleaned the unit checking for gas obstruction and dirt in the manifolds. Replaced all air filters. 2 units share exhaust so doubt blockage in vents as other unit would have an issue as well.Flame is strong, blue and all burners are lit. About ready to replace the IFC as we are basically out of options. Also should mention, no amber light. This all occurred after hurricane sandy and no power for 5 days. Unit fired up and heated for abou 30 minutes after powre restored before the problem started. Will check the roof tomorrow but doubt any issue. Could the storm have caused an issue or emerely coincidence?
  • jack dagnese Nov 07, 2012
    Thank you for you helpful; insight. I ahve not replaced the board yet even though it is getting quite cold here in on Long Island. Hurricane Sandy and lack of power etc for 5 days has made us tough. Anyway, can advise as follows:
    1) Single flame sensor - have rechecked the voltage which should be between 70 - 120 v from what I know. Reading 24 or 48 v. Meter is a light up type not digital so cannot tell you the exact voltage only that it does not go beyond the 48 v light. Sngle wire from sensor leads to a mutliple ( 9 ) wire molex connector which joins another molex connector at the junction of the upper/lower unit. Have checked the connections etc at all points and they appear to be in good order. Trust that the low voltage to the sensor is the fault but if so, what is the reason/fix for this.
    2) The curent flame sensor was swapped out from my other unit ( 2 zone ) so I know that it is good. In addition the one that I removed from the non working unit is working just fine in the other unit as were all other parts.
    3) The flame is robust and blue, covers all burners with no jump etc. Looking at the 2 units, the does not appear to be any difference in the flame between the 2 units.
    4) I removed all filters to see if the improved air flow would help but it did not. Both units share an exhaust meeting the at a point above the units to the exhaust ipie. Checked the roof and it is clear up there and has a mesh cover to prevent critters etc. Is it possible that the exhaust manifold could have a clog? How about the pipe from the unit to the main pipe to the roof?
    5) Confirm that we checked for therm for problem by bypassing on the IFC. Jumper from r to w with therm wires disconnected yielded same result.
    6) Checked all gas conections for leaks and burners for clogs. All are clear and in fine working order. Again, the unit ignites, with robust flame and strong surge, but cuts out. All gas pipe is black iron with no copper anyweher.
    based on the above, I am convinced that it is either the low voltage and or blockage. We have no error code, except lock out after multiple failure trips it, robust flame with no amber light sensing same. I am really keen to know what the low voltage to the flame sensor may be caused by and fix as suspect this to be the cause. keep in mind that all grounds have been checked multiple times as well as polarity. Limit switches have all been checked except the blower motor which should not be a cause here. Appreciate your assitance and look forward to further feedback.
  • jack dagnese Nov 08, 2012
    Confirm that is was the board. After swapping, unit fires up and works as it should.
meBNme
  • 334 Answers
SOURCE: heater problem
The first thing I would look for is a blockage in the gasline, or at the gas valve.
It sounds like you are not getting gas to the ignitor/burners. This would cause it to obviosly, not sense flame.
When a unit does not sense flame, it will shut of, and usually try again up to 5 times (depending on brand/model)
So here's what happens in that scenario.
Call for heat.
Inducer motor kicks on, the sensor detects the inducer motor is working, and the ignitor starts glowing/sparking (depending on type of ignitor)
It will then send gas through the gas valve and ignite.
If the flame sensor does not detect flame, the glow coil shuts down, the gas shuts off, the inducer shuts off and you get your error code.
(Some units will then send on the blower motor, and you have to cut power to reset.)
Do you have a copper line with natural gas?
If so, replace it with stainless steel or black iron.
Coper apearantly reacts with the aditives in natural gas and tends to form a gray ashy substance that builds up in the copper tubings walls and eventually cloggs gas valves.
At the inlet side of the gas valve, there should be a screen to catch such things.
Turn off the gas, turn of the power, and remove the gas line going to the gas valve. Look for anything clogging that area, also look for kinks in the gas line.
Remember to use a "flamable gas approved" pipe dope or thread tape when reinstalling the supply line.
Lets see what you find there and then we can continue the diagnostic if needed.
Posted on Dec 10, 2008
bobsteelesp
  • 22 Answers
SOURCE: LP Ruud furnace achiever 90+. Strange problem.
Sounds like two problems. Not enough combustion air or a defective high temperature limit switch. You enclosure may not be getting enough outside air to properly sustain combustion. If the unit has a rollout thermostat it may be defective and stopping everything.
Posted on Oct 10, 2009
gear001
  • 59 Answers
SOURCE: Goodman GMNT 60 Furnace. Burners shut off after a
No, the board isnt out. The board has a code telling you that its out. Its your flame sensor. You wouldn't have gotten any heat if the gas valve was out. check if that flame sensor goes to another sensor on the same circuit , if it does check that. If it just a one wire sensor make sure its in the right position. If its a one rod flame senor with one wire I would sand it down with sandpaper. if its a two wire senor ohm it out to see if you ger current going through it.
www.fastacservice.com
Posted on Oct 16, 2009
heatman101
  • 43501 Answers
SOURCE: Burner ignites and goes out (Goodman Gas-fired furnace)
The problem you have is water in the exhaust pipe.
Check to see if the pipe has sagged anywhere or if there is a trap in the line.
If you hear gurgling then it is definetly water....
Some times can be hard to find, even a pipe 1/4 full will cause problems. They are very sensitive to flue problems.
Make sure that the flue pipe either runs back to the furnace or out to the outside, a continuos slope either way witha high spot in the middle.
Also check the bottom drain of the blower if it has one, have had them plug and trap water also..
I hope that this will help you to solve your problem!
Thanks for using Fixya!!
