I'm working on a Payne gas pack furnace heater and a/c unit. I replaced the tstat cause the a/c worked but not the heat,also replaced the spark ignition module with gas valve,the transformer, and the contacter now nothing comes on.
  • 7 more comments
  • jr0907 Jan 03, 2009
    i do have 24v coming from the transformer going to the ignitor module. I also checked the voltage at the breaker panel and i have 120v on each leg, but only 120v at the unit.
    yes it does have a fuse block and i replaced both buss fuses and also replaced the 30 amp. breakers in the panel.At the breaker panel i have 120v on each leg but at the unit i only have 120v at the fuse block instead of 240v.
  • jr0907 Jan 05, 2009
    yes this a package unit,it's all outside and i already traced the power wire and it's ok. On the transformer i'm getting 120v going in and it's a step down transformer rated at 208v or 240v down to 24v,is the problem before the transformer
  • dwkcool May 11, 2010
    ok you need to find out at the fuse block where you are loosing power and are you testing the fuse block with or without the fuses in it and have you took the fuse block apart and checked the connections
  • Donni Steen May 11, 2010
    You said you are reading 120V for a transformer that is rated 208v 240v? Then you don't have enough power coming into the transformer. It should read 240v entering and 24v leaving.
    if it is a package unit can you get to your power wire going to the unit and trace it back to the breaker box
    this is a package unit all outside or a split system
    need to find out where you are loosing voltage does it have a fuse block or breakers
    if you have a test meter see if you have 24 volts coming from the transformer
    Problem Solver:
  • 13 Answers
Pull the fuses and check voltage line to line with the fuses out you should have 208 to 240 volts if you have 50 or so volts try line to ground if you have 120 on one leg it will back feed with the fuses in,because of the windings involved. in any case you are missing one leg somewhere to get the voltage readings that you have poasted
Posted on Jan 11, 2009
My Payne furnace is NOT producing the desired heat anymore. Any ideas?
Hello, it could be shutting down on it's high limit switch due to a dirty air filter, dirty blower wheel, weak blower motor. Usually this would cause the furnace to shut down before it reaches the desired temp.
Dec 30, 2011 | Heating & Cooling
Furnace will not start. a/c seems to work ok. i
HI; I need more info. How old is the equipment. name brand of equipment. Also to answer Your question ...Yes the tstat wire goes into the furnace to make several connections then a seperate cable(brown) will follow Your freon lines out to the condensor.Also try removing the cover and have a good light. Get someone to turn on heat at tstat and watch for clicking sound.Sounds like You have a spark assist pilot system. When the sparking starts the pilot light should come on. Then once the pilot sensor feels the heat comming from pilot light it will allow the gas valve to come on...BE CAREFULL...I ASSUME NO RESPONSABILITY FOR YOUR ACTIONS...alpharome416 PS.usually there is nothing to worry about just keep Your space to begin with ok.
Feb 09, 2010 | Dometic Rooftop RV Air Conditioner
I have a Rheem gas furnace that shuts off
POssible feed back thru tstat. This sometimes happens. Take a look at tstat disconnect w or white wire that goes to heater. Turn from heat to cool and abck and see if it does it again if not change tstat. You can get a good one at Home depot or Lowes about 20.00 easy to install Keep in touch Rus
Nov 25, 2009 | Heating & Cooling
RUUD 90 Nat Gas unit, >15 yrs old. T-stat calls for heat, nothing happens. I can place the fan in manual ON, & after a few mins. the warm air starts to circulate. If I leave the fan in auto, the...
sounds like you shorted out the heat anticipator in the tstat. try jumping red to white at the tstat wiring terminal and have a friend stand near the furnace to see if it cranks up immediately. if it does the problem is more than likely in your tstat. be sure to blow out any dust in the workings of your tstat. this is 24 volts and shouldn't hurt you but try not to short it out to the common or other wires.
Nov 24, 2009 | Heating & Cooling
Electric furnace. Just replaced the controller board but no heat. The blower does come on when the thermostat gives the heat command and I was wondering if that means the relays to the furnace coils is...
On a Trane furnace the fan realy must energize before the electric strips will come on. On the thermastat. See if there is setting for electric heat. This will bring the fan on and the strips should come on. First just turn on your heat and and turn fan to on postion if it works you need to set tstat to electric heat mode. Most of the time there is sswitch in the back of the stat that says gas elec. Turn to electric. Rus
Oct 29, 2009 | Heating & Cooling
Thermostat will not turn on for air conditioning
Turn fan to on position to see if fan runs. Is this new tstat. Digital or manual tstat. If digital check back of tstat to see if tstat is set to gas heat. Rus
Jun 21, 2009 | Honeywell Programmable Thermostat Heater
Clicking noise at the gas valve/pilot light unit
It sounds like you might have a spark igniter on the unit that is being told to relight the burners. This is probably the tstat as this is the only control that "tells" the unit to come on. There isn't anything else internally that will cause this problem. Replace your tstat and I bet this solves your problem.
Apr 05, 2009 | Carrier 38BRC048 Air Conditioner
Heating problem
the tstat sounds like it is not connecting the white and red terminals which is usually the heat cycle if it is a gas furnace if so to check I take tstat cover off and jump white terminal to red terminal this is the standard heat position the unit should fire the heat cycle if not a gas funace let me know what type of unit you have hope this helps
Jan 11, 2009 | Heating & Cooling
Payne Gas Pack Furnace A/C and Heat Unit
Do you have power to the unit?
Is it a 110v or a 220v unit?
check your power supply.
Jan 02, 2009 | Heating & Cooling
Need line set size for goodman ck-36-1a
If your running gas heat it's 5/8 3/8 tubing.If it's elec. heat it's 3/4 3/8 tubing. Etheirway 3/4 3/8 works for both. Use 6 wire for tstat from tstat to furnace or air handler, and you need is 2 wire from condensing unit [outside] to furnace or air handler or anything more than two.
Sep 26, 2008 | Goodman Heating & Cooling