All system is woking exept the ignition for the flame, I'd like to find a solution fo my problem

Posted by on

  • Anonymous Dec 29, 2008

    Hi, I have the same intermittent problem. 1 month old installation, nice new unit.

    - Thermostat calls for heat
    - Blower motor starts
    - Ignitor glows red
    - Gas valve does not come on before the Ignitor quits
    - Furnace tries this 3 times, quits, and then light blinks once

    I can shut down power to furnace, letting it reset I think, and then furnace tries again and usually works fine.

    Suggestions welcomed, thanks


  • jrclark2008 Dec 31, 2008

    gmh95/gch9 new installation,started up normal, ran 15 minutes, now no burner, all prestarts seem normal,ignitor glows then shuts down, seems like no gas to ignite

×

1 Answer

  • Level 3:

    An expert who has achieved level 3 by getting 1000 points

    Superstar:

    An expert that got 20 achievements.

    All-Star:

    An expert that got 10 achievements.

    MVP:

    An expert that got 5 achievements.

  • Master
  • 1,420 Answers

If the ignitor is glowing, we will need to check for 24 volts AC across the gas valve. If you do not have it, look at replacing the ignitor first. Even if it glows, it may not be sending the signal to the control board. Secondly you will need to replace the control board. If you get 24 volts for a few seconds but does not ignite, you either have a bad gas regulator, dirty burners or a bad gas valve. What is abnormal is that you say it runs for 15 minutes but does not restart.

Hope this is some help

Posted on Jan 02, 2009

1 Suggested Answer

6ya6ya
  • 2 Answers

SOURCE: I have freestanding Series 8 dishwasher. Lately during the filling cycle water hammer is occurring. How can this be resolved

Hi,
a 6ya expert can help you resolve that issue over the phone in a minute or two.
best thing about this new service is that you are never placed on hold and get to talk to real repairmen in the US.
the service is completely free and covers almost anything you can think of (from cars to computers, handyman, and even drones).
click here to download the app (for users in the US for now) and get all the help you need.
goodluck!

Posted on Jan 02, 2017

Add Your Answer

Uploading: 0%

my-video-file.mp4

Complete. Click "Add" to insert your video. Add

×

Loading...
Loading...

Related Questions:

1 Answer

Mobile Home Furnace Problem. I have replaced the furnace "board" [$150.00] and the thermostat [$65.00] and my furnace still turns itself off during night time hours - only. Is there anything else...


What you are describing is a lock-out condition that occurs after the furnace attempts to establish flame three times (usually) and fails, necessitating manual cycling of the power to 'reset' the circuit board. Its unusual that it is only happening at night unless the night temps drop extremely lower in you location than the daytime temps and the heat loss is greater so the furnace needs to come on more ofter. Hmmm.... Still a bit odd.

I'd have a tendency to inspect the flame rod or flame sensor and its connections back to the 'sensor' spade clip on the circuit board. It is responsible for signalling the control board that the flame has been established so gas can continue to flow feeding the flames. If it does not send the signal in a few short seconds after the gas valve opens, it shuts the system down and it re establishes the cycle again....only up to three times before a lockout.

Your system may not have a separate flame sensor and if not the ignition electrode or hot surface igniter itself performs double duty as the ignition device AND the flame sensor. If so, check the connections and make sure there is no oxidation between the wire and the connector.

Jan 07, 2015 | Heating & Cooling

1 Answer

Payne 383KAV heater. Gas valve won't open to fire heater.


Being as how you changed the gas valve, make sure the arrow on the bottom of the gas valve is pointed towards the burner. Check for 24 volts at the common and main valve terminals on the gas valve when the thermostat is calling for heat...terminals MV and C. You will only have 24v there if the flame sensor senses flame... either pilot flame or main gas. You coud have 24v there without gas flowing or flame if is is a thermocouple standing pilot system and the gas valve is not in the 'on' position. But standing pilot systems usually do not have flame sensors.

With a flame sensor in the system, you have to have either spark ignition or glow coil ignition. If its spark ignition check for 24 volts at the pilot valve and common terminals on the gas valve WHILE the ignitor is sparking. That would be PV and C. The ignitor should spark and 24v should be on PV and C for 30 seconds to a full minute without ignition if it is a spark-to-pilot system.

