Question about Goodman GMS90703BXA Heater
Furnace is not staying lit
Furnace starts up then shuts down. Flame starts and then goes out.. The air compressor works fine.
  • 96 Answers
If the main burners are firing but goright out it could be the flame sensor which is a straight wire with one wire going to it you can clean it with steel wire or fine sand paper if not check the flashing code on the control board
Posted on Dec 25, 2008
Furnace won't stay lit. Intertherm Model M2RC-080A-16BN. Ignightor glows, flame starts and after a few seconds the flame shuts off. Then it starts the cycle again. It goes thru this cycle a fe
It sounds like the flame sensor is bad. If thats not the case you may need to replace the control board. You should make sure the flame sensor is directly into the flame.
Nov 20, 2014 | Intertherm Heating & Cooling
Janitrol GUPS075-3 Furnace burners will not stay lit
The first thing I would do is make sure the flame sensor is clean, this is a metal rod immersed in the burner flame on the opposite side of the igniter. If too much oxidation builds up on it, it will not allow the burner to stay lit. To clean, just turn off furnace and remove flame sensor and clean with steel wool and then reinstall. If this does not solve the problem there may be a problem with the gas valve.
Nov 08, 2012 | Heating & Cooling
Ruud 90+ Model UGRA 10EZAJS Trips Out
Check for condensation buildup in the Induction Blower housing. The condensate tubes or canister may be blocked and causing the diaphragm switch to trip the unit out causing the burners to shut down.
Feb 11, 2012 | Ruud Heating & Cooling
Furnace goes on red light stays on exhaust fan for heat chamber goes on gas igniter comes on but soon as gas comes on furnace kicks off have to shut off power for furnace for it to reycyckle but same...
Check your filter to make sure it is not plugged. If it is plugged - replace with filter recommended for your furnace. Every manufacture recommends you have your furnace checked and cleaned on an anual basis to keep itrunning safely and at it's top efficiency. If the filter is plugged or the blower wheel plugged, the furnace will shut itself off. Make sure all registers are uncovered - suppply and return registers.
Jan 03, 2011 | Heating & Cooling
Rheem 90+ NG Furnace. When furnace starts, draft inducer starts, ignitor glows and gas ignites. Burners stay lit for 10 seconds or so, then the flame reduces for a few seconds then goes out. Main blower...
Check the draft inducer air switch ( vacuum diaphragm switch) If the switch is opening when the burner starts, you might have a blockage on air piping coming into the furnace. Also prime the condensate trap on the condensate drain from the combustion fan. Also check the gas pressure, if your gas pressure is dropping, the gas pressure switch will shut it down. If it's too high the moment it comes on could raise the pressure in the furnace dropping out the combustion fan proving switch.
Oct 29, 2010 | Electric Circuit Breaker Kit for Furnace
Amana Air Command 80 SSE gas furnace will not stay running
In the path of the flame on the last burner that starts, there will be a small rod. That rod is the flame sensor. Take a scrub pad and polish it. Also check the electrical connection that goes back to the circuit board. Disconnect any ground wire from the circuit board to furnace cabinet, sand it and replace it.
Mar 14, 2010 | Heating & Cooling
Heater will fire but wont stay lit.
I assume that you are referring to a natural gas forced air furnace. If so you just described the symptoms of a dirty flame sensor. Remove the sensor with a 1/4" nutdriver. clean the flame sensor with a small piece of fine grit sandpaper or emery cloth. replace the sensor and turn the furnace back on.
Good luck.....
Apr 11, 2009 | Heating & Cooling
Furnace pilot problem
check the pilot gas pressure, might be too weak and blowing out when the blower starts, the clicking noise is the gas valve shutting down when it detecks no pilot flame, that park is normal.
Jan 10, 2009 | Honeywell Power Humidifier: Furnace...
Rheem gas furnace pilot lights, but no burners or fan
If the burners do not fully ignite, the sensor will shut the furnace down. The lack of sufficient burner flame is a gas valve or gas pressure problem within the valve.
Replacing the gas valve with the original one may get you going. I surely suggest a professional service company for safety reasons and a thorough inspection. A 20 year old furnace is past it's normal life span.
Jan 06, 2009 | Heating & Cooling
Pilot lights fine, furnace fires up, when it turns off the pilot goes out
need to have at least 3 feet of vent out of the roof, if it is to low the coll air will cold soak down to the pilot and shut it down.