Question about Amana PTC153B35AE Air Conditioner

3 Answers

Furnace dont have heat

My furnace ignitor is not igniting inducer motor comes on then stop when blower comes on then blink 4 times model # amv911550xa

Posted by on

  • 5 more comments 
  • mac1wil Dec 21, 2008

    I dont know because the installer did not leave the book and they removed the code problem on the door please help me

  • mac1wil Dec 21, 2008

    ignitor looks good and I tried to call the number 1-877-254-4729 but they close for the weed end

  • Ken Bledsoe May 11, 2010

    Most units 4 flashes means limit or roll-out switch open. good luck

  • Stephen Evans May 11, 2010

    Have you tried turning of the switch on the side of the furnace and then back on? Then try furnace and let me know it the ignitor glows. Sorry but without the code and being there this is hard to determine. Steve

  • Stephen Evans May 11, 2010

    If you feel comfortable, remove the ignitor, usually held in with a 1/4" socket head. Be very careful not to bump it. Even the slightest hair line crack and its usless. if you see a crack it needs replacing. There are some companies such as Servall that may carry them and sell to the public. I cannot get the codes online. You might try calling a different htg company than the one that installed it and see if they will tell you what the code is. Also



    To speak with a Heating and Air Conditioning Consumer Affairs Representative from within the United States, please call 1-877-254-4729



    It is ilegal for the installer to take the owners instuction manual. This is to stay with the homeowner, it also usually contains the fault codes. They took these things because nowadays if you have them, with the newer furnaces you can diagnose the problem yourself. Keeping them from bilking you for big dollars. When you talk to Amana I would appriase them of your situation with the htg contractor that installed your furnace. Hope this helps, let me know. Steve

  • Stephen Evans May 11, 2010

    I cannot get the code listing online, But here the # for Amana

    To speak with a Heating and Air Conditioning Consumer Affairs Representative from within the United States, please call 1-877-254-4729.. Hope this helps? Any further questions dont hesitate. Steve

  • Stephen Evans May 11, 2010

    It sounds like you have a hairline crack in the ignitor. What does the code chart say for the 4 flashes? Steve

×

3 Answers

  • Level 1:

    An expert who has achieved level 1.

    Hot-Shot:

    An expert who has answered 20 questions.

    Corporal:

    An expert that has over 10 points.

    Mayor:

    An expert whose answer got voted for 2 times.

  • Contributor
  • 22 Answers

Check for pressure switch trouble or cracked ignitor.

Posted on Jan 21, 2010

  • Level 3:

    An expert who has achieved level 3 by getting 1000 points

    All-Star:

    An expert that got 10 achievements.

    MVP:

    An expert that got 5 achievements.

    President:

    An expert whose answer got voted for 500 times.

  • Master
  • 1,304 Answers

No ignition....
check you exhaust an intake clear of obstruction
if they are both clear i would replace your ignitor

Posted on Oct 06, 2009

  • Level 2:

    An expert who has achieved level 2 by getting 100 points

    Hot-Shot:

    An expert who has answered 20 questions.

    Corporal:

    An expert that has over 10 points.

    Mayor:

    An expert whose answer got voted for 2 times.

  • Expert
  • 70 Answers

Pressure switch stuck take off hose **** on it then put back on

Posted on Oct 04, 2009

1 Suggested Answer

6ya6ya
  • 2 Answers

SOURCE: I have freestanding Series 8 dishwasher. Lately during the filling cycle water hammer is occurring. How can this be resolved

Hi,
a 6ya expert can help you resolve that issue over the phone in a minute or two.
best thing about this new service is that you are never placed on hold and get to talk to real repairmen in the US.
the service is completely free and covers almost anything you can think of (from cars to computers, handyman, and even drones).
click here to download the app (for users in the US for now) and get all the help you need.
goodluck!

Posted on Jan 02, 2017

Add Your Answer

Uploading: 0%

my-video-file.mp4

Complete. Click "Add" to insert your video. Add

×

Loading...
Loading...

Related Questions:

1 Answer

I have a ng furnace downstairs that started this a couple of days aga....It comes on like it is suppose to and runs until it shuts off. Once the blower cuts off it stays off for about 1 second and then...


