Main burners don't come on, though the ignitor goes bright
The sequence seems to be fine - thermostat sends heat signal, inducer motor turns on, in about 30 sec ignitor glows bright but the main burners don't start. The sequence is repeated 3 times then I think the furnace locks.
Goodman GSMS0603
Any help is appreciated as it's now pretty cold in Ottawa ;)
  • 1 more comment
  • maxpad1 Jan 03, 2009
    Thanks for your reply paulcarew. yes, there's a click. How can I tell if the valve is opening? Re air filter the main one right before the blower is clean. Is there another air filter that I should check? Thanks.
    Forgot to mention that after the cycle runs 3 times, the red light gives out 1 blink which according to the manual is the ignition problem (gas valve, gas pressure, flame sensor)
  • flappy_20032 Jan 05, 2009
    I am having the smae problem with the same heater we had someone come out he cleaned it all out and turned the pressure gauge up. but it still wants to shut down before the main burners light up. you can hear the motor and it will click the little organe igniton light comes on you can hear a few more clicks then it go off. It does this 3 times and then the whole things will just shut down.
  • Goodman Master
  • 3,238 Answers
You should hear a click ,its the valve opening ? of check to see if the air fiter is clean ,
Posted on Jan 03, 2009
  • Paul Carew Jan 04, 2009
    the click means the gas valve is open air fiter clean that is okay try jumping out the pressure switch should light up , you can also clean the flame sensor with sone steek wool
    GAS pressure can be check at the inlet on the reg but you will need a pressure gauge for that ,
    see if that hepls
Furnace glow plug lights but main burner doesn't go on
Hi, on a call for heat from your thermostat, you get a signal to your ignitor module to send voltage to your pilot glow plug. As it glows it sends a signal back through the flame sensor to tell the MGV, (main gas valve) to open and start the burners. When this glow plug glows, you should here a click at the gas valve as 24 volts is sent to it to open. Unless the gas is off for some reason, which I doubt you turned it off, the gas valve is shorted out. You might want to try this first, with the power off the flame sensor that is beside this glow plug as we call it may be dirty and not sending a signal back to open this valve. It is about 4 to 6" long and round, made of porcelin with a metal tip on the end. Take a piece of sanding cloth or steel wool and clean the tip, so it gets nice and hot from the glow plug. Turn the power back on and cycle the thermostat on heat again. The inducer motor will start first, then close the pressure switch and the plug will glow. After this, it will send a signal back to the module to open the gas valve. Hopefully this is the problem, just a dirty flame sensor. If that didn't do it, the gas valve is bad and will need to be replaced. Please rate me on this as I know you will be kind. If its a dirty flame sensor, you should be up and running in no time at all.
Sincerely,
Shastalaker7
A/C, & Heating Contractor
Sep 28, 2010 | Heating & Cooling
No blinks normal running igniter glows gas comes on wont run
Check for 24 volts across the gas valve when Ignitor is glowing. If no, bad board. If yes, bad gas valve or blockage.
On a call for heat, the 24 volt thermostat sends a signal to the control module. The control module will indicate a call for heat with a light on the control either blinking or remain solid depending upon model. The inducer (exhaust) blower will purge all gasses from the furnace and pressurize a pressure switch. Once the pressure switch tells the module to continue, the electronic ignition will energize and send 120 volts to the igniter. The igniter will glow and you will be able to see it if viewed thru the small inspection port. Once the igniter gets hot enough, it sends a signal to the module opening up the gas valve (24 volts). Either a pilot will come on or the burner tube will ignite then spread the flame to all burners. Lastly a safety sensor will be looking for a certain temperature within a few seconds and the furnace will continue to operate and the room air blower will turn on in a minute or two.
What could go wrong? The unit will not run if there is no signal from the thermostat (bad thermostat or broken wire), the control module does not sense a signal from the thermostat (bad control), the inducer does not energize (bad motor), the pressure switch does not close (blocked vent piping, bad switch, plugged condensate hose), the igniter does not energize (bad control, bad igniter), the gas valve does not open or there is no gas (bad gas valve, broken wire, no gas), the pilot does not light (dirty pilot), the burner does not light (bad burner, plugged orifice, not enough combustion air), the flame does not spread to each burner (bad flame spreader, dirty flame spreader, more bad burners), the flame safety sensor does not detect flame (dirty or bad flame spreader, bad flame sensor, broken wire, bad control), or the room air blower does not energize (bad fan motor, bad control).