Heatman101
Posted on Dec 24, 2009
  • 2517 Answers
SOURCE: GMNT080-4B Goes into lock after 20 minutes or so of operation
Hi jump out the presure switch see if it lights check fan control is clean at the back of it check air filter is clean
Posted on Feb 22, 2010
Rheem super quiet 80 turns on lights up for 5 or 6 seconds then shuts down then repeats once i replaced the flame sensor still does same thing?
Three possible problems come to mind. A dying inducer motor, or a partially obstructed exhaust vent could do that; bypass your pressure switch to find out. Also, and this one is trickier, it is possible that the flame isn't hitting the flame sensor just right. Adjusting those brackets can be a pain, and there is no easy test to eliminate that. Finally, real or perceived overheating of the exchanger can cause short-cycling. A bad high limit can do that, or you can run your unit fan on medium or high windings to trick it for now.
I would try testing in that order.
Nov 24, 2016 | Heating & Cooling
LX2000 gas furnace. It starts and runs for about 5 seconds, then why does it shut off?
Fix Furnace Flame Sensor (Flame That Goes Off) - YouTube
? 1:22
https://www.youtube.com/watch?v=fBJ3r9MUa-U
Nov 29, 2011 - Uploaded by RochNoure
A Furnace Flame Sensor is a safety device that reads the temperature and ... easy fix, but the furnace is ...
Troubleshoot the ignitor of the Rheem RGDA model gas ...
? 5:53
https://www.youtube.com/watch?v=Bx1pXONg2Oc
Dec 12, 2012 - Uploaded by grayfurnaceman
Troubleshoot the ignitor of the Rheem RGDA model gas furnace.... Jun Sim 5 months ago ... My lennox ...Missing: lx2000
Rheem Criterion II No Heat - YouTube
? 0:47
https://www.youtube.com/watch?v=yOSk6qvpWbA
Jan 7, 2010 - Uploaded by Work12Progress
Rheem Criterion II gas furnace model # RGPH-07EAMGR. When a call for heat is made t wo green led's ...Missing: lx2000
Heater will not kick on unless... [Archive] - Self Help Forums
www.selfhelpforums.com/archive/index.php/t-2153.html
Oct 19, 2004 - 25 posts - ‎9 authors
After a certain amount of time of not running, the heater will refuse to kick back on. ... 2 flashes, then a 2 second pause = pressure switch is open. What do .... On LP gas furnaces, the spark starts and the gas valve opens. ... Buffing them up with a little steel wool (5 minute job) is a good annual PM thing to do.
Dec 16, 2015 | Heating & Cooling
I am getting an ignition lockout code on the digital readout. what would be the cause? it sparks and calls for heat and will fire for about 2 seconds and then the ignition lockout code is displayed as the...
Ignition Lockout on this unit means #1 that it is set up on propane. If you are low on propane, or were low on propane and just refilled, low/no gas pressure could be the issue. If you ran out of propane, thre is now air in the gas line that needs to be fully blead out.
If propane level is not the issue, replace the ignitor.
The ignitor on these units is also the flame rectifier (flame sensor). If the unit is firing up, but the computer thinks that it is not, then it is not sensing a flame. Replacing the flame rectifier/ignitor will fix the problem in this case.
Jul 07, 2011 | Rheem M206A 206K BTU Pool and Spa Propane...
Rheem RTG-64DVN model, brand new unit installed during the weekend. fired up but shout down automatically within about 5 seconds. showed error code 12.
contact your gas company if the error code is "12," indicating that the gas supply was interrupted.
have a good day !! In LP models, the 12 error code may also appear if the LP gas supply has gotten low. To clear the code, replace or refill the LP gas supply.
go here for a list of codes for rheem tankless water heaters-- www.ehow.com/list_7833182_error-rheem-gas-water-heater.html
May 09, 2011 | Rheem Tankless Hot Water Heater...
RHEEM CLASSIC QUIET 80 HEATER MODEL RGLN-07EAMER AUTO INGITER WORKS BUT BURNER WILL LIGHT AND GO OUT 2 SECONDS AFTER LIGHTING. WHAT SHOULD I TRY?
Hello, check the flame sensor, this is a metal rod on the opposite side of the igniter. Turn off power to the furnace remove flame sensor and clean it up with some steel wool, then reinstall and turn power back on to the furnace.
Mar 24, 2011 | Heating & Cooling
Paloma (Rheem) tankless water heater 7.4 gpm 199,000 btu outdoor unit. Red light is blinking on pc board. unit fires up for approx 2 seconds then shuts off, then cycles once more for 2 seconds and shuts...
i think your flame sensor is bad but you will need to confirm that with rheem i am unsure what the c7 is for but code 12 is flame failure and there could be carbon build up on the flame rod...
Aug 06, 2010 | Rheem Tankless Hot Water Heater...
Rheem Classic Series Super Quiet 80 gas furnace problem
I have this same POS model. It is not the thermostat. this model is just garbage and cant wait to get something that works right. i have been fighting this thing for 4+ years now.
Dec 25, 2009 | Heating & Cooling
Rheem powervent ignites then goes out, electronic ignition.
Sounds like a bad thermocouple. This part sends a millivolt signal to keep the gas valve open but shuts it off when it cools - or if something goes wrong with the ignighter - to prevent fires. It's easy to replace and not super expensive. See your local Rheem dealer.
Aug 13, 2009 | Water Heaters
My rheem quiet 80 ignition flame keep going out. it'll turn on and then go out.
I have a Rheem Classic 80 furnace that would ignite but not stay lit. Cleaned the ignition sensor which was easy to get to and the flame sensor which was under the burner plate and it fired up and stayed lit. The flame sensor was about 6" under the burner plate. Easy to get out, but tough to get back in. Used the old piece of paper shim trick to get the screw to "stick" in the socket and it was much easier to position the screw and get it back where it belonged.