1. Thermostat calls for heat. 2. Draft inducer motor starts. 3. Pressure switch attached by a small plastic or rubber tube senses the negative pressure produced by the draft inducer and closes. 4. Draft inducer runs for 30 seconds to a minute before you hear a gas hissing sound. The ignitor did not glow, the flame sensor (a small metal probe about 1/8" in diameter, with a white porcelain base) does not sense the flame, so after 8 to 10 seconds the hissing sounds stops with no ignition of gas to heat your home. Your furnace shuts down and goes into a lock out condition until you turn your power switch back off and on again. Then the sequence starts all over again with no ignition of the gas. Solution:You probably need to purchase and install a new ignitor. I would suggest that you inspect your ignitor closely for cracks. Make sure you do not touch the ignitor with your bare hands. If you do not visually see a crack, then you could have a furnace control board problem or a limit, rollout switch problem. The furnace's control board might not be supplying the voltage to the ignitor. If your furnace lights and the gas stays on for 8 to 10 seconds, then shuts right back off, then you need to clean your flame sensor with light sand paper or steel wool. You might need a new flame sensor, but most of the time they can be cleaned an will work well after cleaning.

Dec 06, 2010 | Heating & Cooling

1 Answer

I have a newer tappan heater and get 4 blinks on led for error code the unit starts up fine and has flame but flame goes off when blower kicks on


Problem: Your furnace will not ignite the gas to produce heat for your home. When a furnace has a bad ignitor what I see most of the time is the following sequence of operation:


1. Thermostat calls for heat. 2. Draft inducer motor starts. 3. Pressure switch attached by a small plastic or rubber tube senses the negative pressure produced by the draft inducer and closes. 4. Draft inducer runs for 30 seconds to a minute before you hear a gas hissing sound. The ignitor did not glow, the flame sensor (a small metal probe about 1/8" in diameter, with a white porcelain base) does not sense the flame, so after 8 to 10 seconds the hissing sounds stops with no ignition of gas to heat your home. Your furnace shuts down and goes into a lock out condition until you turn your power switch back off and on again. Then the sequence starts all over again with no ignition of the gas. Solution: You probably need to purchase and install a new ignitor. I would suggest that you inspect your ignitor closely for cracks. Make sure you do not touch the ignitor with your bare hands. If you do not visually see a crack, then you could have a furnace control board problem or a limit, rollout switch problem. The furnace's control board might not be supplying the voltage to the ignitor. If your furnace lights and the gas stays on for 8 to 10 seconds, then shuts right back off, then you need to clean your flame sensor with light sand paper or steel wool. You might need a new flame sensor, but most of the time they can be cleaned an will work well after cleaning.

Nov 26, 2010 | Heating & Cooling

1 Answer

Induction fan motor cycles on and off , with no call for heat


Problem: Your furnace will not ignite the gas to produce heat for your home. When a furnace has a bad ignitor what I see most of the time is the following sequence of operation:


1. Thermostat calls for heat. 2. Draft inducer motor starts. 3. Pressure switch attached by a small plastic or rubber tube senses the negative pressure produced by the draft inducer and closes. 4. Draft inducer runs for 30 seconds to a minute before you hear a gas hissing sound. The ignitor did not glow, the flame sensor (a small metal probe about 1/8" in diameter, with a white porcelain base) does not sense the flame, so after 8 to 10 seconds the hissing sounds stops with no ignition of gas to heat your home. Your furnace shuts down and goes into a lock out condition until you turn your power switch back off and on again. Then the sequence starts all over again with no ignition of the gas. Solution: You probably need to purchase and install a new ignitor. I would suggest that you inspect your ignitor closely for cracks. Make sure you do not touch the ignitor with your bare hands. If you do not visually see a crack, then you could have a furnace control board problem or a limit, rollout switch problem. The furnace's control board might not be supplying the voltage to the ignitor. If your furnace lights and the gas stays on for 8 to 10 seconds, then shuts right back off, then you need to clean your flame sensor with light sand paper or steel wool. You might need a new flame sensor, but most of the time they can be cleaned an will work well after cleaning.