Mar 05, 2010 | Goodman GMS90703BXA Heater
Turn heat on, I hear it ignite and furnace runs and runs fine then usually there is a slight delay and blower turns on and blows heat, but now it does not, I put my hand up to a nearby vent to no heat and...
Jan 06, 2010 | Goodman GMS90703BXA Heater
HEIL 80% furnace T-STAT calls for heat, Inducer runs and nothing else happens, Ohm meter reads 4.9 on ignitor. MDL#NTGM100EHA2....Any help with this?
Nov 03, 2009 | Heating & Cooling
My problem is with the central heat. The thermostat will click, but the heater doesnt come on. What will cause that?
On a call for heat, the 24 volt thermostat2.gif sends a signal to the control module. The control module will indicate a call for heat with a light on the control either blinking or remain solid depending upon model. The inducer (exhaust) blower will purge all gasses from the furnace and pressurize a pressure switch. Once the pressure switch tells the module to continue, the electronic ignition will energize and send 120 volts to the ignitor. The ignitor will glow and you will be able to see it if viewed thru the small inspection port. Once the ignitor gets hot enough, it sends a signal to the module opening up the gas valve (24 volts). Either a pilot will come on or the burner tube will ignite then spread the flame to all burners. Lastly a safety sensor will be looking for a certain temperature within a few seconds and the furnace will continue to operate and the room air blower will turn on in a minute or two.
What could go wrong? The unit will not run if there is no signal from the thermostat (bad thermostat or broken wire), the control module does not sense a signal from the thermostat (bad control), the inducer does not energize (bad motor), the pressure switch does not close (blocked vent piping, bad switch, plugged condensate hose), the ignitor does not energize (bad control, bad ignitor), the gas valve does not open or there is no gas (bad gas valve, broken wire, no gas), the pilot does not lite (dirty pilot), the burner does not lite (bad burner, plugged orifice, not enough combustion air), the flame does not spread to each burner (bad flame spreader, dirty flame spreader, more bad burners), the flame safety sensor does not detect flame (dirty or bad flame spreader, bad flame sensor, broken wire, bad control), or the room air blower does not energize (bad fan motor, bad control).
Most newer furnaces will have a diagnostic center or control built into the control module. You may be able to view it as it is running thru a small viewing port. Some models will require the removal of an access panel prior to finding it. On the reverse of the access panel, there will be a diagnostic chart that will aide you in understanding any error code recorded (usually a blinking light).
Oct 18, 2009 | Heating & Cooling
Funace gag goes on than off right away
Oct 18, 2009 | Honeywell Electronic Programmable...
I have a Goodman air heat unit that will not come on.
On a call for heat, the 24 volt thermostat sends a signal to the control module. The control module will indicate a call for heat with a light on the control either blinking or remain solid depending upon model. The inducer (exhaust) blower will purge all gasses from the furnace and pressurize a pressure switch. Once the pressure switch tells the module to continue, the electronic ignition will energize and send 120 volts to the ignitor. The ignitor will glow and you will be able to see it if viewed thru the small inspection port. Once the ignitor gets hot enough, it sends a signal to the module opening up the gas valve (24 volts). Either a pilot will come on or the burner tube will ignite then spread the flame to all burners. Lastly a safety sensor will be looking for a certain temperature within a few seconds and the furnace will continue to operate and the room air blower will turn on in a minute or two.
Jan 27, 2009 | Goodman GMS90703BXA Heater
I have goodman gmp heater dose work for few mintes
Sequence of operation on your gas furnace may help diagnose your problem.
Most newer furnaces like yours will have a diagnostic center or control built into the control module. You may be able to view it as it is running thru a small viewing port. Some models will require the removal of an access panel prior to finding it. On the reverse of the access panel, there will be a diagnostic chart that will aide you in understanding any error code recorded (usually a blinking light).
Dec 10, 2008 | Goodman GMS90703BXA Heater
Goodman furnace blinked 1 time
Furnace attempted to start but failed after so manay tries. This may help you.
Sequence of operation, Gas Furnace.
This is why we technicians earn the big bucks!
Dec 05, 2008 | Goodman GMS90703BXA Heater
No heat
knowing the sequence of operation on your gas furnace may help you diagnose your condition.