How many arc fault circ breakers can you stack in a subpanel . We have stacked them and they fell very warm.
thanks
Peter Tucker
peter.tucker@redondo.org
  • 3 more comments
  • peter_tucker Dec 23, 2008
    the breakers are rated at 20 amps
  • CBWood Feb 04, 2009
    I am having the same warm condition. Assume a code compliant installation to the max breaker rating. Should they get warm when used as intended?
  • Allen Neal
    Allen Neal May 11, 2010
    NEED MORE INFO AMPERAGE OF BREAKERS PANEL RATING NUMBER OF BREAKERS
  • Anonymous Mar 18, 2014
    what is the difference between gold and green labels on arc faults breakers
  • 69 Answers
If its a 100 amp panel only 5- 20 amp breakers, if its a 200 amp panel 10- 20amp breakers
Posted on Dec 25, 2008
My 3 arc fault breakers run hot and draw about a third of an amp from the ground bar wire each, 24/7. Is this possibly normal?
How did check amps. I would check the amps on the circuit itself. Might be drawing close to max. thats why it's hotter. breaker should have no more than 80%. Of an amp draw on the circuit
Oct 05, 2016 | Eaton ARC FAULT CIRC BREAKER
Why are these breakers hot and constantly draw .35 amps from the ground bar?
When current is going through wiring and devices it normally operates warm. That is why most wire and devices such as breakers are rated at 70 degrees Celsius. In a panel, heat can be transferred through the buss bar they are connected to.
Breakers will trip for 2 reasons. Overload amperage and heat.
Power outage and now ARC fault won't reset??
In general, they have small heaters in them. If they go bad they won't reset. Replace it.
Dec 08, 2013 | Eaton ARC FAULT CIRC BREAKER
15amp Eaton Arc fault breaker type BRAF trips every day at same time. There are no high amp electrical things plugged in. What is causing this? should I have it replaced?
"Arc fault" breakers trip when an arc occurs, either in a receptacle or a light switch, for example. An arc can be caused by an old light switch, when turning it on. An arc can also occur when you unplug a chord while the device is still turned on or running.
Aug 25, 2013 | Eaton ARC FAULT CIRC BREAKER
Red light blinks on 20 amp eaton arc fault breaker
Alot of the times if 2 circuits are sharing a neautral it will give u arc faukt problems.
Dec 25, 2012 | Eaton ARC FAULT CIRC BREAKER
On a arc fault breaker type chaf how do you test it to see if it is bad?
many of these have not been working right out of the box.... if it will not stay on then replace it with another one and make sure it is not something in the circuit...
heatman101
Jan 23, 2011 | Eaton ARC FAULT CIRC BREAKER
I accidentlly press the arc breaker button and need help cause the light would not go on
turn the breaker all the way to the off position and then to the on position.
Aug 05, 2010 | Eaton ARC FAULT CIRC BREAKER
Arc fault circ breakers feel warm
If the breakers are 20 amp and the panel is rated at 100 amps, only 5 breakers. if the panel is 200 amp, only 10, 20 amp breakers and so on
Dec 23, 2008 | Eaton ARC FAULT CIRC BREAKER
3 combination arc fault breakers tripping under load
What is happening is the white wire that comes off the breaker is probably too close to another neutral or too close to a hot wire that is on one of the other circuits that will make it trip when you use a drill etc... Check to see if the coiled up white wire off of the breaker is not near a hot in the panel. I have had lots of arc fault breakers trip for that reason.