Nov 26, 2010 | Heating & Cooling

1 Answer

I AM WORKING ON A CARRIER 90% FURNACE. IT WILL NOT FIRE UP. IT SHOWS A 34 CODE. THE IGNITOR DOES NOT ENERGIZE FROM THE BOARD. NO POWER COMING FROM THE BOARD. I HERE A CLICK AS IF IT IS TRYING BUT NO...


Problem: Your furnace will not ignite the gas to produce heat for your home. When a furnace has a bad ignitor what I see most of the time is the following sequence of operation:


1. Thermostat calls for heat.

2. Draft inducer motor starts.

3. Pressure switch attached by a small plastic or rubber tube senses the negative pressure produced by the draft inducer and closes.

4. Draft inducer runs for 30 seconds to a minute before you hear a gas hissing sound. The ignitor did not glow, the flame sensor (a small metal probe about 1/8" in diameter, with a white porcelain base) does not sense the flame, so after 8 to 10 seconds the hissing sounds stops with no ignition of gas to heat your home. Your furnace shuts down and goes into a lock out condition until you turn your power switch back off and on again. Then the sequence starts all over again with no ignition of the gas. Solution: You probably need to purchase and install a new ignitor. I would suggest that you inspect your ignitor closely for cracks. Make sure you do not touch the ignitor with your bare hands. If you do not visually see a crack, then you could have a furnace control board problem or a limit, rollout switch problem. Please see "limits, rollout switches & furnace control boards" further down on this page. The furnace's control board might not be supplying the voltage to the ignitor. If your furnace lights and the gas stays on for 8 to 10 seconds, then shuts right back off, then you need to clean your flame sensor with light sand paper or steel wool. You might need a new flame sensor, but most of the time they can be cleaned an will work well after cleaning.

Nov 25, 2010 | Heating & Cooling

1 Answer

Carrier 58sxc120 won't ignite and I get a fault code blinking light of short long short don't know what it means.


Problem: Your furnace will not ignite the gas to produce heat for your home. When a furnace has a bad ignitor what I see most of the time is the following sequence of operation:


1. Thermostat calls for heat. 2. Draft inducer motor starts. 3. Pressure switch attached by a small plastic or rubber tube senses the negative pressure produced by the draft inducer and closes. 4. Draft inducer runs for 30 seconds to a minute before you hear a gas hissing sound. The ignitor did not glow, the flame sensor (a small metal probe about 1/8" in diameter, with a white porcelain base) does not sense the flame, so after 8 to 10 seconds the hissing sounds stops with no ignition of gas to heat your home. Your furnace shuts down and goes into a lock out condition until you turn your power switch back off and on again. Then the sequence starts all over again with no ignition of the gas. Solution: You probably need to purchase and install a new ignitor. I would suggest that you inspect your ignitor closely for cracks. Make sure you do not touch the ignitor with your bare hands. If you do not visually see a crack, then you could have a furnace control board problem or a limit, rollout switch problem. Please see "limits, rollout switches & furnace control boards" further down on this page. The furnace's control board might not be supplying the voltage to the ignitor. If your furnace lights and the gas stays on for 8 to 10 seconds, then shuts right back off, then you need to clean your flame sensor with light sand paper or steel wool. You might need a new flame sensor, but most of the time they can be cleaned an will work well after cleaning.

Nov 24, 2010 | General Heating & Cooling

1 Answer

Hot surface ignitor won't ignite,I replaced the igniter and it still won't.


