Question about Intertherm Heating & Cooling
Intertherm Furnace Will not stay on
I have had to hit the reset button for it to heat. Now, I have a blinking light that indicates "Limit Circuit Open or External Load on W." What does this mean?
I have had several problems with this furnace. Every year it seems we have to replace a part or two.
  • Keith Miller
    Keith Miller May 11, 2010
    limit switch can be high temp in fire box due to low air flow dirty air filter will the blower fan run
  • 30 Answers
Your furnace is likely getting too hot check your filter. make sure the fan is running. if you have weak air flow you may have a blocked heat transfer coil. you should have your heating and cooling system serviced yearly by a qualified company to inspect and test equipment.
Posted on Jan 05, 2009
2 Suggested Answers
  • 67 Answers
SOURCE: Intertherm Furnace Will not stay on
dirty air filter low air flow causing high temp in fire box to trip limit switch or fan motor
Posted on Jan 07, 2009
Where is the limit switch on an Intertherm M1MB070ABW furnace?
it would be a safety switch up by blower assembly. typically has red reset button.
Apr 26, 2015 | Intertherm Heating & Cooling
Furnace will not kick on
going out on high limit which requires manual reset
Dec 15, 2013 | Intertherm P3RA-048K Air Conditioner
Furnace lights blows heat in cycle, pops sensor on blower and continuosly blows air until button on sensor is pushed back in
If the sensor knocks the unit off and the the fan keeps blowing without a flame ,the limit (the sensor is a limit comptroller that turns off flame @ a set temp and allows the fan to run until the heat exchanger cools to @ set temp) has out lived its lifetime and needs to be replaced.the button is a manual reset that once reset would allow the unit to continue to run flame and blower at the same time after having been set once, if it is an ongoing problem and needs to be reset more than once then replace the limit control (sensor) in kind. (With the same mode and set-points for the limits)
Oct 25, 2012 | Intertherm 56000 Btu Gas Furnace
No heat, one flash says limit circuit open on my furnace
If your limit circuit open it is an indication of either a power surge opening the circuit OR that your furnance has another problem and the limiter opened because of it. You can buy and replace the limit circuit, but if it opens right away, you will need to go further into your furnace.
Jan 16, 2012 | Frigidaire Dryers
Intertherm mmha070
Hi, did he bypass the high limit to see if it was bad? Sounds like you are getting false codes and you have a problem in your module or main board, which ever you have. The way it is acting, saying the high limit is open but the tech says its not, I would change the board.
Nov 14, 2011 | Intertherm P3RA-048K Air Conditioner
My furnace the burners light and come on and heat up the unit. But the fan never kicks on and blows. The fan itself works because I can turn it on manually so I know it's not that. The trouble code...
The manual selection on the thermostat bypasses the fan relay. When in Auto, the fan relay turns on the blower. You are probably looking at replacing the circuit board. As far as the three blinks, on the reverse side of the front panel there is a wiring diagram and error code chart. It will give you a starting point where to look for a problem. The three blinks could indicate an open limit because the blower is not operating. Keep the blower on manual and let the furnace run normally until you can figure out what the problem is.
Feb 23, 2011 | Intertherm Heating & Cooling
Hi, I have a York furnace and I am having problems with it staying on. The warning message I get is a red light blinking 4 times, Limit switch open. What does that mean? Any suggestions?
a limit open is saying that your furnace is over heating. a few things could be wrong. dirty filters, blocked air return or closed vents. the roll out switch,if your furnace has one , is also in this loop .it normaly will be needed to reset and is on top of the roll out sheild in the burner compartment. call a repair company if this is the problem.
Feb 03, 2011 | Heating & Cooling
Furnace main fan comes on but the furnace doesn't come on. The indicator red light blinks four times. What does this signify?
You have to get in to the main circuit board. At the bottom of the circuit board it will tell you what the flashes mean, in very small print. Read this print for you codes.
Dec 25, 2009 | Goodman GMS90703BXA Heater
possible dirty air filter low air flow causing high temp in fire box to trip limit switch or fan motor is bad hope this help let me know if you if this solved problem I may need more info
Jan 04, 2009 | Intertherm P3RA-048K Air Conditioner
Goodman furnace 4 blinks
Ohm out the safety switches also known as the high limits usually at least two on units they look like little buttons, with two wires going to each one. An open high limit will mean the circuit is not closed and allowing for the system to complete the circuitry to fire the heat, best way to diagnose is to jump out the suspected high limit s/w if the unit runs then you have your answer, but never, never leave the high limit switch jumped w/o the switch.
Dec 21, 2008 | Goodman GMS90703BXA Heater