Hc01-f12 fault code vulcan ducted heater touch pad control
Heating wont come on
3 Suggested Answers
  • 86 Answers
SOURCE: vulcan cx90 ducted heater
240 volt wiring required.
Posted on Mar 17, 2008
heatman101
  • 43501 Answers
SOURCE: Vulcan gas ducted heating systemr
The reason the heater is cutting out is because it is getting too hot or it thinks it is too hot...
Check the filter and also that enough air vents are open so it can move enough air....make sure the gas pressure is correct and that the flame is not too high. Check that the blower is working correctly and starting up when it should. Check the post purge... make sure the blower is running to remove residual heat after the flame shuts down.
If all that checks out then you may have a bad sensor or control module, but they are much more difficult to troubleshoot.
Bottom line is that for some reason you are either getting too hot or the furnace is sensing too hot of temperatures and shutting down.
heatman101
Posted on May 24, 2011
F1/08 vulcan fault code
Hi Geoff,
Is your heater a ducted gas heater how old is it and what does the wall control look like.
May 10, 2014 | Heating & Cooling
Bonaire vulcan comfort control
No it cant really be fitted as the evap system uses much larger duct and also in some cases people use a different type of duct that when running a gas heater threw it it tends to melt with the heat. Your best option would be to get new ducting that way you can size it correctly so you dont have air alance issues down the track.
I have a Vulcan Ultra 21E ceiling ducted unit The LED flashing fault is no 8 which is a gas interruption. The unit fan runs, ignition starts full flame and gas flows for about 2 secs then shuts down The...
Just been thru a similar problem with my Climate Technologies Vulcan High Efficiency Ducted Gas heater which in this case is installed under the house. This heater is about 7 years old and I have previously (2 years back) refurbished the controller by replacing the main power supply electrolytic filter capacitors.
I also had a communication problem with the Touch pad Thermostat which in the end required replacing the entire touch pad as one of it's voltage regulators had gone intermittent (Touch pads are available on E-Bay). To operate the heater while the touch pad was out of commission I installed a manual switch between the heat contacts on the heater controller. Closing the switch causes the heater to permanently run if it has no thermostat. Once communication with the touch panel was restored we were able to try and find the intermittent heater fault.
Again I have been getting Fault Code 08 "Gas Interruption" however the heater was lighting OK and then going out after about a minute or so. In the end I found 2 distinct heater faults.
Fault 1 was the flame sensor where the weld between the wire and flame probe rod had broken but it was still touching. This meant it was sensing Flame OK and then later would go open with expansion as the temperature rose. I fixed this by replacing the Flame Probe with a new one sourced from Reece HVAC.
At this point I celebrated thinking it was fixed!
Fault 2 after the flame sensor issue was cleared the fault still persisted but slightly less often.
The heater was cycling 3 times to get going and then locking out, requiring a reset from the touch thermostat or heater controller board. Sometimes the heater would achieve a onging burn for a long period, and other times just locking out after 3 tries.
Careful observation of the flame, through the observation holes after it lit, showed correct flame sensing but as soon as the nominal 65C duct temperature was reached the combustion fan (modulates) throttles back too far and the flame goes out, the flame sensor switches off and gas valve is then closed. The pressure differential across the burner manafold controls the Gas flow rate so if the combustion fan goes too slow the flame goes out due to lack of gas.
On the control board there is a potentiometer marked "MIN GAS RATE" this needs to be tweaked clockwise until the burner remains lit when the nominal 60-65C duct temperature is reached. Don't turn it up too far or the heater may not throttle back enough and end up going out on overheat.
Once a stable flame is achieved when throttled, try the heater in the economy mode which uses a lower recirculating fan speed and check the flame still remains lit. My problem was most obvious in the Econ mode.
Hope this helps someone else - It took me over a year to solve this one. NeilP
Aug 21, 2011 | Heating & Cooling
Fault code HC01 then flash to F04
I assume the heater has been installed for a year or more therefore, F1is the fault number O4 is the fault code and this 04 means the auto over temp has been tripped due to poor airflow through the heater. (the rear of the heater is getting above 65 deg C)
Check all outlets and remove any filter in the outlets.
Remove the return air filter clean if fitted.
On 4 & 5 star heaters check fan speeds are set correctly on control, low fan 27 to 30 and high fan 35. (download customer manual from climate technologies website) 70% of outlets capacity must be open at any time.
Check if the ductwork has been obstructed in any way.
Have the room fan checked and the auto high limit changed by a qualified person. Have a Carbon monoxide test done every 2 years.
May 17, 2011 | Vulcan Heating & Cooling
Bonaire Vulcan ducted heating system flashes F08 and HC 01. What do I do?
I was able to fix my Pyrox ducted gas heater (flashing between HC01 and F08 by pressing the reset button on the main PCB located in the main heating unit.
The reset button is located next to a set of indicator led's. It's easy to get to by just removing the covering shroud.
May 02, 2011 | Heating & Cooling
We have a Vulcan Ultra high efficiency gas ducted heating
Gas ducted central heater won't switch on all of a sudden
Nov 04, 2009 | Vulcan AUW230A Heater
I have a similar problem
I just went into the Bonaire website and downloaded their FAQ on gas ducted heating from their support link. Their instructions are pretty easy to understand.
Sep 08, 2009 | Heating & Cooling
Vulcan cx90 ducted heater
Mar 06, 2008 | Heating & Cooling
Vulcan ducted heating not working
How many wires for the thermostat do you have? If you tell me I can help. The green flashing, instead of red, in my experience, means a thermostat problem.