Problem: Your furnace will not ignite the gas to produce heat for your home. When a furnace has a bad ignitor what I see most of the time is the following sequence of operation:


1. Thermostat calls for heat.
2. Draft inducer motor starts.
3. Pressure switch attached by a small plastic or rubber tube senses the negative pressure produced by the draft inducer and closes.
4. Draft inducer runs for 30 seconds to a minute before you hear a gas hissing sound. The ignitor did not glow, the flame sensor (a small metal probe about 1/8" in diameter, with a white porcelain base) does not sense the flame, so after 8 to 10 seconds the hissing sounds stops with no ignition of gas to heat your home. Your furnace shuts down and goes into a lock out condition until you turn your power switch back off and on again. Then the sequence starts all over again with no ignition of the gas.
Solution: You probably need to purchase and install a new ignitor. I would suggest that you inspect your ignitor closely for cracks. Make sure you do not touch the ignitor with your bare hands. If you do not visually see a crack, then you could have a furnace control board problem or a limit, rollout switch problem. The furnace's control board might not be supplying the voltage to the ignitor. If your furnace lights and the gas stays on for 8 to 10 seconds, then shuts right back off, then you need to clean your flame sensor with light sand paper or steel wool. You might need a new flame sensor, but most of the time they can be cleaned an will work well after cleaning.

Oct 25, 2010 | Heating & Cooling

1 Answer

York furnace model p2mpd12h06401f flashes 4 times for trouble code does'nt have code list inductor motor comes on but ignitor does'nt come on


Check pressure switch for inducer motor. If switch closes, check for crack in ignitor. If gas valve opens and you can hear/smell gas, the ignitor is bad probably. If pressure switch isn't closed you need to check for blocked vent/chimney/heatexchangers.

Dec 18, 2009 | York Furnace Draft Inducer Blower Fasco #...

2 Answers

Goodman furnace blinked 1 time


Furnace attempted to start but failed after so manay tries. This may help you.

Sequence of operation, Gas Furnace.

On a call for heat, the 24 volt thermostat sends a signal to the control module. The control module will indicate a call for heat with a light on the control either blinking or remain solid depending upon model. The inducer (exhaust) blower will purge all gasses from the furnace and pressurize a pressure switch. Once the pressure switch tells the module to continue, the electronic ignition will energize and send 120 volts to the ignitor. The ignitor will glow and you will be able to see it if viewed thru the small inspection port. Once the ignitor gets hot enough, it sends a signal to the module opening up the gas valve (24 volts). Either a pilot will come on or the burner tube will ignite then spread the flame to all burners. Lastly a safety sensor will be looking for a certain temperature within a few seconds and the furnace will continue to operate and the room air blower will turn on in a minute or two.

What could go wrong? The unit will not run if there is no signal from the thermostat (bad thermostat or broken wire), the control module does not sense a signal from the thermostat (bad control), the inducer does not energize (bad motor), the pressure switch does not close (blocked vent piping, bad switch, plugged condensate hose), the ignitor does not energize (bad control, bad ignitor), the gas valve does not open or there is no gas (bad gas valve, broken wire, no gas), the pilot does not lite (dirty pilot), the burner does not lite (bad burner, plugged orifice, not enough combustion air), the flame does not spread to each burner (bad flame spreader, dirty flame spreader, more bad burners), the flame safety sensor does not detect flame (dirty or bad flame spreader, bad flame sensor, broken wire, bad control), or the room air blower does not energize (bad fan motor, bad control).

Most newer furnaces will have a diagnostic center or control built into the control module. You may be able to view it as it is running thru a small viewing port. Some models will require the removal of an access panel prior to finding it. On the reverse of the access panel, there will be a diagnostic chart that will aide you in understanding any error code recorded (usually a blinking light).

This is why we technicians earn the big bucks!

Dec 05, 2008 | Goodman GMS90703BXA Heater

1 Answer

Furnace pilot is not igniting.


the first blower you hear is the inducer motor it pushes the exhaust out. sounds like abad gas valve.do you have a standing piloit light or is it eletronic ignition. if electronic and there is no glow you have a bad ignitor

Oct 04, 2008 | Honeywell Power Humidifier: Furnace...

Not finding what you are looking for?
Amana PTC153B35AE Air Conditioner Logo

213 people viewed this question

Ask a Question

Usually answered in minutes!

Top Amana Heating & Cooling Experts

Dan Webster
Dan Webster

Level 3 Expert

8205 Answers

Donni Steen

Level 3 Expert

659 Answers

Bill Long

Level 3 Expert

587 Answers

Are you an Amana Heating and Cooling Expert? Answer questions, earn points and help others

Answer questions

Manuals & User Guides

Loading...