Question about Aprilaire 550 Humidifier
Looks like my humidistat calls for coil fan and for furnace heat
I have an Aprilaire 560 and recently it started to give me headaches. I think that the humidifier should work only when the coil fan is on…and that should happen only when the thermostat calls for heat on this zone. The fan is on “AUTO” and is controlled by the thermostat not by the furnace. If I change settings on my humidistat dial while the coil fan is off, I hear the “click” and the fan is starting instantly…after a while the furnace goes too and the temperature goes beyond the thermostat program. If I lower the humidity level just under the typical “click”, the furnace and the fan stops.
The only way to get some humidity without reaching 78F is to let the fan on “ON” instead of “AUTO” and to raise the level on my humidistat…this way the furnace follows the thermostat program set for 73F.
Any suggestions?
  • wargold51 Jan 23, 2009
    Same problem.
  • thom46 Feb 07, 2009
    I had a similar problem with my 560. The humidifier was tricking the furnace computer into calling for heat. My furnace short cycled all day long, still providing heat when the stat called for it, but the fan would NEVER shut down. I thought I had a bad limit switch, then a bad stat, then after saying bad words I decided to treat it like a computer problem - disconnected all wires to the brain board and reconnected one at a time. After adding the stat wires the furnace began behaving normally. Soon as I added the aprilaire wire - same problems started up again. That's how I found the problem
  • 3 Answers
It sounds like the humidifier may be improperly wired.
It's hard to solve without checking the wiring, but it seems like the humidistat is wired so that as the dial is advanced, it incorrectly turns on the fan, or furnace, or both.  The contacts of the humidistat should be wired so that they turn on the solenoid only.  Also, the power to the humidistat, to turn on the solenoid, should come on only when the fan is on.
Hope this helps!
Posted on Jan 28, 2009
2005 Aprilaire 700 humidifier. Replaced a non-working circuit board. Now, the humidifier works fine when the furnace is running. It starts and stops as it should based on humidistat setting. Problem: ...
It sounds like it is just miswired. The low voltage wiring off the humidistat should be on W and C on the circ. board at the furnace. If you have it on R and C then it will power it constantly regardless if the heat is running or not. W is only energized on a call for heat which is typically when you want that type of humidifier to run
Feb 02, 2013 | Aprilaire Humidifiers
I have a aprilaire 700 I just installed on return plenum. Have a problem with the wiring, the instruction say to connect the R&C wires from humidistat to the same on furnace power strip. Is the C
Depending on the age of your furnace you may have an aux terminal for a humidifier. If not, you should use the white wire (heat) coming from the homes thermostat to power up the humidistat and ultimately bring on the humidifier. This way it will only run when in heating mode.
Nov 16, 2012 | Aprilaire 700 Humidifier
When does the humidifier fan start? Does the water flow trigger it? Will the fan nt start if I turn off the water supply?
Humidifier should be powered from the furnace heating 24 volt terminals through a humidistat and then to your humidifier. The fan and the water solenoid on the unit should come on together. if the water is not turned on the fan should still run, unless the unit is not plugged in.
Nov 13, 2010 | Aprilaire 700 Humidifier
Function of HUM terminal on 1Source Panel
That will work, The HUM feeds power to the humidifier when the fan is operating even in cooling on most models, However the humidistat must also be calling for humidity and probally won't call during the cooling months
Jan 15, 2010 | Aprilaire 700 Humidifier
My Aprilaire 560 doesn't shut off even if the blower is off.
My Aprilair 560 turns on and off repeatedly.Making a loud banging sound.Changed my water valve worked 1 day and started agin.
Dec 20, 2009 | Aprilaire 550 Humidifier
Turning on the humidifier shuts off the furnace
It is possible you may have wired it wrong. Make sure your humidifer is not robbing power from your thermostat. This would explain when your humidifer makes a demand to come on it robs power from your t-stat making it lose its call for heat. Wire your humidistat to the "w" terminal and the common terminal so it only runs on a call for heat. With the bypass type of humidifier you purchased it wont do you any good to run when the heat isn't running anyway. If you want an independent operation humidifier you need a steam type.
Dec 02, 2008 | Aprilaire 600 Humidifier
AprilAire 760 not running after installing new circuit board
I called the service company that put in my new furnace (FAmily Heating and Cooling in Detroit, very highly recommend these people)
Anyway they sent out a second service tech who determined that I would be better off having the humidifier wired to go on whenever the furnace fan was running instead of using the humidifier signal from the circuit board on the furnace. After he changed the wiring the unit runs fine. It is pretty likely that the circuit board was bad also.
Nov 27, 2008 | Aprilaire 700 Humidifier
Aprilaire 700 operating at wrong time
You want the humidifier to run in heat mode which is the r-w1 terminal on the stat.
Nov 17, 2008 | Aprilaire 700 Humidifier
Aprilaire 560 humidifier
Hello All,
Was having a similar problem. Disconnected the source line and opened saddle valve. I was getting water to the solenoid but nothing out the other side. My humidistat doesn't have a "test" setting, it's either off or the highest humidity. I held the outbound line in my hand and experimented with adjusting both sadlle valve and humidistat. I didn't get any water until I opened the saddle valve MUCH further than I thought was necessary and turned the humidistat to near the highest setting. Once I had water coming though I experimented with the setting on the humidistat, turning it off and then slowly increasing the humidity until the solenoid clunked and water started coming out. I would recommend anyone having this same problem to open the saddle valve all the way (I was surprised how many turns that took) and set the humiditstat to it's highest setting.
Randall
Dec 15, 2007 | Aprilaire 550 Humidifier
Aprilaire 550 Humidifier Logo
225 people viewed this question
Top Aprilaire Humidifiers Experts
Paul Carew
jdthefixer
Mack Baxter
Are you an Aprilaire Humidifier Expert? Answer questions, earn points and help others