My Carrier gas furnace (ser. 1903A41848) located in the attic, is five years old and suddenly won't light. IT cycles the fan when I cycle the power to the unit and seemingly attempts to ignite through 3 auto-attempts, (I can smell the gas), yet no continuous operation with heat occurs afterwards. Two lights exist on the exhaust vent both begin green yet one turns red after the ignition attempt. Please let me know your thoughts. -Doug
  • 70 Answers
The igniters bad or if unit ignites the flame sensor is bad try this first
Posted on Jan 04, 2009
Try the fuse ,check the ignition element .do You have a drip leg on your gas supply line just before the gas pipe enters the furnace .if not your gas valve maybe folded .
Gas furnace short cycles 2 minutes or less. Multiple troubleshoot steps and replaced components - no help. Any advice?
I did not see that your indoor fan motor started. Near your indoor fan motor there is a temperature switch that is called the fan delay relay. On a temperature rise the relay shuts a contact that turns on the indoor fan motor. If the contact does not close the high temperature limit will shut the gas controls off like your getting. A fan delay relay also allows the fan to run a minute or so to carry away the remaining heat in the furnace and help cool the furnace down. The fan delay relay is normally mounted in a recessed area in the fire wall of the furnace plate. I have also seen them on the top of the furnace heat exchanger. Anyway, the fan delay relay will probably not be available on a sunday, so temporarily until parts are available, try turning the thermostat fan from auto to on and try the furnace again. By turning on the fan to on the high temp limit will not shut you down again.
I have had high temp limit change there trip points, but you said you bypassed it and did the same thing.
Another cause could be using the wrong type of air filter. The new pleated filters sold block to much air flow. If air mass flow rate drops the difference in temperatur go up and when the difference in temperature go up, it gets nearer the high limit and causes it to trip. All pleated filters drop normal air flow through ducts by at least 35%. To make your air duct system work properly use the what is called throw away filters which cost about 1/3 the cost of the pleated filter. Remember to either clean or change the throw away filter monthly to reduce dirt being drawn into your duct system.
Hope this helps.
Feb 13, 2015 | Heating & Cooling
I'm considering installing a Goodman LP Gas Furnace:sizing? Ops?
Gerge, if you go to website www.energycodes.gov
you can do a heat load calc yourself. Basically, you figure out the sizes of walls, total area of glass. total doors to outside, ceiling area and types of building materials used. It is pretty easy and then you will know for sure. The contractor should be suppling you with one but if not use this, it is free!
Nov 03, 2009 | Goodman GMS90703BXA Heater
I have a Carrier 58SX060 Furnace with air. I turned the thermostat to heat and the exhaust comes on and runs and the pilot comes on but the burner never light s and the blower never comes on. If I turn the...
carrier gas furnaces will try to light three times then will usually go on a lockout for one hour you can bypass the lock out by resetting the power, turn furnace on, remove wires from gas valve, you will need a multi meter to check for voltage to valve, if control board sends a call to the gas valve the valve is bad, if voltage is never present during the lighting cycle your control board is bad
Sep 30, 2009 | Heating & Cooling
Extreme heating bills
easy way to fine the high usage is to turn everything off and watch your meter and have someone start turning thing back on and watch for the most usage of power
Jan 25, 2009 | Carrier XHB123D X/Y Series Heat/Cool Air...
Rheem gas furnace pilot lights, but no burners or fan
If the burners do not fully ignite, the sensor will shut the furnace down. The lack of sufficient burner flame is a gas valve or gas pressure problem within the valve.
Replacing the gas valve with the original one may get you going. I surely suggest a professional service company for safety reasons and a thorough inspection. A 20 year old furnace is past it's normal life span.
Jan 06, 2009 | Heating & Cooling
Carrier Furnace wouldn't light, fan was running all the time.
Most furnaces have a photo cell if it gets dirty the photo cell does not see a flame so it trips the reset button on flame failure.
May 13, 2008 | Heating & Cooling
Carrier Infinity Control Thermostat SYSTXCCUID01-B
Your old stat is wired for a traditional thermostat and not a communication stat like the new infinity you have. There is a module plug on the furnace board that will need to be connected to the new thermostat for it to work. The wires that are wired now are from a terminal strip inside the furnace. Please contact your local Carrier dealer. They may be able to get that harness for you
Dec 06, 2007 | Heating & Cooling
Heater blower motor cycles on and off (frequently). I have a class 2 LR95329 Honeywell Thermostat
The clicking noise is a relay or switch of some sort. You are right about that. I have 2 questions. 1) does the thermostat have a mercury bulb in it? 2) when the fan shuts off and on, does the burner stay on?
Nov 05, 2007 | Honeywell Programmable Thermostat Heater
Heating & Cooling Logo
142 people viewed this question
Top Heating & Cooling Experts
Paul Carew
Dan Webster
Dan Webster
Tim Whalen