If the unit operates for a short times then locks out and is reset by cycling the power it is going into a "Hard Lockout" and this can be caused by several things. The most common are pressure switch and flame retification issues. Both of these issues will display erro code flashes.
Here are the codes for RUUD Furnaces:
Furnace: 1 blink. Soft lock out. Ignition sequence failed to prove flame. Check polarity & ground.
Flame sensor should be clean and surrounded by flame. Burner mounting screws must be
tight.
2 blinks. Pressure switch did not close when inducer motor started. Check for blocked
flue or obstructions in pressure switch tube.
3 blinks. Open limit switch. Check for dirty filters, closed registers, crushed ducts.
Temperature rise must match range stated on unit tag. Increase fan speed.
4 blinks. Pressure switch did not open when inducer motor stopped. Replace pressure
Switch.
5 blinks. Twinning circuit problem. Control board cannot confirm communication second furnace. Check twinning dip switch setting
Once you have a code, please feel free to contact me and I can walk you thru a more indepth diagnostic of the unit to repair the issue or direct you of what you need to do...
Richard (Rick) Drennan
Global HVAC Distributors
RUUD Field Support Representative / Instructor
rdrennan@globalhvac.com
900 Spreckels Ave
Manteca, Ca. 95336
Office (877)448-7263
you need to see what code is flashing on the control board and look on the door panel to see the flash codes