Do you have a wiring diagram for (2) Honeywell V8043E zone valves with separate thermostats?
I'm trying to wire (2) Honewell zone valves to my Weil McLain CG series boiler. The manufacturer's diagrams are confusing. I'm using a 24V transformer and have one circulator pump. My confusion lies around how to tie into the existing boiler circuitry. I found your 2-wire thermostat with a 3-wire zone valve helpful, but my zone valve has 4 wires, and I need to know how to tie it into my boiler.
2 Suggested Answers
SOURCE: I have a Weil-McLain hot
Hello.Prob#1 valve has a bad END SWITCH,change the power head,thad brings the circ on when open.Prob#2 try manual overide lever.iS IT TIGHT OR SMOOTH?DOES IT JUMP/SNAP?motor very hot? all bad signs.Change that power head too.The transformers are OK because 1 trans can only run 3 valves max.
Posted on Sep 21, 2010
All of the sudden, my Honeywell zone valve opens all the time even with thermostat lowered.
Have you checked to see if you are getting a power call from the thermostat to the valve? Possible Zone valve stuck open. Pull wire off valve to see if valve closes if not then valve is bad. If valve closes then you need to check to see if you have a wire shorted over from power supplied from stat> If supply wire to valve from stat is making contact with power wire supplied to stat this will keep valve open all the time.
Dec 17, 2014 | Honeywell Heating & Cooling
Replacing double pole 220 v with honewell ct410a two wire120/140v wiring diagram not clear
1 power wire (120v) will go to the thermostat and 1 power wire (120v) will go directly to the unit. The other wire on the unit will go to the other side of the thermostat. The safety precaution behind using a single pole to replace a double pole contactor is that you will always have 1 leg of power going to the unit. Many systems are designed like this from the factory, but it is always better to have a 2 pole to cut all power off to the unit unless it's in operation. The unit will still not work as long as it does not have both legs of power.
L1 to Thermostat T1 to Unit
L2 and T2 wired together.
This is only for 240v systems. 120v Will have 1 common and 1 power, therefore you will need to know which wire is which. Power to thermostat, common wired direct.
Nov 26, 2013 | Honeywell Programmable Thermostat Heater
Wiring a Honeywell V8043E for two zones
Honeywell posts pdf manuals.
Google seArch Honeywell V8043E .pdf
Include .pdf in search parameter to find manual with wiring diagrams.
http://www.forwardthinking.honeywell.com/related_links/water/5000_series/install/95c_10932.pdf
Oct 26, 2012 | Honeywell V8043E1012 Zone Valve 3/4 Sweat,...
I have a Weil-McLain hot water boiler for baseboard heat. The system has one circulator pump. The system has 5 zones - 3 work fine and two are not working. All the zone valves and thermostats are...
Sep 20, 2010 | Honeywell (CT62B1015) Baseboard Heater
Replacing WHITE-RODGERS manual thermostat with 3 wires ( red, white, blue and installing Honeywell electronic thermostat RTH110B, how do I connect it? The heating is not central, baseboard heating.
I have only seen one Honeywell thermostat that would work with a 3-wire heating system.
I would replace it with a White-Rodgers 1F80-0471. They are about $100, but they are a good thermostat, and they work well with the 3-wire zone valves.
Most other thermostats have the "Y" terminal that you need, but do not control the zone valve correctly.
Helping Hands Services
- Fairbanks, Alaska -
Jan 30, 2010 | Honeywell Electronic Programmable...
I have a red and a white wire but the heater wont
It sounds like you have at least 2 zones in your system. If this is a normal hot water boiler system with zone valves. When you have your thermostat call for heat it closes the 24 volt circuit that then energizes the motorized zone valve for that thermostat. In that motorized zone valve there is an end switch that will close and complete the circuit to the boiler. Zone valves when they start to clog up with mineralization will not allow the motor to go far enough to close the end switch, so then the boiler and circulating pump will not come on. If this is the case then you need to have the zone valve replaced.
Also make sure your wires at the thermostat are connected correctly. One thing you could also check at the thermostat to make sure it works or not is to jumper the 2 wires and see if your system starts up or not. If the system starts up then the thermostat or its subbase is defective. Hope I was of help to you!! Good luck!!
Nov 29, 2009 | Honeywell Programmable Thermostat Heater
I just purchased a honewell RTH 221 thermostat. I
Typically the four thermostat wires are:
R = power (or common)
G= FAN
W = Heat
Y = Cool
Assuming that you have a normal electric or gas furnace and air conditioning, if the heat really is coming on, then just switch the position of the the Yellow and White wires.
Nov 02, 2009 | Honeywell Programmable Thermostat Heater
How can I repair a Honeywell V8043E 1020 Zone Valve?
Replace it...you'll need to do that in a year if you get it to run at all by monkeying with it.
Nov 23, 2008 | Honeywell Heating & Cooling
Replacing Round Honewell Mercury Thermostat
try to get one that is made for oil heat, the installation is easy only two wires, and the instructions make it easy.
Oct 23, 2008 | Honeywell Electronic Programmable...
Wiring a Honeywell VisionPRO TH8320U1008 Thermostat
the thermostat will to any temperature but will not shut off
Nov 25, 2007 | Honeywell CT3600 7 Day Electronic...
Heating & Cooling Logo
259 people viewed this question
Top Heating & Cooling Experts
Paul Carew
Dan Webster
Dan Webster
Tim Whalen