If you have a glow coil, it will energize and burn bright orange for a minimum of 30 seconds BEFORE the main valve is energized. Then MV and C is only receiving 24v for approximately 5 to 6 seconds. This gives the flame sensor the time to prove the flame....if it does not prove flame, the system shuts down.

Dec 29, 2014 | Heating & Cooling

1 Answer

My York furnace sometimes doesn't completely ignite


A noisy inducer probably is headed for replacement.

The igniter can produce a healthy glow and still be defective. Mine had to be replaced with a new, improved one.

The thermocouple could be defective even though it seems to open the gas valve when it should.

The heat sensor in the bonnet could be defective. That controls main blower operation.

The heat exchanger could be cracked.

Jan 10, 2014 | Heating & Cooling

1 Answer

Bryant model 340mav no flame status 31


try jumping out pressure switch see if it lights , see if flame senser is clean.

Apr 21, 2012 | Heating & Cooling

1 Answer

Heater keeps turning on & off. Come on & you can see the flame & hear it come on then seconds later it goes off & then starts then back off. What could be the problem?


That sound to me like the flame sensor is contaminated . Get a dry brillo pad and clean it up. Then restart it. I have 2 offerings here:
Video: auto cycleing quick fix and how it works electronic ignition pdf. See older electronic ignition systems used a grounding wire from the spark electrode to verify heat and therefore ignition and newersystems now use a flame detector to sense resistance changes and verify that YES Houston we indeed have igition!. So what happens is the gunk on the sensor prevents the control from readily sensing ignition, it has a cow and shuts down everything.

Furnace lockout

Electronic ignition diagnostics and stuff pdf

Jan 15, 2011 | Goodman GMS90703BXA Heater

1 Answer

Went to bed last night with heat woke up today everything house was cold, looked at thermastat it said 63degrees,, checked out furnace it starts up but doesnt ignite, sounds like its in the start up stage...


Does the hot surface igniter glow? If not, it is probably cracked. If this is
a 90% furnace, it could be that yuor intake air is causing the problem.

Dec 27, 2009 | Goodman GMS90703BXA Heater

1 Answer

My goodman heater will not run all of the sensors check out ok and have voltage the vacuum switch is also working I am getting one blink after the furnace shuts back down,there is no voltage to the...


This is a step system for heat ,,, step 1....... thermostat calls fo heat and send power to the vent fan motor, it proves its running by a small suction on the red tube which closes a switch and tell the c. b. to go to step--2 lite the hsi this glows &in20 seconds....step --3 the gas valve opens and dump raw gas in the venturis tubes.. and proves it has a flame thru the flame sensor. and step 4... the box heats up and closes the fan switch..

Dec 20, 2009 | Goodman Heating & Cooling

1 Answer

All-Pro 200 will not ignite.


It sound like you have either an ignition or 'dirty fuel' issue. The now Desa 'All Pro 200 T' that I have I fixed numerous times.. the approx $70 'ignitor'. But when the error code says flame' If you can tell that the thing started a flame... for a few seconds or at all.. then you can be sure that the ignitor is not the problem. .. yet. And that the flame is not a consistent lighted color.. which can meen diferent fuels mixed together..or water in the fuel. I'd try starting your heater with a high octane 'power boost' type fuel additive straight.. and then if it runs on that w/o a problem.. then you know its the fuel or fuel system.. Also you might check that the blue wire eye.. that 'looks at the flame' window is clean and wiped off with a clean cotton swab.
md

Nov 15, 2008 | All-Pro Kerosene Garage Shop Heaters - All...

Not finding what you are looking for?
Goodman GMS90703BXA Heater Logo

Related Topics:

48 people viewed this question

Ask a Question

Usually answered in minutes!

Top Goodman Heating & Cooling Experts

Dan Webster
Dan Webster

Level 3 Expert

8205 Answers

paulcarew

Level 3 Expert

2047 Answers

Brandon Berry
Brandon Berry

Level 2 Expert

407 Answers

Are you a Goodman Heating and Cooling Expert? Answer questions, earn points and help others

Answer questions

Manuals & User Guides

Loading...