Blower Motor cycles on & off
Burner ignites fine but the blower motor will not stay on. It blows hot air for about 10 seconds and shuts down for about 30 seconds and will continue this cycling, meanwhile the burner is staying lit.
  • 700 Answers
Whats happening is thje heat exchanger is cooling off and cycling the fan off this is a normal occurance whenever the unit is first turned on.
Posted on Dec 22, 2008
Replaced ignator and flame sensor. Heater comes on normally but flame only stays on for 10 to 15 seconds. Faullt blinks 3 times. It will blink 3 times for about 30 seconds. Then re-cycles again.
Sounds like your you may have a dirty pilot assembly if your unit is a direct spark system. Also check ground wires are secure.
If you need further help, I’m available over the phone at https://www.6ya.com/expert/jerry_8a145f1328fa119f
Feb 17, 2017 | Heating & Cooling
Johnson air ease furnace blower motor getting hot
Check for correct voltage ,also would check capacitor and motor rotation.
Dec 08, 2017 | Heating & Cooling
Heil furnace blower motor stays on won't shut off at thermostat blows cold air continuously
Do you have t sat fan switch in on position??? If so blower will run continously set it to auto and it will cycle with heat call
Nov 12, 2012 | Heating & Cooling
Have a Goodman GMT070-3B which the vent motor seems to be sticking. I took apart and cleaned the brushes and reassembled. The furnace will come on only after what seems like the vent motor comes up to...
The whole assembly must be replaced.
The sequence of operation is -
Combustion fan purges the heat exchanger. A pressure switch verifies combustion air fan is running. Usually a 30-45 second purge before the hot surface ignitor glows, or the spark ignition starts.
Gas valve opens after 10-15 seconds and main burners light. Control board monitors for flame and shuts gas valve after 2-3 seconds if main burner does not light.
If burner does not light, some boards repeat this for 3 tries, then locks out and is reset by cycling power.
Air blower comes on after another 30-45 seconds after main burner ignition.
Times may vary based on the specific controller board. A flow chart and timing sequence should be located somewhere on the unit, usually in the fan compartment.
Dec 16, 2009 | Goodman GMS90703BXA Heater
Pilot light will stay on until the burner shuts off. Seems to blow out the pilot each time the burner shuts off.
Need to check the vent tube for restrictions
and check to see if the blower motor air is not blowing out the pilot if it is the blower motor air blowing out the pilot nthe the heat exchanger may be cracked and could be dangers
Dec 01, 2009 | Vanguard International Blue Flame - Medium...
Ruud furnace Model URKA A030jK08 Code opt 589
Flip the lower panel over and look for a wiring diagram. On that diagram there will be a diagnostic chart. Let me know what 5 blinks represent. Then I want you to read on.
On a call for heat, the 24 volt thermostat sends a signal to the control module. The control module will indicate a call for heat with a light on the control either blinking or remain solid depending upon model. The inducer (exhaust) blower will purge all gasses from the furnace and pressurize a pressure switch. Once the pressure switch tells the module to continue, the electronic ignition will energize and send 120 volts to the igniter. The igniter will glow and you will be able to see it if viewed thru the small inspection port. Once the igniter gets hot enough, it sends a signal to the module opening up the gas valve (24 volts). Either a pilot will come on or the burner tube will ignite then spread the flame to all burners. Lastly a safety sensor will be looking for a certain temperature within a few seconds and the furnace will continue to operate and the room air blower will turn on in a minute or two.
What could go wrong? The unit will not run if there is no signal from the thermostat (bad thermostat or broken wire), the control module does not sense a signal from the thermostat (bad control), the inducer does not energize (bad motor), the pressure switch does not close (blocked vent piping, bad switch, plugged condensate hose), the igniter does not energize (bad control, bad igniter), the gas valve does not open or there is no gas (bad gas valve, broken wire, no gas), the pilot does not light (dirty pilot), the burner does not light (bad burner, plugged orifice, not enough combustion air), the flame does not spread to each burner (bad flame spreader, dirty flame spreader, more bad burners), the flame safety sensor does not detect flame (dirty or bad flame spreader, bad flame sensor, broken wire, bad control), or the room air blower does not energize (bad fan motor, bad control).
Nov 23, 2009 | Heating & Cooling
A 1979 Colman RV furnace. Blower shuts off shortly after burner shuts off leaving a hot heat exchanger. After 15 seconds blower comes on again blows for 10 seconds shuts off comes on in 15 seconds blows...
The fan limiting switch is acting up. It should stay running until lower temp is reached. It will cycle until the temp stays below or at the low setting. Limit switches are adjustable.
Jun 09, 2009 | Coleman Propane Forced Air Heater...
Heater Burner ignites but main blower motor will not turn on.
it sound like the blower motor may be seizing up. try spining the blade by hand to see if it feels free or not. the motor could be trying to turn but can then tripping itself out on overload. (most motors have built in safety overloads which will trip during an overcurrant event. aka too many amps.) you may have to replace blower motor
Mar 16, 2009 | Mr. Heater Natural Gas Garage Heater -...
Heating & Cooling Logo
171 people viewed this question
Top Heating & Cooling Experts
Paul Carew
Marvin
Marvin
john h