I have a Cozy one-sided gas wall heater. It is no longer lighting the burners when the wall thermostat reaches the temperature set point. The thermostat will "click" on, but the burners won't ignite in the heater. This has been an intermittent problem, but is growing steadily more frequent by the day. Sometimes when the burners won't ignite, I'll bang on the heater and then they ignite. But even that "temporary fix" is becoming less effective. What part on the wall heater needs to be replaced or serviced so that the burners light when the wall thermostat sends out its signal? A new wall thermostat was installed about a month ago because the same problem was happening with it, so I know it's not the thermostat.

Posted by on

1 Answer

  • Level 2:

    An expert who has achieved level 2 by getting 100 points

    All-Star:

    An expert that got 10 achievements.

    MVP:

    An expert that got 5 achievements.

    Vice President:

    An expert whose answer got voted for 100 times.

  • Expert
  • 306 Answers

Can you remove the front cover to the wall unit? Look for the wiring and follow it till you see a round about the size of a fifty cent piece. Should have 3 of them. One of them is not closing and allowing the signal to go through. So turn up the t-stat to call for heat take each one of the limit switches and by pass them one by one till you find the one that is bad. Depending on where you hit the cover is where I would look first. The limit's are rated by temperature so replace with correct size. You should be able to see the temp. on the limit something like 180 is what you are looking for. Also make sure the wires are in good shape where they connect to the switches. Might have a loose connection. ken

Posted on Jan 03, 2009

Add Your Answer

Uploading: 0%

my-video-file.mp4

Complete. Click "Add" to insert your video. Add

×

Loading...
Loading...

Related Questions:

1 Answer

I have a Vulcan Ultra 21E ceiling ducted unit The LED flashing fault is no 8 which is a gas interruption. The unit fan runs, ignition starts full flame and gas flows for about 2 secs then shuts down The...


Just been thru a similar problem with my Climate Technologies Vulcan High Efficiency Ducted Gas heater which in this case is installed under the house. This heater is about 7 years old and I have previously (2 years back) refurbished the controller by replacing the main power supply electrolytic filter capacitors.

I also had a communication problem with the Touch pad Thermostat which in the end required replacing the entire touch pad as one of it's voltage regulators had gone intermittent (Touch pads are available on E-Bay). To operate the heater while the touch pad was out of commission I installed a manual switch between the heat contacts on the heater controller. Closing the switch causes the heater to permanently run if it has no thermostat. Once communication with the touch panel was restored we were able to try and find the intermittent heater fault.

Again I have been getting Fault Code 08 "Gas Interruption" however the heater was lighting OK and then going out after about a minute or so. In the end I found 2 distinct heater faults.

Fault 1 was the flame sensor where the weld between the wire and flame probe rod had broken but it was still touching. This meant it was sensing Flame OK and then later would go open with expansion as the temperature rose. I fixed this by replacing the Flame Probe with a new one sourced from Reece HVAC.

At this point I celebrated thinking it was fixed!

Fault 2 after the flame sensor issue was cleared the fault still persisted but slightly less often.
The heater was cycling 3 times to get going and then locking out, requiring a reset from the touch thermostat or heater controller board. Sometimes the heater would achieve a onging burn for a long period, and other times just locking out after 3 tries.

Careful observation of the flame, through the observation holes after it lit, showed correct flame sensing but as soon as the nominal 65C duct temperature was reached the combustion fan (modulates) throttles back too far and the flame goes out, the flame sensor switches off and gas valve is then closed. The pressure differential across the burner manafold controls the Gas flow rate so if the combustion fan goes too slow the flame goes out due to lack of gas.

On the control board there is a potentiometer marked "MIN GAS RATE" this needs to be tweaked clockwise until the burner remains lit when the nominal 60-65C duct temperature is reached. Don't turn it up too far or the heater may not throttle back enough and end up going out on overheat.

Once a stable flame is achieved when throttled, try the heater in the economy mode which uses a lower recirculating fan speed and check the flame still remains lit. My problem was most obvious in the Econ mode.

Hope this helps someone else - It took me over a year to solve this one. NeilP

Aug 21, 2011 | Air Conditioners

2 Answers

I turned on hot water to take a bath, and it was hot. by the time the tub had filled the water was freezing. now we cant seem to get hot water out of anywhere. the pilot light is on. the knob is set to on,...


if I was a betting may I would say that this is a small water heater, what is the temperature set on, as the pilot light will be lit once the temperature is reached, but until then the burners will be lit. I would move the temperature knob and listen to see if I hear the burners kick on. Hope this helps Tim

Apr 17, 2011 | Air Conditioners

1 Answer

I have an early 80's mobile home with an "intertherm gas atmospheric furnace" pilot light is lit but can't get the furnace to "fire". Seems as though the limit control is stuck open. ...


If your pilot light is lit then I would first check your thermostat. Make sure it is on heat setting and fan is on auto, turn stat up to where it should be calling for heat. If you don't get burner to light remove front cover from thermostat and see if it has a mercury switch, if it does move temperature selector up and down and see if you can see a spark in mercury switch vial. If y ou cannot see a spark remove screws that attach t-stat to base.Remove carefully and disconnect wires that go to r and w terminals on stat base. Temporarily connect these two wires together. This should make burner light if you have power to thermostat. If burner does light disconnect wires and replace thermostat. Also if you have a volt meter check across these two wires and see if you have power there. Should be around 24 volts a.c. If your thermostat has a fan on setting try that. If fan runs you know you have power to furnace The gas valve needs 24 volts to operate and inside the electric control box in furnace there is a transformer to step down 110-120 supply voltage to 24 volts. If transformer is working you should be able to hear a low buzz or humming sound. You can also check across gas valve terminals when t-stat is set for heat, you should read about 24 volts. If you have 24 volts to gas valve and it is not opening then you need to replace gas valve. The main purpose of the limit switches is to turn blower on when temperature in heat exchanger reaches fan on temp,shut off blower after burner shuts off and heat in heat exchanger reaches fan off temperature, and limit if temperature exceedes set point without blower coming on. I hope this helps you. Thanks

Nov 25, 2010 | Air Conditioners

1 Answer

The furnace starts and everything works fine but the furnance does not turn off when it reaches the set temperature. I replaced the thermostat, however this did not solve the problem. what else could it...


You must match the amp draw of the gas valve to the wall thermostat heat anticipator.
Look on the gas valve and say it is .3 amps. Put the arrow on the .3 amp portion on the wall thermostat. If you do not know the amp draw of the gas valve their is equipment that can be used to determine that amp draw. Setting the thermostat to match the valve greatly reduces Overshoot or droop. That is where you dang near freeze before the thermostat kicks in and then burn up when it finally shuts down. I hate that. READ MORE ABOUT IT HERE

Nov 16, 2010 | Air Conditioners

1 Answer

I have a central air and heat heat uses gas so when the heat is on should the main fan be turning


Typical systems are designed with a thermostatic "fan limit switch" which protrudes into the heater (house air portion of the passages). The "fan limit switch" is mounted to, and protrudes into the duct within the burner section of the heater.

This switch triggers to fan to turn on only after the air in the duct has reached well above ambient temperature. This prevents the fan from coming on too soon and the system blowing cold air, which people don't like.

Depending on system design, installation and current operating conditions, the time delay from main burners on to fan on can be up to a couple of minutes.

This same limit switch, if the temperature goes high enough, will also turn the gas valve off; a fire safety function.

Jan 06, 2010 | Goodman CKL49AR49 Air Conditioner

1 Answer

Pilot keeps going out


The pilot assembly, pilot oriface, and pilot burner should be cleaned and the thermocouple replaced.

May 01, 2009 | Air Conditioners

1 Answer

I have had the gas off for two years. I got the pilot light to work but when I turn the thermostat up to get some heat it got the heater going about three times in over twenty-five tries over a couple


you need to clean the burner assembly. Over time dust and settled inside the unit and it is possibly restricting the flow of gas through the burners. This is a dangerous situation. get it cleaned before you try again.

Apr 29, 2009 | Air Conditioners

1 Answer

Cozy wall heater working intemittently


Sounds like a limit switch is tripping.
This appliance is equipped with a manual reset blocked
flue switch designed to protect against a blocked flue condition,
which would cause combustion products to spill back into the
living quarters. NOTE: A partially blocked, inadequate, or
disconnected vent system may not activate the switch.
Discoloration of the grille is an indication of a bad vent. If this
occurs, the vent can be checked by a qualified serviceman using
a draft gauge. After 15 minutes the gauge should read between
-.02 up to -.04 inches w.c. Vent must be checked at the
beginning of each heating season.

Jan 28, 2009 | Air Conditioners

1 Answer

Home Heater / thermostat isn't working


It is possible that it may happen again. I reccomend having the burners and burner compartment cleaned, including the Heat exchanger.

If you dont, mind, please rate this solution. All the others were clarificatin requests so we could be sure we found the problem. Now that we found it, It would be great if you could rate the service.

Dec 30, 2008 | Air Conditioners

1 Answer

Weather King 8PJ10NDR01 When I turn the heater switch to ON position the furnace runs what sounds like an internal fan. Second, the igniter glows and when it reaches it's hottest stage the fan thrusts air...


The gas valve is not sensing flame, and the unit shuts down on safety.

Chances are the flame sensor is bad, its a common problem.

If its a thermocouple you can buy one for 10 bucks, If its a newer style they can usually be had for less than 30.

They are easy to replace ad they are usually installed with two screws and one to two wires.

They sit directly in the flame pattern in front of the burners.

A service call should only cost you 250 or less for the repair, but you can do it yourself for less than 50 (including gas to drive to the HVAC supply house that sells your brand unit.)

You will need the model and serial #s when locating the parts.

Dec 27, 2008 | Weather King 12AJA4801AH Air Conditioner

Not finding what you are looking for?
Air Conditioners Logo

Related Topics:

97 people viewed this question

Ask a Question

Usually answered in minutes!

Top Air Conditioners Experts

Dan Webster
Dan Webster

Level 3 Expert

8147 Answers

Bill Long

Level 3 Expert

577 Answers

Tim Whalen

Level 3 Expert

3056 Answers

Are you an Air Conditioner Expert? Answer questions, earn points and help others

Answer questions

Manuals & User Guides

Loading...